Default "Standard" recptacle in floor

In a cabinet.

I'm recommending a receptacle approved for floor mount, but was curious if this could be an exception.

TIA
Attached Thumbnails
standard-recptacle-floor-dsc05575.jpg  
Reply With Quote
Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America)
  #2  
Old 1/3/10, 11:02 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,568
Default Re: "Standard" recptacle in floor

as it is inside a cabinet I'm not sure it could really count as a floor mount receptacle Rick...be interesting to see what one of the sparkies have to say



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 1/3/10, 11:16 PM
Larry J. Michael Larry J. Michael is offline
InterNACHI Member
 
Join Date: Nov 2009
Location: Greensboro, N. C.
Posts: 732
Default Re: "Standard" recptacle in floor

Not a sparkie, but I can see your point as dust and debris could still into the receptacle.



Greensboro Home Inspection
Providing home inspections in Greensboro, High Point, Burlington and the surrounding areas.
greensboro-home-inspection.html

Raleigh Home Inspection
Home inspections in Raleigh, Durham, Cary, Chapel Hill, Apex and surrounding areas.
Raleigh-home-inspection.html

BassRumors.com
Providing a blog, news, and forum dedicated to bass fishing.
Reply With Quote
  #4  
Old 1/3/10, 11:17 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: "Standard" recptacle in floor

Client has two children and were talking about the storage space (previous owner obviously had AV equipment here) for games, toys etc.

Sure would hate to see one of them reaching in there with that outlet on a regular basis.

I am curious as to the sparky's opinions too.
Reply With Quote
  #5  
Old 1/4/10, 8:25 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: "Standard" recptacle in floor

314.27(C) Floor Boxes. Boxes listed specifically for this application
shall be used for receptacles located in the floor.

Exception: Where the authority having jurisdiction judges
them free from likely exposure to physical damage, moisture,
and dirt, boxes located in elevated floors of show
windows and similar locations shall be permitted to be
other than those listed for floor applications. Receptacles
and covers shall be listed as an assembly for this type of
location.

If the receptacles are in a cabinet then the NEC will not have a say on it. In your example, 314.27(C) does not apply...but I felt it would be nice to post it. Now, in your case I would examine it and see what it looks like. If it looks clean and clear I probably would not say anything about it.

If you really want to protect a child from it, recommend tamper resistant devices and protect with GFCI otherwise you wanted an electricians take and you know we are going to stick to what the code says...which leaves you up to your own personal views and you are free to do that as HI's.



Paul W. Abernathy
Reply With Quote
  #6  
Old 1/4/10, 8:29 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: "Standard" recptacle in floor

P.S. You topic title is misleading...the receptacle is not actually IN the floor....lol



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Commercial Electrical Inspections jtedesco1 Commercial Inspections 29 1/12/08 5:03 AM
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Moisture control for slab on grade in protecting floor finishes mcyr General Inspection Discussion 2 8/13/07 7:53 PM


All times are GMT -4. The time now is 8:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts