Default Re: Square D HOM Breaker & Max Wire Size

Marc S.

I did notice on the breaker that 40°C marking is that correct for the HOM breakers ?? i am used to see 60°C or 60/75°C marking on it

if so i have to watch that one.

Merci, Marc
Reply With Quote
  #17  
Old 3/3/08, 6:14 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Square D HOM Breaker & Max Wire Size

Quote:
Originally Posted by Marc Benz
Marc S.

I did notice on the breaker that 40°C marking is that correct for the HOM breakers ?? i am used to see 60°C or 60/75°C marking on it

if so i have to watch that one.

Merci, Marc
See #28:
Reply With Quote
  #18  
Old 3/3/08, 7:02 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Square D HOM Breaker & Max Wire Size

Quote:
Originally Posted by Marc Benz
Marc S.

I did notice on the breaker that 40°C marking is that correct for the HOM breakers ?? i am used to see 60°C or 60/75°C marking on it

if so i have to watch that one.

Merci, Marc
That is the ambient temp rating, not the terminal rating. The terminal rating is at the upper right in my picture.
Reply With Quote
  #19  
Old 3/3/08, 8:05 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Square D HOM Breaker & Max Wire Size

I wrote a proposal question whether a panel full of AFCIs in unairconditioned space that might exceed 104f/40c and they just blew it off with a no answer answer.
I was hoping they would refer to something that tells you the consquence of being in an ambient above 40c. That can happen in a Florida garage and wouldn't be unusual at all in Arizona.
Reply With Quote
  #20  
Old 3/3/08, 9:08 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Square D HOM Breaker & Max Wire Size

Thanks Marc and Joe T. for highlighting this


sorry about confuseing with the rating i just want to double check it that all

Many thanks

Merci, Marc
Reply With Quote
  #21  
Old 3/3/08, 9:22 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Square D HOM Breaker & Max Wire Size

Quote:
Originally Posted by Greg Fretwell
I was hoping they would refer to something that tells you the consquence of being in an ambient above 40c. That can happen in a Florida garage and wouldn't be unusual at all in Arizona.
They trip quicker. That's all. They might even trip below their marked ampacity. No hazard, for sure, but possibly a nuisance. It's not really anything that people have field reported as ever being a real problem. It's interesting to talk about, for sure, but in practice it's not causing any troubles.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Tell me again what size wire goes on a 100 amp breaker? jfunderburk Electrical Inspections 3 8/20/07 10:39 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 4:28 PM
30 amp breaker wire size kweiss Electrical Inspections 18 10/10/06 9:53 PM


All times are GMT -4. The time now is 2:07 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts