Default Steel Trusses and Conductors

I was inspecting a steel frame home. While in the attic space i noticed the electrical conductors for the house lying along the edges of the steel trusses.

My thoughts were that if one was in the attic and stepped on a wire just right and sliced it it would charge the whole attic.
When running wires in attics with steel frame trusses is there anything required to protect conductors from getting damaged/cut
Reply With Quote
  #2  
Old 2/25/07, 9:22 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Steel Trusses and Conductors

Hi Matthew,

Yes those conductors should be protected from any potential damage with either, bushings, conduit or a nailer attached to the steelwork. As you have stated this setup has the ability to energize the framing.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 2/25/07, 9:45 AM
Mathew Hawley Mathew Hawley is offline
Active Poster
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Steel Trusses and Conductors

Thanks Gerry
Reply With Quote
  #4  
Old 2/25/07, 10:54 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel Trusses and Conductors

First off, metal framing should be bonded. This will prevent any chance of "energizing" it.

Second, yes, if passing through holes in the framing there must be protection. If the cables are just laying across the outside of the framing, and they are well away from the scuttle hole, and clear of being stepped on, there is no protection required.
Reply With Quote
  #5  
Old 2/25/07, 11:09 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Steel Trusses and Conductors

Is the attic designed to be commonly accessed?

tom
Reply With Quote
  #6  
Old 2/25/07, 12:56 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel Trusses and Conductors

Got any pictures? I'd like to see what the attic of a steel framed dwelling might look like.
Reply With Quote
  #7  
Old 2/25/07, 2:00 PM
Mathew Hawley Mathew Hawley is offline
Active Poster
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Steel Trusses and Conductors

I do not have pictures, however there were wires at the scuttle entrance and around the air handler unit.

I was also given this information:

250.104 Bonding of Piping Systems and Exposed Structural Steel.
- - (C) Structural Steel. Exposed structural steel that is interconnected to form a steel building frame and is not intentionally grounded and may become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with Table 250.66 and installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible.

Thank you all for your replies.
Reply With Quote
  #8  
Old 2/25/07, 2:14 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,843
Default Re: Steel Trusses and Conductors

Metal framing is an excellent conductor of electricity. Therefore extra caution shall be observed too avoid contacting energized electrical conductors (wiring) when entering or working in the subject property attic space for equipment servicing or other purposes. Never install service or storage platform materials atop the electrical wiring.

If anyone is dumb enough to directly contact, step on or stand on wiring, no matter the location they may deserve the consequences.

Thinning of the gene pool is necessary in certain cases.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 9/30/08 at 4:16 PM..
Reply With Quote
  #9  
Old 2/25/07, 2:29 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Steel Trusses and Conductors

Found this: http://www.mikeholt.com/videodisplaynew.php?pageid=4328

250.104(c) There is a comment about metal studs, and requirements.

tom
Reply With Quote
  #10  
Old 2/25/07, 3:13 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel Trusses and Conductors

Florida has added bonding steel studs to the building code but the NEC does not require it.
I can see where it would be likely that an inspector would require all RX in the attic of a steel framed building to be secured. They are pretty conscientous in this county about making sure ALL wiring in the attic is secured before the ceiling drywall goes up. If you see loose RX it was put there after the FEPAC. Steel trussers are still pretty rare here so the wiring is going to be laying on wood truss chords. Where it comes through the steel wall members it is required to be in grommets and also draft stopped.
Reply With Quote
  #11  
Old 2/25/07, 3:16 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Steel Trusses and Conductors

Steel studs are not "structural" steel. They have virtually no load bearing capability in the guage you see in residential construction. A load beraring wall will still be wood.
Reply With Quote
  #12  
Old 2/25/07, 4:10 PM
Mathew Hawley Mathew Hawley is offline
Active Poster
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Steel Trusses and Conductors

Thomas,
very helpful video.

Thanks everyone for your input.
Reply With Quote
  #13  
Old 2/25/07, 4:30 PM
Mathew Hawley Mathew Hawley is offline
Active Poster
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Steel Trusses and Conductors

Here is a intresting video/story

http://www.local6.com/money/7302637/detail.html
Reply With Quote
  #14  
Old 2/25/07, 4:45 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,843
Default Re: Steel Trusses and Conductors

Quote:
Originally Posted by Greg Fretwell
Steel studs are not "structural" steel. They have virtually no load bearing capability in the guage you see in residential construction. A load beraring wall will still be wood.
Check IRC R603

I think that disputes your statement and the home in my photos complies, no wood except for blocking or backing.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #15  
Old 2/25/07, 5:00 PM
Mathew Hawley Mathew Hawley is offline
Active Poster
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Steel Trusses and Conductors

Hello Greg,

I looked at the home under construction next to the one i inspected. It was steel frame all the way around, including all interior walls. The only wood was the roof sheathing.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Steel Trusses and Conductors mhawley Structural Inspections 3 2/25/07 2:25 PM


All times are GMT -4. The time now is 9:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts