Default Stranded wires lower gauges

This home has a lot of lower gauge stranded wire. 10-14 Gauge. The connections are poor.

Q. What are you thoughts on stranded wire for the higher gauge wires? Normally I see from SEC to the 8 gauge as stranded which is OK.

The home also had black iron gas pipe being used as conduit.

Q. Any comments on the gas piping?

There also was an odd type of receptacle for the refrigerator. It tripped liked a GFCI and buzzed when tripped.

Q. Any thoughts on this type of receptacle.

Thanks

I did catch a 40 amp brreaker with 20 amp wire and missing knock out.

Older K & T

No grounding jumper @ main.

Inproper grounding @ garage sub. One wasnt connected. The others when to the box. (This may be OK if conduit is continuous to the main) Q. Wheres the subs grounding bar?

I deffered to a sparky.
Attached Thumbnails
stranded-wires-lower-gauges-90407-021-small-.jpg.jpg
Views:	94
Size:	63.1 KB
ID:	8768   stranded-wires-lower-gauges-90407-020-small-.jpg.jpg
Views:	79
Size:	69.0 KB
ID:	8769   stranded-wires-lower-gauges-90407-037-small-.jpg.jpg
Views:	85
Size:	56.1 KB
ID:	8770   stranded-wires-lower-gauges-90407-031-small-.jpg.jpg
Views:	74
Size:	24.4 KB
ID:	8771   stranded-wires-lower-gauges-90407-011-small-.jpg.jpg
Views:	87
Size:	46.5 KB
ID:	8773  

Reply With Quote
  #2  
Old 1/29/07, 1:06 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stranded wires lower gauges

Dave,

I will attempt to answer a few here....basically anything in conduit 8 AWG or OVER is required to be stranded. Absolutly nothing wrong with stranded wire in my opinion as it is your ONLY real option in larger conductors.

AHH.......if GAS piping is being used as electrical conduit....GREAT CALL...and defer this as the pipe was not intended to be used for this purpose.

Ahh.....looks like a replacement model GFCI to me....looks like it has a reset on it and test button.

On the 40A breaker on a 20A wire, just be sure it was not in compliance with the nameplate rating on the HVAC system...for example if the nameplate said Max OCPD 40A and Minimum Wire 12 AWG then it would technically be fine according to the NEC....but only you can make that statement knowing if you saw the system labeled as such...if it was a normal branch circuit then yes it is wrong.

Missing KO's.....a given..

If you are refering to the last image...that method of attaching the EGC's is wrong and should be terminated on a buss properly.

Defer this to the electrical contractor with your list of things they should evaluate.
Improper bonding and so on at the sub-panels ( remote distribution panels )



Paul W. Abernathy
Reply With Quote
  #3  
Old 1/29/07, 1:11 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Stranded wires lower gauges

Thank you Mr electrical Guru
Reply With Quote
  #4  
Old 1/29/07, 4:18 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Stranded wires lower gauges

Black Pipe!!!

I had an inspector warn me about the possible rush of black pipe being used as conduit. He had a home owner run conduit, and the inspector recognized it as black pipe. The home owner argued that it was ok, because some fool in an orange apron said so.

Damn Orange Aprons!

tom

Last edited by tdietrich1; 1/29/07 at 4:28 PM..
Reply With Quote
  #5  
Old 1/29/07, 4:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stranded wires lower gauges

lol......



Paul W. Abernathy
Reply With Quote
  #6  
Old 1/29/07, 4:23 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is online now
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: Stranded wires lower gauges

Black people???
Reply With Quote
  #7  
Old 1/29/07, 4:27 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded wires lower gauges

Quote:
Originally Posted by tdietrich1
I had an inspector warn me about the possible rush of black people being used as conduit...
Is there a name for the typing version of a Freudian slip?
Reply With Quote
  #8  
Old 1/29/07, 4:28 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stranded wires lower gauges

I think he meant Black Pipe.......lol...I hope so anyway...lol



Paul W. Abernathy
Reply With Quote
  #9  
Old 1/29/07, 4:30 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Stranded wires lower gauges

Darn!

Fixed, yelling at a 5 year old and typing can be counter productive!

Reply With Quote
  #10  
Old 1/29/07, 4:35 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded wires lower gauges

I question whether that is "illegal" black pipe. WAY back in the day that type of rigid conduit was extensively used as electrical conduit. I see it all the time.
I personally think it was a standard installation for the day.

I don't have my 1941 copy of the NEC so I can't say for sure whether conduit needed to be "listed".
IMO you can't simply say because black pipe is not legal today it was not legal "in the day".
There is certainly no danger.
Reply With Quote
  #11  
Old 1/29/07, 4:43 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded wires lower gauges

The only thing you have to be careful about in old homes is the old conduit WAS black. It is painted and not black oxide like black iron (typical gas) pipe. I ran into a lot of it in the Ringling Mansion restoration in Sarasota. The boxes were black too. This was before galvanizing became the norm for corrosion protection and explains some of that language in chapter 300.
Reply With Quote
  #12  
Old 1/29/07, 4:50 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stranded wires lower gauges

Quote:
Originally Posted by Speedy Petey
I question whether that is "illegal" black pipe. WAY back in the day that type of rigid conduit was extensively used as electrical conduit. I see it all the time.
I personally think it was a standard installation for the day.

I don't have my 1941 copy of the NEC so I can't say for sure whether conduit needed to be "listed".
IMO you can't simply say because black pipe is not legal today it was not legal "in the day".
There is certainly no danger.
I have a 1940 something NEC at home so I will look when I get home, I was basing it on the comment....stated ; Black Iron Gas Piping which irrespective of the date...would not be listed for electrical wiring but no date I believe was given for the time of installation...

See if you can get away with doing that with black gas pipe today speedy..lol...no actually the boxes on the ends look rather new"ish"...



Paul W. Abernathy
Reply With Quote
  #13  
Old 1/29/07, 4:57 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded wires lower gauges

I think Greg's explanation describes it best.
I just think the boxes and pipe are just still clean after all these years.
I'd put that installation in the 40's or 50's.
Reply With Quote
  #14  
Old 1/29/07, 5:00 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stranded wires lower gauges

I will look in the NEC I have dating back then when I get home this evening. Granted he has enough other issues that once the EC gets their he can look at it closer.



Paul W. Abernathy
Reply With Quote
  #15  
Old 1/29/07, 5:10 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stranded wires lower gauges

The only real difference between plumbing pipe and conduit is the conduit is supposed to be free of burrs that would damage the conductors. Personally I doubt the actual manufacture is all that much different. I bet they all are made the same and just get marked differently but I am not supposed to have an opinion when I am inspecting.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wires ran from lugs to auxilary panels Kevin Luce Electrical Inspections 7 9/20/07 9:24 AM
Loose/terminated wires in main panel csteele Electrical Inspections 13 7/19/07 4:39 PM
grounding wires tvanvranken Electrical Inspections 14 3/16/07 7:24 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM
Ground Wires Grouped Together psmothers Electrical Inspections 7 5/24/06 7:53 AM


All times are GMT -4. The time now is 8:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts