Is stranded (not solid) copper wire allowed when making connections in the breaker box? Hopefully the picture will load and you can see the wires.
Thank you in advance, Louis |
|
#2
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
I don't see a problem, but I am Canadian.
|
|
#3
|
|||
|
|||
|
Stranded is okey dokey.
|
|
#4
|
||||
|
||||
|
One caveat to be aware of concerning stranded wires in a breaker panel is to be on the look out for those times when the diameter of the wire is too large to fit into the lug and some clever little spud decides to "trim" some of the strands off to make it fit.
|
|
#5
|
|||
|
|||
|
Please Note:
Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
is a non-member guest and is in no way affiliated with InterNACHI or its members.
As long as the stranded wire is not from an extension chord.
|
|
#7
|
||||
|
||||
|
Last edited by dedwards; 3/2/06 at 9:52 PM.. |
|
#8
|
|||
|
|||
|
Thank you everyone for your answers.
The NACHI message board ROCKS!! Louis, Treesh Home Inspections |
|
#9
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
isn't there different lugs for stranded wire??
|
|
#10
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
There are different lugs for "fine stranded wire" but this refers to the very fine wire you use for battery cables and such. It becomes a problem in photovoltaic arrays where this type of wire can be used.The regular THHN/THWN style wire can be used in normal lugs.
|
|
#11
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
thanx Greg, for clearing that up. i knew i'd seen "strand wire lugs" in supply houses, but was unsure of there use.
|
|
#12
|
|||
|
|||
|
Answered my question today........Search and you shall find.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 2 | 1/8/11 8:04 PM |
| Chimney flashing photo's needed: brick and stone done correctly | kshepard | Exterior Inspections | 6 | 10/13/07 9:10 AM |
| Electrical Guru Question? Breaker lock outs | pdoane | Electrical Inspections | 4 | 9/7/07 3:05 PM |
| Bathroom Shut-off Valves - Mineral deposits - Do you note them as leaking in reports? | jwatts1 | Plumbing Inspections | 8 | 7/29/06 12:50 PM |
| Looking for comment by Caoimhín P. Connell | phinsperger | Ancillary Inspection Services & Additional Topics | 2 | 2/18/06 12:22 PM |