Default Stranded Copper Grounding Electrode Conductor

I think this is the first time I've seen anything other than solid copper, 6 AWG, used as the GEC. The elect. system and the CSST gas piping were grounded to to two separate rods using stranded copper wire.

Is this allowed? I couldn't find anything that specified it had to be solid copper. (Photos of gas and elect. system grounding attached.)

stranded-copper-grounding-electrode-conductor-021009-046.jpg stranded-copper-grounding-electrode-conductor-021009-041.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #2  
Old 2/11/09, 6:01 AM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded Copper Grounding Electrode Conductor

Hi,

The stranded ground is ok bare or insulated but it's the size that concerns me. Is that a 200 Amp service? Judging by the picture it looks to be about a 2" PVC conduit.

Mike
Reply With Quote
  #3  
Old 2/11/09, 6:21 AM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded Copper Grounding Electrode Conductor

Hi,

While my first post awaits moderation, if this is a 100 Amp service the ground is fine.

I apologize, I do see that you said two separate rods. Do systems in the US not need 2 ground rods spaced a ten feet apart with a continuous run to the second rod?

Mike

Last edited by Michael Thellend; 2/11/09 at 11:09 AM..
Reply With Quote
  #4  
Old 2/11/09, 7:22 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,255
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Stranded Copper Grounding Electrode Conductor

Hi Joe,

I with you, I've never seem stranded used for the ground but can't say its wrong, however I doubt that the acorn clamp on the driven rod is correct when using stranded conductors.

Maybe one of our resident Sparkies can clear this up (if we haven't scared them all off)

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 2/11/09, 7:27 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 11,748
Default Re: Stranded Copper Grounding Electrode Conductor

I was under the assumption it had to be solid
Reply With Quote
  #6  
Old 2/11/09, 7:43 AM
Douglas Cossar, CMI.'s Avatar
Douglas Cossar, CMI. Douglas Cossar, CMI. is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Whitby, On
Posts: 1,717
Default Re: Stranded Copper Grounding Electrode Conductor

We see stranded copper ground wires in our neck of the woods all the time

Cheers



Doug Cossar CMI, CNHI
Accurate Home Inspection
Services Inc.
Whitby Ontario
Serving Pickering, Ajax, Whitby, Oshawa, Clarington and surrounding areas
www.accuratehomeinspections.ca
05021384
Reply With Quote
  #7  
Old 2/11/09, 7:48 AM
Larry Kage, CMI Larry Kage, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: NW, MI
Posts: 10,870
Default Re: Stranded Copper Grounding Electrode Conductor

Quote:
Originally Posted by dcossar View Post
We see stranded copper ground wires in our neck of the woods all the time

Cheers
Same.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/
____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
whis11 @ charter.net
The above post represents my personal opinion.
Reply With Quote
  #8  
Old 2/11/09, 8:13 AM
jallcroft jallcroft is offline
InterNACHI Member
 
Join Date: Apr 2008
Location: Springfield, VA
Posts: 65
Default Re: Stranded Copper Grounding Electrode Conductor

Same here, if you have ever seen lightening arrest wiring it is also stranded, in fact it actually appears to be braided. The green wire appears to be undersized, might be the pic tho...
Reply With Quote
  #9  
Old 2/11/09, 8:24 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 11,748
Default Re: Stranded Copper Grounding Electrode Conductor

See what happens when we assume lolol
Reply With Quote
  #10  
Old 2/11/09, 9:00 AM
bemelander bemelander is offline
Active Poster
 
Join Date: Nov 2003
Location: Grand Rapids, MI
Posts: 342
Please Note: bemelander is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded Copper Grounding Electrode Conductor

Stranded is the standard in my neck of the woods

Bill
Reply With Quote
  #11  
Old 2/11/09, 4:15 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Stranded Copper Grounding Electrode Conductor

The ground rod conductor can be solid or stranded. It needs to identified with a green marking or be bare. #6 awg. is the largest size needed unless a job spec. states otherwise. Regarding the clamp on the gas pipe. it appears to be aluminum alloy which is not approved for wet locations. Tis wire also needs to be protected againstphysical damage.
Reply With Quote
  #12  
Old 2/14/09, 8:32 AM
Bob Electric Bob Electric is offline
New User
 
Join Date: Dec 2007
Location: 84,Pa.15330
Posts: 9
Please Note: Bob Electric is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded Copper Grounding Electrode Conductor

That is all I use for G.E.C. Less labor,little more cost. Power company o.k. with it.
Reply With Quote
  #13  
Old 2/16/09, 5:30 PM
Paul W. Abernathy, CMI Paul W. Abernathy, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania,VA
Posts: 8,550
Send a message via Skype™ to pabernathy
Default Re: Stranded Copper Grounding Electrode Conductor

Quote:
Originally Posted by gbeaumont View Post
Hi Joe,

I with you, I've never seem stranded used for the ground but can't say its wrong, however I doubt that the acorn clamp on the driven rod is correct when using stranded conductors.

Maybe one of our resident Sparkies can clear this up (if we haven't scared them all off)

Regards

Gerry
250.62 Grounding Electrode Conductor Material.
The
grounding electrode conductor shall be of copper, aluminum,
or copper-clad aluminum. The material selected shall
be resistant to any corrosive condition existing at the installation
or shall be suitably protected against corrosion. The
conductor shall be solid or stranded, insulated, covered, or
bare.


P.S....scare us off.....I hear ya !



Paul Abernathy
Electrical Industry Associate


Disclaimer - All my posts on this forum are of my own personal opinion and in no way represent the opinions of any association, organization or affiliation. The voices in my head are mine and mine alone.
Reply With Quote
  #14  
Old 2/20/09, 2:43 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded Copper Grounding Electrode Conductor

It is very common to used stranded conductors for grounding electrode conductor however there is one item it need to be addressed.,

IMO looks like too small to me unless the photo play trick on my eyes.

It should have second rod near by minum of 2 meter{6 feet } away.

Speaking of gas pipe that conductor is correct size if 100 amp main OCPD there if 200 amp no it is too small and I am not 100 % famuair with OP's local code requirement related to bonding on gas pipe so I will leave that answer to OP's electrician whom they are famuair in that area.

Merci,Marc
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 2:00 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM

All times are GMT -4. The time now is 12:35 PM.
no new posts