#1
|
|||
|
|||
|
I inspected a Square D HOM 30 amp breaker with a stranded CU #8 wire for the A/C. The wire strands are split to fit under the special washer and around the screw of all three terminations (see photo)
Unfortunately, I can not find my Square D HOM installation guide and could not run the A/C to capture a thermal image. (dam) I am concerned that it's incorrect. I know what to right if I can not find any printed info, so does anyone have an installation guide? Peter |
|
#2
|
||||
|
||||
|
I have a 20a homeline breaker in front of me, and it's rated up to 8# as a single conductor. I GUESS this is OK, but I'm concerned with those splitting of stands.
hth, tom |
|
#3
|
|||
|
|||
|
is it write???
|
|
#4
|
|||
|
|||
|
Quote:
|
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I guess the only question is if splitting the strands is better than trying to clamp them on one side. With no further guidance from the instructions I am OK with what you see.
|
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
No, it's not right, because the breaker clearly has a picture molded in it as to how the conductor is to be terminated. Splitting the strands is not permitted. Let me run out to the truck and take a picture of the instructions on an HOM230.
|
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here we go. This is a picture of a HOM230. You can see that in two places, molded on the breaker, it shows that the conductor is not split. The left hand side shows how the stripped conductor is to be prepared, and the top right picture shows that one #8 is to go under one side of the square captured washer.
|
|
#8
|
|||
|
|||
|
Excellent, I love learning stuff, hope I can remember some of it.
"Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#9
|
|||
|
|||
|
Thanks Marc.
I knew it was wrong, but I did not have that view of the breaker. Peter |
|
#10
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
You guys ever go to Lowes or Home Depot just to look at stuff? Bring the wife along. She'll love that. |
|
#11
|
||||
|
||||
|
Quote:
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#12
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc, that is "better guidance". I defer to your answer. Stranded always looks ugly in anything but a lug but it is legal.
|
|
#13
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#14
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is what I was curious about too. I have some QO 30s in both styles.
I still don't think I would tag a breaker with the screw/plate design and the #8 split like that. The real issue is still whether you have a secure connection and if the terminal is rated for that wire size. |
|
#15
|
|||
|
|||
|
Greg, a sq. d rep. emailed me a diagram about 1.5 yrs. ago.
He specifically stated that the wires must be the same size so the washer sits flat/square, and places equal pressure/surface contact on the wires. So your point about the secure connection is mine too especially if we consider the following: How much twisting pressure did the electrician use to create the diameter of the wire, which is probably not equal on both sides, hence, a problem. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| Tell me again what size wire goes on a 100 amp breaker? | jfunderburk | Electrical | 3 | 8/20/07 11:39 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical | 0 | 7/2/07 1:35 PM |
| Service wire size to breaker panel | sfalvey | Electrical | 12 | 10/31/06 5:28 PM |
| 30 amp breaker wire size | kweiss | Electrical | 18 | 10/10/06 10:53 PM |