Default Step Down Transformer

Inspected a commercial building today with four step down transformers. Three of the four were operating at between 80 and 85 deg f. The fourth was at 168 f. Two of the four are 25 kva @ 575 down to 240/120vac. the others are 15kva @ 575 down to 240/120vac.They are all located in the same mechanical room. I know they are all rated @80deg celcius and the 168 deg f falls within that but can anyone offer an expanation as to why the one is running at a higher temperature than the others. Is it possible that the load being drawn on the higher temp transformer is higher and causing the higher temperature reading.
Reply With Quote
  #2  
Old 10/27/08, 10:14 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 188
Gary T. Heller is often very helpful Gary T. Heller is often very helpful
Default Re: Step Down Transformer

That transformer is probably just drawing more current than the other two. The higher the load, the higher the temp.
Reply With Quote
  #3  
Old 10/27/08, 10:17 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,897
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Step Down Transformer

Quote:
Originally Posted by gheller View Post
That transformer is probably just drawing more current than the other two. The higher the load, the higher the temp.
What he said. These things can get pretty freaking hot when they're loaded closer to their maximum rated capacity. Some are even rated to be overloaded for short periods of time. There can be some serious heat rolling out of them puppies sometimes and still be completely within spec.
Reply With Quote
  #4  
Old 10/27/08, 11:22 PM
Stewart Mussolum Stewart Mussolum is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: london, On
Posts: 6
Stewart Mussolum hasn't had much positive or negative feedback
Default Re: Step Down Transformer

Thanks guys
Reply With Quote
  #5  
Old 10/28/08, 3:21 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 242
Frank P. Newman is generally well trusted
Default Re: Step Down Transformer

Remember also that the nameplate temperature rating is the allowable temperature RISE over a standard ambient (usually 40 deg C). As mentioned before that can result in very hot running temps for a heavily-loaded transformer.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #6  
Old 11/1/08, 9:14 PM
Randall Romoser's Avatar
Randall Romoser Randall Romoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 171
Randall Romoser has had a little positive feedback
Default Re: Step Down Transformer

Does the transformer in question have the proper clearances to walls to allow for ventilation? Typically 6 inches is minimum wall clearance. Also a very dusty/dirty transformer runs hotter.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Transformer humming noise mnicholet Electrical 13 11/25/08 5:05 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
Step crack leading to further cracks gmendes Structural 4 6/21/07 11:40 AM
Step cracks in stucco on block home dbucknavich Structural 0 5/19/06 8:01 PM


All times are GMT -4. The time now is 6:29 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics