  #1  
Old 4/27/11, 10:17 AM
Ken Peckham Ken Peckham is offline
InterNACHI Member
 
Join Date: Apr 2011
Location: St. John's, Newfoundland, Canada
Posts: 107
Default Stab-lok panel

Hello,

I'm a new inspector, and I'm in the process of doing some mock inspections. I have found a FP Stablok panel on a new home built in 2009. Is this a major concern?

Thanks,

Ken
Attached Thumbnails
stab-lok-panel-dscf0436.jpg   stab-lok-panel-dscf0437.jpg   stab-lok-panel-dscf0438.jpg   stab-lok-panel-dscf0439.jpg  
Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/27/11, 10:33 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Stab-lok panel

WARNING! You are not to remove this panel because it exposes the service area.
The authority having juristiction has not given the OK.
And they are dangerous according to most InterNachi Inspectors.
Even if they are in new condition they still have the same problems.
I do not like that the service portion is on the bottom also.

You have a Federal Pacific panel which is legal, but there is a possibility that the circuit breakers may not trip when shorted possibly causing an electrical hazard. Opinions by licensed electricians on this panel varies between safe and unsafe. I recommend you consult a licensed electrician for an opinion and correct if necessary.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #3  
Old 4/27/11, 10:55 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Stab-lok panel

Ken - I will assume you are in Canada as your profile is incomplete.

These are commonplace in Canada.

Kevin - can you explain your response? Why would an inspector remove the panel?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 4/27/11, 11:14 AM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 194
Default Re: Stab-lok panel

This is Federal Pioneer ! Been around for about 50 years I have used them , been around them , never seen a problem yet . If you are in doubt with any panel (regardless of brand) you should never remove the dead front . Now I have seen a Siemans blown apart . , have seen one with a breaker parted in two pieces . Any panel can be dangerous !



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #5  
Old 4/27/11, 11:21 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Stab-lok panel

A new inspector should not remove the dead front cover.
Seasoned and trained in proper electrical schooling with proper safety equipment is OK on some panels and not OK on others.
This is part of the training process.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 4/27/11, 11:23 AM
Ken Peckham Ken Peckham is offline
InterNACHI Member
 
Join Date: Apr 2011
Location: St. John's, Newfoundland, Canada
Posts: 107
Default Re: Stab-lok panel

Yes, I'm in Canada. I did not remove the Deadfront, would this be common pratice on this type of panel? It looks like the design of the breakers makes removing the Deadfront a bit of a problem as they extend over the Deadfront.

Thanks for all your help!

Ken
Reply With Quote
  #7  
Old 4/27/11, 11:40 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,107
Default Re: Stab-lok panel

Correct



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 4/27/11, 11:58 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Stab-lok panel

Still manufactured and approved in Canada .
I expect there is a difference from USA panels .
I have a 200 amp in my home no big deal . Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #9  
Old 4/27/11, 7:32 PM
Ken Peckham Ken Peckham is offline
InterNACHI Member
 
Join Date: Apr 2011
Location: St. John's, Newfoundland, Canada
Posts: 107
Default Re: Stab-lok panel

Quote:
Originally Posted by rcooke View Post
Still manufactured and approved in Canada .
I expect there is a difference from USA panels .
I have a 200 amp in my home no big deal . Roy
OK would you report the "Stab-lok" issues in the report or not mention it?

Thanks,

Ken
Reply With Quote
  #10  
Old 4/27/11, 7:43 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stab-lok panel

Are the Canadian FPE's profoundly different than the firestarters that we have here in the US?
Reply With Quote
  #11  
Old 4/27/11, 7:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Stab-lok panel

Quote:
Originally Posted by Robert Meier View Post
Are the Canadian FPE's profoundly different than the firestarters that we have here in the US?
Apparently so

I've seen no difference in designed components - same key-holed bus bars, same Stab-lok breakers - but Canadians are still installing these things in new construction. Although they are now Federal Pioneer.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 4/27/11, 7:51 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stab-lok panel

Quote:
Originally Posted by jpope View Post
Apparently so

I've seen no difference in designed components - same key-holed bus bars, same Stab-lok breakers - but Canadians are still installing these things in new construction. Although they are now Federal Pioneer.

So I'm guessing that they've changed some elements of the design to fix the problems we have with the equipment from the 60's and 70's.
Reply With Quote
  #13  
Old 4/27/11, 9:38 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Stab-lok panel

Quote:
Originally Posted by kpeckham View Post
OK would you report the "Stab-lok" issues in the report or not mention it?

Thanks,

Ken
What issues there are approved in Canada .

I do report size and manfacture of all panels .

The answer is NO report ,and do not mention it .

I have seen no reason to say any thing.



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/28/11, 12:27 AM
Richard L. Overton Richard L. Overton is offline
InterNACHI Member
 
Join Date: Apr 2009
Posts: 16
Default Re: Stab-lok panel

Federal pacific here in the US. You have Federal Pioneer. In the US the UL carefully looked at the federal Pacific breakers and there associated problems. After review, they did NOT revoke the UL rating, contrary to what most believe. I report that these panels have been known to fail to open under heavy load and also fail to open when manually turned off. This is really all I can say, as that is the extent of what UL found and what I have experienced. Additionally, the problem was limited to specific sizes of breakers ( size I cannot recall).
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts