I think this is the first time I've seen anything other than solid copper, 6 AWG, used as the GEC. The elect. system and the CSST gas piping were grounded to to two separate rods using stranded copper wire.
Is this allowed? I couldn't find anything that specified it had to be solid copper. (Photos of gas and elect. system grounding attached.)
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#2
|
||||
|
||||
|
Please Note:
Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hi,
The stranded ground is ok bare or insulated but it's the size that concerns me. Is that a 200 Amp service? Judging by the picture it looks to be about a 2" PVC conduit. Mike |
|
#3
|
||||
|
||||
|
Please Note:
Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hi,
While my first post awaits moderation, if this is a 100 Amp service the ground is fine. I apologize, I do see that you said two separate rods. Do systems in the US not need 2 ground rods spaced a ten feet apart with a continuous run to the second rod? Mike Last edited by Michael Thellend; 2/11/09 at 11:09 AM.. |
|
#4
|
||||
|
||||
|
Hi Joe,
I with you, I've never seem stranded used for the ground but can't say its wrong, however I doubt that the acorn clamp on the driven rod is correct when using stranded conductors. Maybe one of our resident Sparkies can clear this up (if we haven't scared them all off) Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#5
|
||||
|
||||
|
I was under the assumption it had to be solid
|
|
#6
|
||||
|
||||
|
We see stranded copper ground wires in our neck of the woods all the time
Cheers Doug Cossar CMI, NHI Accurate Home Inspection Services Inc. Whitby Ontario www.accuratehomeinspections.ca 05021384 |
|
#7
|
|||
|
|||
|
Same.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#8
|
|||
|
|||
|
Same here, if you have ever seen lightening arrest wiring it is also stranded, in fact it actually appears to be braided. The green wire appears to be undersized, might be the pic tho...
|
|
#9
|
||||
|
||||
|
See what happens when we assume lolol
|
|
#10
|
|||
|
|||
|
Stranded is the standard in my neck of the woods
Bill Bill Emelander Professional Edge Home Inspection Grand Rapids and all of West Michigan NACHI #03111914 www.proedgehi.com |
|
#11
|
||||
|
||||
|
The ground rod conductor can be solid or stranded. It needs to identified with a green marking or be bare. #6 awg. is the largest size needed unless a job spec. states otherwise. Regarding the clamp on the gas pipe. it appears to be aluminum alloy which is not approved for wet locations. Tis wire also needs to be protected againstphysical damage.
|
|
#12
|
|||
|
|||
|
Please Note:
Bob Electric is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is all I use for G.E.C. Less labor,little more cost. Power company o.k. with it.
|
|
#13
|
|||
|
|||
|
Quote:
250.62 Grounding Electrode Conductor Material. The grounding electrode conductor shall be of copper, aluminum, or copper-clad aluminum. The material selected shall be resistant to any corrosive condition existing at the installation or shall be suitably protected against corrosion. The conductor shall be solid or stranded, insulated, covered, or bare. P.S....scare us off.....I hear ya ! Paul W. Abernathy |
|
#14
|
|||
|
|||
|
Please Note:
Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
It is very common to used stranded conductors for grounding electrode conductor however there is one item it need to be addressed.,
IMO looks like too small to me unless the photo play trick on my eyes. It should have second rod near by minum of 2 meter{6 feet } away. Speaking of gas pipe that conductor is correct size if 100 amp main OCPD there if 200 amp no it is too small and I am not 100 % famuair with OP's local code requirement related to bonding on gas pipe so I will leave that answer to OP's electrician whom they are famuair in that area. Merci,Marc |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What do you think? Can this work for you? | jtedesco1 | Electrical Inspections | 21 | 2/26/11 2:00 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Where is it written.... | bgromicko | General Inspection Discussion | 21 | 1/19/08 9:02 PM |