I inspected a Square D panel that was approved for two wires. My question is, if the breakers are approved for two wires, does that mean two wires could be under each lug at the Neutral buss bar? There was double tapping at the buss bar. I recommended it to be further evaluated by an electrician. Now the homeowner is calling telling me that it is approved to have two wires under each lug. This only applies to the breaker itself correct? or does this include the buss bar as well?



Matt Murphy
Murphy Home Inspections
Springfield Illinois
Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 3/25/09, 3:10 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Square D Neutral Double Tap

The breakers being listed for use with 2 wires is a only for the breakers. The neutral buss is a different matter. The buss can accept 2 grounding wires under one screw if they are within the size range listed. Grounded or neutral wires are limited to one per terminal. no sharing of the terminal with grounded and grounding conductors.

Article 408.41 spells this out regarding the neutrals. Previously it was in the listing and labeling instructions and on the label inside the panel.
Reply With Quote
  #3  
Old 3/25/09, 3:21 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Square D Neutral Double Tap

Two nuetrals under one lug was ok and the norm for many years. I can not recall when the NEC no longer allowed this condition, but am sure some one will be able to tell us. But current standards do not allow two nuetrals under one lug.

You did your job by telling the client of the condition you found, if they want to tell you it is ok, fine.
Reply With Quote
  #4  
Old 3/25/09, 3:47 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: Square D Neutral Double Tap

Quote:
Originally Posted by bkelly2 View Post
Two nuetrals under one lug was ok and the norm for many years. I can not recall when the NEC no longer allowed this condition, but am sure some one will be able to tell us. But current standards do not allow two nuetrals under one lug.

You did your job by telling the client of the condition you found, if they want to tell you it is ok, fine.
It was the norm, but I don't think it was ever OK. It was/is OK to have two grounding wires under the same lug but not two grounded (neutral) wires. I think the code was misinterpreted, and it was believed to be OK to have two neutrals together. But like you said, someone will be able to tell us and in ether case it is not OK now.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #5  
Old 3/25/09, 3:59 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Square D Neutral Double Tap

It's been discussed many times.

Here is an earlier thread.

http://www.nachi.org/forum/f19/calli...any-gru-22075/



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #6  
Old 3/25/09, 4:18 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Square D Neutral Double Tap

http://www2.sea.siemens.com/NR/rdonl...rminations.pdf



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 3/25/09, 4:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Square D Neutral Double Tap

Quote:
Originally Posted by bkelly2 View Post
But current standards do not allow two nuetrals under one lug.
. . . except where allowed by the equipment manufacturer for circuits with parallel conductors.

Most panels are listed for a single neutral at each terminal connection. I have never seen a Square D panel listed to accept more than one neutral conductor.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/25/09 at 4:28 PM..
Reply With Quote
  #8  
Old 3/25/09, 4:31 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Square D Neutral Double Tap

Quote:
Originally Posted by jpope View Post
. . . except where allowed by the equipment manufacturer for circuits with parallel conductors.

Most panels are listed for a single neutral at each terminal connection. I have never seen a Square D panel listed to accept more than one neutral conductor.
Dangit Jeff, I decided I have been doing this long enough now that I should probably start calling the Neutrals by their correct term ie the Grounded Conductors, and now you spring the parallel conductors on me.
Reply With Quote
  #9  
Old 3/25/09, 4:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Square D Neutral Double Tap

I just don't want you getting too comfortable. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 3/26/09, 12:40 PM
mmurphy4 mmurphy4 is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Springfield Illinois
Posts: 48
Default Re: Square D Neutral Double Tap

Thanks guys,
I wasnt sure if the manufacturer allowed it or not. Thanks for the help Mr. Pope. It was reassuring to hear that you have never seen a Square D panel that allowed this. Told them its not up to the 2002 NEC code, but is only a hazard when working on one of the two double tapped circuits. I'll let them figure out what to do about it.



Matt Murphy
Murphy Home Inspections
Springfield Illinois
Reply With Quote
  #11  
Old 3/26/09, 5:18 PM
mmurphy4 mmurphy4 is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Springfield Illinois
Posts: 48
Default Re: Square D Neutral Double Tap

Ok seriously, I've gotten 4 phone calls already about this situation. The electrician, both realtors, the home owner. I just keep telling them, it is potentially unsafe when someone is working on one of those circuits, it is safe under normal usage. I am somewhat new, do they always have such a fit when this is called out?



Matt Murphy
Murphy Home Inspections
Springfield Illinois
Reply With Quote
  #12  
Old 3/26/09, 5:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Square D Neutral Double Tap

Tell them that the electrician has the final say, so long as he puts it in writing. Move on.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 3/26/09, 9:25 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Square D Neutral Double Tap

I find this condition in the majority of the homes I inspect. I always write it up, but have never had a follow-up call about it. Maybe they are just ignoring me?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #14  
Old 3/27/09, 9:55 AM
Peter Foxe Smothers's Avatar
Peter Foxe Smothers Peter Foxe Smothers is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Shreveport, LA
Posts: 912
Default Re: Square D Neutral Double Tap

Quote:
Originally Posted by mmurphy4 View Post
Thanks guys,
I wasnt sure if the manufacturer allowed it or not. Thanks for the help Mr. Pope. It was reassuring to hear that you have never seen a Square D panel that allowed this. Told them its not up to the 2002 NEC code, but is only a hazard when working on one of the two double tapped circuits. I'll let them figure out what to do about it.

Also, do not site code during your home inspection or in your inspection report. Your doing a general home inspection not a code inspection. Current building practices or current building standards are both good substitutes for the code word.



Foxe Smothers ( Owner / Inspector )
Pelican State Inspection
Your Best Choice for Home Inspection in the Shreveport & Bossier City Area!


www.PelicanState.Net
www.ShreveportHomeInspector.net
www.BossierCityHomeInspector.net
foxe@pelicanstate.net
LSBHI #10399
Reply With Quote
  #15  
Old 3/27/09, 10:32 AM
mmurphy4 mmurphy4 is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Springfield Illinois
Posts: 48
Default Re: Square D Neutral Double Tap

Thanks for the advice. I did not put the code into the report. The buyer asked specifically if it was up to code so I told him. I dont really know specific building codes unless I do research on a topic, which I did on this one.



Matt Murphy
Murphy Home Inspections
Springfield Illinois
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Square D double taps abishop Electrical Inspections 3 10/29/06 9:01 AM
Square D Files Lawsuit to Prevent Counterfeiting jtedesco1 Electrical Inspections 2 5/26/06 6:36 PM


All times are GMT -4. The time now is 8:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts