Default Strangest defect I've encountered

Inspected about an 80-year old house today. It had some electrical issues. The oddest one was that I could not get the hall light to come on initially, but later I noticed that it was on dimly. Towards the end of the inspection, I was checking the oven which had been on for a while. It was just barely warm. I turned the knob up and out of the corner of my eye, I noticed it get brighter in the hallway. After playing around with the oven knob for a couple of minutes, I realized the hall light came on dimly when I turned the oven knob on. I could turn the hall light on brightly by turning the knob to "Broil".

I'm not necessarily asking for an explanation of this. I just wanted to share this with ya'll.
Reply With Quote
  #2  
Old 11/8/06, 12:10 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Strangest defect I've encountered

Quote:
Originally Posted by mmorgan
Inspected about an 80-year old house today. It had some electrical issues. The oddest one was that I could not get the hall light to come on initially, but later I noticed that it was on dimly. Towards the end of the inspection, I was checking the oven which had been on for a while. It was just barely warm. I turned the knob up and out of the corner of my eye, I noticed it get brighter in the hallway. After playing around with the oven knob for a couple of minutes, I realized the hall light came on dimly when I turned the oven knob on. I could turn the hall light on brightly by turning the knob to "Broil".

I'm not necessarily asking for an explanation of this. I just wanted to share this with ya'll.
So to turn the Hall Light on, You need to set the Oven to Broil.

Is there a Problem with that?




Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #3  
Old 11/8/06, 1:41 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Strangest defect I've encountered

Quote:
Originally Posted by jhagarty
So to turn the Hall Light on, You need to set the Oven to Broil.

Is there a Problem with that?

No problem, you have to see what the Rock is cookin........




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #4  
Old 11/8/06, 5:43 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Strangest defect I've encountered

Sounds Like a neutral is loose in the panel .
Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 11/8/06, 7:53 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: Strangest defect I've encountered

that is a good one!




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #6  
Old 11/8/06, 8:13 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Strangest defect I've encountered

Very nice...
Reply With Quote
  #7  
Old 11/8/06, 11:54 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Strangest defect I've encountered

Quote:
Originally Posted by rcooke
Sounds Like a neutral is loose in the panel .
Thought the same when read about the hall light, but the oven made me think (since it was mentioned as having bearing on the problem) that something else is wrong. Since electric ovens typically use 240v, no neutral required(except for features: clocks, timers, lights, etc). Makes me also wonder if it's a 120 service, which makes me lean back towards a floating neutral.

IMHO: Definiately defer to an electrician.

tom
Reply With Quote
  #8  
Old 11/8/06, 1:39 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Strangest defect I've encountered

How would a floating neutral create this condition?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #9  
Old 11/8/06, 2:07 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Strangest defect I've encountered

Simple terms:

Voltage is the measure of potential between two points. This case what is called a 'hot' and a 'neutral'. For case of argument we can assume a good path for electricity back to the source will mean that a neutral is zero volts, since no 'back-pressure' is created. When you loose a neutral in the panel going back to the service, you loose that great path back to the pole, and now electricity must 'return' via another path, often the grounding rod or grounded water piping. Since there is much resistance, this creates a sort of back-pressure. So very little electricity(amps) can flow. So lights(120 volt) dim, and electric toasters[120v] don't heat up.

I tried to keep it simple for typing reasons, if something doesn't make sense, feel free to ask, but it comes down to this, if the return path is broken, then no flow of electricity. However if there is a grounding path(ground rods,etc), electricity will continue to flow very slowly, since the earth is a path back to the electric source.

You can verify this on different levels. As a HI, you can visually inspect the service conductors, see if the cables are in good condition, good crimps at the POA. Look inside the panel, do all wires look properly terminated, and uncorroded? As an electrician, there are other opptions, amp meter on the grounding electrode conductor, votages accross bars, etc.

Once again IMHO: Defer to an electrician.

tom
Reply With Quote
  #10  
Old 11/9/06, 7:45 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: Strangest defect I've encountered

Tony, Tony.....




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #11  
Old 11/9/06, 8:08 AM
mmorgan mmorgan is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Brownwood, TX
Posts: 196
Default Re: Strangest defect I've encountered

The service is 240 volts. When the oven did not get very hot, I thought it may only be getting 120 volts.
Reply With Quote
  #12  
Old 11/9/06, 9:08 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Strangest defect I've encountered

" I turned the knob up and out of the corner of my eye, I noticed it get brighter "

"When the oven did not get very hot, I thought it may only be getting 120 volts"

This is a textbook case of an open hot leg.

Last edited by brian winkle; 11/9/06 at 9:27 AM..
Reply With Quote
  #13  
Old 11/9/06, 10:42 AM
Michael Martin Michael Martin is offline
New User
 
Join Date: May 2005
Location: Cleveland, Ohio
Posts: 24
Please Note: Michael Martin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Strangest defect I've encountered

But a simple open hot leg doesn't explain the effect on a hall light.
Reply With Quote
  #14  
Old 11/9/06, 11:51 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Strangest defect I've encountered

What if the oven and hall light were on the same circuit, the light downstream from the oven and the light had the switch on the neutral conductor instead of the hot.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #15  
Old 11/9/06, 3:57 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Strangest defect I've encountered

Quote:
Originally Posted by Michael Martin
But a simple open hot leg doesn't explain the effect on a hall light.
Sure it does. If there was an open leg, none of the 120 loads on that bus would work. Then you turn on a 240 resistive load like an oven and the current passes thru the oven element and onto the dead bus. The voltage is limited by the resistance of the oven element, acting as a dimmer. I suspect there may have been more than the hall light not working. Mike may have had the oven warming up as he checked receptacles, which would have enough current to light up the little neon test lights. Also, the problem could be at a subpanel with only a few 120 loads.

Last edited by brian winkle; 11/9/06 at 4:01 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 6:56 PM
Can you find the defect.... dmacy Plumbing Inspections 7 3/21/07 5:57 PM
A box cover can fall off and become a defect jtedesco1 Electrical Inspections 5 4/3/06 12:42 PM
Homeowner special....defect or just informational? tneumann Plumbing Inspections 7 2/9/06 2:32 AM


All times are GMT -4. The time now is 2:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts