Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information
Default Strand copper wire.

Did an inspection a while back, and much of the wiring looked as if it had been replaced.

My question is this. The wiring for the 15 and 20 amp circuits was all copper stranded wiring, instead of the solid copper I usually see. I assumed at the time it was fine, but for some reason, this came back to me and caused me to question. It stranded copper okay for lower amperage circuits?
Reply With Quote
  #2  
Old 10/31/08, 6:46 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 3,670
James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute
Default Re: Strand copper wire.

was it the appropriate size and in conduit Mark ???



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 10/31/08, 7:59 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: St. Peters, MO
Posts: 2,194
Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information
Default Re: Strand copper wire.

Quote:
Originally Posted by jmckee View Post
was it the appropriate size and in conduit Mark ???
Yea, it looked like the correct gage.
Reply With Quote
  #4  
Old 10/31/08, 8:04 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 3,670
James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute James F. McKee has a reputation beyond repute
Default Re: Strand copper wire.

if it is the correct gauge and in protected conduit my understanding is it's fine....sure one of the sparky's will have a better explanation



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 10/31/08, 8:09 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is online now
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,208
Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Strand copper wire.

Hi Mark,

if the conductors were in a conduit then its likely that they used stranded copper wire of the correct gauge as it is much easier to pull through than single strand.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #6  
Old 11/2/08, 2:17 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,897
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Strand copper wire.

Like everyone said, if this was a conduit job, stranded is fine. Some people like to work with stranded better when pulling in conduit.

If this was cable, stranded would be a red flag. There were only a couple very special cables ever manufactured for general building wiring that featured stranded conductors. Normally, when you see a stranded cable connected in a panel, that's normally your clue that someone improperly did some wiring with rubber cord or something like that.
Reply With Quote
  #7  
Old 11/2/08, 3:54 PM
Ms Sparky Ms Sparky is offline
New User
 
Join Date: Sep 2008
Posts: 25
Ms Sparky is generally well trusted
Please Note: Ms Sparky is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Strand copper wire.

If properly installed, the stranded is fine. I would check the devices, ie...receptacles and switches and make sure they used the right type and didn't try to stab stranded wire into the back or put stranded wire under a screw connector. I've seen that a lot. The devices have to be "listed" for stranded wire.

Ms Sparky
http://mssparky.com/
Reply With Quote
  #8  
Old 11/2/08, 5:22 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 229
Jeffrey R. Wicklander is often very helpful Jeffrey R. Wicklander is often very helpful
Default Re: Strand copper wire.

What's wrong with a screw connector?

Jeff
Reply With Quote
  #9  
Old 11/2/08, 5:24 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: St. Peters, MO
Posts: 2,194
Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information Mark Nahrgang is very trusted source of information
Default Re: Strand copper wire.

Quote:
Originally Posted by Ms Sparky View Post
If properly installed, the stranded is fine. I would check the devices, ie...receptacles and switches and make sure they used the right type and didn't try to stab stranded wire into the back or put stranded wire under a screw connector. I've seen that a lot. The devices have to be "listed" for stranded wire.

Ms Sparky
http://mssparky.com/
I didn't pull any outlet covers (never do) to check the receptacles and switches. The wires were run through conduits, so from what I'm reading, I'm thinking that this was just fine. Just out of curiosity though, if back stabbing, and under a screw connector isn't correct, then what is? There was nothing different in the service panel, lugged like you always see it.
Reply With Quote
  #10  
Old 11/2/08, 5:34 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,897
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Strand copper wire.

Quote:
Originally Posted by mnahrgang View Post
Just out of curiosity though, if back stabbing, and under a screw connector isn't correct, then what is? There was nothing different in the service panel, lugged like you always see it.
There are "backwired" receptacles which agree with stranded wires much better. They have a hole, like backstabbed, but the conductor gets trapped between two plates inside when you tighten the screw on the side.

Most every screw terminal receptacle nowadays is okay'd for use with stranded conductors, however, but it's not that easy to do. It would be very unusual to find a screw terminal that said "solid wire only".
Reply With Quote
  #11  
Old 11/3/08, 7:32 PM
Ms Sparky Ms Sparky is offline
New User
 
Join Date: Sep 2008
Posts: 25
Ms Sparky is generally well trusted
Please Note: Ms Sparky is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Strand copper wire.

Mark you are right. It took a little bit to convince me, but you are. I'm glad you caught that. I must be spending too much time at the Nukes. Different standards. I still don't recommend it for "side-wire (binding screw)". But it's not illegal.

Here's the UL White Book page that describes it.

TERMINALS

Terminals of 15 and 20 A receptacles not marked "CO/ALR" are for use with copper and copper-clad aluminum conductors only. Terminals marked "CO/ALR" are for use with aluminum, copper and copper-clad aluminum conductors.
Terminals of receptacles rated 30 A and above not marked "AL-CU" are for use with copper conductors only. Terminals of receptacles rated 30 A and above marked "AL-CU" are for use with aluminum, copper and copper-clad aluminum conductors.
Terminals marked "75 C" may be wired using the ampacities for conductors rated 75°C as well as conductors rated 60°C in Table 310.16 of the NEC.
Terminals of the wire-binding screw, setscrew, or screw-actuated back wired clamping types are suitable for use with both solid and stranded building wires.
Screwless terminal connectors of the conductor push-in type (also known as "push-in-terminals") are restricted to 15 A branch circuits and are for connection with 14 AWG solid copper wire only. They are not intended for use with aluminum or copper-clad aluminum wire, 14 AWG stranded copper wire, or 12 AWG solid or stranded copper wire.
Single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have been investigated to feed branch-circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
  • Back wire (screw actuated clamp type) terminations with multiple wire access holes used concurrently to terminate more than one conductor
  • Side wire (binding screw) terminals used concurrently with their respective push-in (screwless) terminations to terminate more than one conductor
Single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have not been investigated to feed branch-circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
  • Side wire (binding screw) terminal with its associated back wire (screw actuated clamp type) terminal
  • Multiple conductors under a single binding screw
  • Multiple conductors in a single back wire hole
Duplex receptacles rated 15 and 20 A that are provided with break off tabs may have those tabs removed so that the two receptacles may be wired in a multi-wire branch circuit.

Ms Sparky
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 4 3/25/07 11:41 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical 9 8/28/06 2:08 AM


All times are GMT -4. The time now is 7:21 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics