  #16  
Old 10/26/07, 10:33 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stray Voltage can kill

OK.....I read it and to be honest with you it was a NICE read. I am not an Eng. by trade.....but I would say I agree with his statements.

The issue of the voltage on the cow will effect her behaviour and could reduce milk production....after all I TICK off my wife and she does not put out so...it stands to reason....in fact she never puts out anymore so I guess I have a Magnetic Personality......

Anyway I felt the article was fine.....I have no other comments on it as the guy is more qualified than me to write it...now if he made improper statements about grounding and bonding then I would step in.....but he is right about usually the neutral being undersized, improperly terminated or in fact neutral lines in the ground with damage or worn insulation can effect the ground voltage levels......all facts.....

so.....I have no problems with it...except in the effects of the Equipotential Plane in a case of a dairy cow.....I happen to agree with the part they said evidence does show voltages can effect a cows behaviour....so logic would dictate it can effect their production.....so it appears it is enough evidence for me. Also the IEEE and NFPA must believe the Equipotential Plane is needed in the case of a dairy cow senario...look at the explantion of the Equip. requirements....we cant remove voltages on the earth due to the nature of the beast......BUT we can reduce its effects by establishing an equal potential......but alas being theory and all some dont agree with that statement as well.........but it works....wont remove it.....but does give some level of equalization to the surrounds.



Paul W. Abernathy

Last edited by pabernathy; 10/26/07 at 10:37 AM..
Reply With Quote
  #17  
Old 10/26/07, 10:46 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Stray Voltage can kill

You got to admit I sure do get some interesting threads started.
Gets many people thinking and thats what NACHI is about .
We do not have too always agree .
.... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #18  
Old 10/26/07, 10:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stray Voltage can kill

Animal research:
A great deal of research on the effects of stray voltage on farm animals has been
conducted over the past 40 years. The first study of stray voltage on dairy farms was published in New
Zealand in 1962. In this early study a series of experiments were carried out to establish the lowest level
of contact voltage at which there was a response. It was concluded that 3 volts (rms) would be a likely
minimum level for response.
A summary of the effects of the most common form of stray voltage (steady 60 Hz contact voltage) on
animals was published in 1991 by the USDA. The authors of this document reviewed the numerous
studies of dairy cow reaction to voltage and current exposure and concluded that the most sensitive cows
(less than 3 percent) begin to perceive contact voltage levels of about 1 volt causing 1 milliamp
(measured as rms) of 60 Hz electrical current to flow through the cow. As the voltage and current is
increased, a larger percentage of cows will perceive the current and behavioral responses will become
more pronounced. Numerous studies have documented avoidance behaviors in the range of 3 to 6
milliamps of current flowing through the cow. This response assumes that the cow comes into contact
with objects that have different voltages and that this voltage causes sufficient current to flow through the
cow. The authors recommended that cow contact voltage be kept below 2 - 4 volts (rms) to prevent
adverse responses.

Ok....sad fact is in tests voltage on the earth due to improper neturals and well the nature of a multi-grounded system is around 3 V.......now it is better to negate the effects than to discount them.....this is the preceived nature of the creation of the Equipo. Plane........atleast thats the NFPA's stance on it.




Paul W. Abernathy
Reply With Quote
  #19  
Old 10/26/07, 10:48 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stray Voltage can kill

Roy....it is not about right or wrong in many cases...it's all about the QUEST my friend.



Paul W. Abernathy
Reply With Quote
  #20  
Old 10/26/07, 10:51 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stray Voltage can kill

BTW.....Mike Holt has some GREAT stuff on Stray Voltage and his thoughts on it as well.....welcome to THEORY.....we are still learning many things in this thing we call Paul-tricity...I mean...Electricity...sorry

Just go to his site and click on NEWSLETTERS and find the ones about Stray Voltage....

Ironically I read this info on a site that of all things sells SOLUTIONS...but I would say they made a statement in the article like this..."Electricity takes the path of least resistance. The low resistance offered by a farm’s equipotential grounding grids represents a serious threat to cows in that it provides a low resistance path to where cows are being milked. "

The first statement alone makes me question them.....Electricity does NOT take the path of least resistance...it takes all paths available...proportional to the about of resistance...

Heck if that was the case......having a metal light pole with no EGC running to it and just driving a ground rod next to it would make it safe......NOT....if someone touches it at a body resistance of 1000 OHMS.....and the ground rod has a perfect 25 OHMS.....it is the lease resistance...so if the man touched it are we saying he would not possibly DIE?.....heck no because while some will travel on the earth because it is a conductor....granted a poor one.....the OCPD will never TRIP because simple OHMS LAW says........120 divided by 25 OHMS is what....4.8 Amps....will that trip an OCPD...NOT HARDLY....so when a company makes that kind of statement...I start to question ALL their research.....

But alas here is their article...http://www.strayvoltage.ca/Paper.htm

Ironcially I do agree with a few of their solutions.....dealing with the neutral and isolation.



Paul W. Abernathy

Last edited by pabernathy; 10/26/07 at 11:01 AM..
Reply With Quote
  #21  
Old 10/26/07, 11:06 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Stray Voltage can kill

Exactly just take a garden hose and turn on the water and see all the different paths the water takes down a paved drive way .

. Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #22  
Old 10/26/07, 11:07 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stray Voltage can kill

Figured this was a GOOD time to understand what STRAY VOLTAGE really is.....it is......it wont KILL you.....thats different than Stray Voltage in itself but depending on the conditions......well I will let you read it.


STRAY VOLTAGE: KNOW YOUR TERMS




CONFUSION ABOUT THE TERM STRAY VOLTAGE IS A SERIOUS CONCERN. Historically, the term was associated with an elevated voltage that is difficult to mitigate but is not a threat to human life. These days, however, usage of the term is associated with much higher, dangerous voltages that can easily be corrected when discovered.
The issues associated with distribution system grounding, in particular stray voltage, have caused much confusion recently. Using the historic definition of the term, stray voltage has been a relatively dormant issue; it was associated with low-voltage magnitudes not considered dangerous. But recent events have caused confusion about the usage of this term, and the result is that some are now associating stray voltages with lethal voltages, those that could cause death.
GROUNDING MATTERS
There are many ways to ground the primary distribution system: the four-wire multi-grounded, the five-wire system, the four-wire uni-grounded, the three-wire uni-grounded, and the ungrounded wye and delta systems. There is no best system; they all have pros and cons.
The four-wire multi-grounded system used in the United States is a good choice. But, like most choices, one must be cognizant of the characteristics of this grounding system, one of which is that unbalanced currents flowing through the neutral and earth can cause stray voltages.
WHERE TERMS ORIGINATE

The IEEE Guide for the Application of Neutral Grounding in Electrical Utility Systems, Part IV — Distribution (IEEE C62.92.4-1991), is primarily concerned with the classification of distribution system grounding as it relates to temporary overvoltages and the selection criteria for surge arresters. In the appendix, this guide covers techniques for the interconnection of primary and secondary neutrals, which mitigate stray voltages. It is important to note that the term stray voltage is never specifically addressed. Historically, stray voltage was a concern on farms, where milking machines in the presence of stray voltages caused microshocks that resulted in decreased milk production and other behavioral abnormalities in cows.

Special isolating devices have been available for quite some time to isolate transformer primary and secondary neutrals to prevent stray voltages to the customer neutral from the utility system. While the IEEE guide recognizes the issue of stray voltage, it does not address such issues as how much of it should be allowed and how to mitigate it.
GROUND IMPACT
The statement that “good grounding solves all power-quality problems including stray voltage” belongs with the statement “lightning never strikes twice in the same place.” Tell that to workers at the Empire State Building. Without several relevant qualifiers, both of these statements are nonsense. In the case of grounding, sometimes good grounds are beneficial, sometimes they are a problem source and sometimes they make little difference — it all depends. Following is the impact of grounds on:
  • Fault currents. Good grounding has little effect on the magnitudes of fault currents.
  • EMF. Bad grounding reduces EMF.
  • Line protection (using arresters). Good grounds are not required.
  • Shield wire protection. Good grounding is required.
  • Lightning arresters. Although it depends on the application, good grounds are generally not required.
  • Temporary overvoltages. For a four-wire multi-grounded system, the impact of ground rod resistance is relatively minimal.
  • Stray voltage. Good grounds can improve stray voltage but also can make it worse. Also, better grounding to resolve stray voltage issues may not be an effective solution.
CORRECT TERMINOLOGY
The term stray voltage is becoming all things to all people. The following are terms often interchanged with the term stray voltage, some of which are incorrect and causing a lot of the present confusion:
  • Stray voltage
As generally defined by utility engineers, stray voltage refers to the persistent voltage imposed on the distribution primary neutral. Stray voltages are mostly due to return currents from unbalanced loads. This is a normal condition of a four-wire, multi-grounded system. In the context of the last 40 years, this voltage is associated with problems in dairy farms and, generally, the voltages do not exceed about 8 V. Stray voltages are not lethal.
  • TOV
Transient overvoltages (TOVs) are sometimes referred to as stray voltage, but they are not. TOVs are 60-Hz line-to-neutral overvoltages that occur on the unfaulted phases of a four-wire multi-grounded system during a fault (Fig. 1). As the nomenclature implies, TOVs are transient or temporary in nature. They are not persistent. A single line-to-ground fault creates a shift in the neutral voltage of approximately 35%. While this voltage is relatively high, it only lasts as long as it takes the protective equipment to clear the fault (normally in tens of cycles, usually less than a second). This is not stray voltage.
  • Contact voltage
This term is normally used to address the condition in which the “hot” lead (120 V or more) contacts the casing of a device, such as a streetlight. This situation can be dangerous and possibly result in death. Contact voltage is not stray voltage, although it is sometimes misused in this context.
HARD TO IDENTIFY
Stray voltage is caused by voltage drop and ground currents that could have their origin either on the utility system or the customer premises itself. The problem can be very difficult to analyze since the return path of the unbalanced currents is especially complex. In many circumstances, system changes to mitigate the problem can cause the opposite effect. Throughout the years, the greatest interest in stray voltage has been in the area of dairy farming, because cows are sensitive to microshocks caused by stray voltage, which can affect milk production.
The path of unbalanced current flow on a distribution system is not obvious. One thing that greatly complicates an accurate model is that the loads are distributed, making the flow of current between the neutral and earth very complex.
Figures 2 and 3 illustrate the typical effect of unbalanced current flow on stray voltage. Figure 2 shows that the stray voltage level at substation is high, as it also is at the end of the feeder. There are two interesting points to make. First, the stray voltages near the substation are of opposite polarity to those at the end of the line (current reversal), and the voltages in the middle of the feeder are relatively low. Also, it is interesting to note that if the substation ground is good (1 V), the situation gets worse in some areas and better in others.
Figure 3 shows the effect of changing the system pole ground rod resistances from 5 Ω to 50 Ω. As can be seen, stray voltages are reduced, but not as much as one might think. In the areas with the highest stray voltage, the benefit of improving grounding is questionable.
RECENT EVENTS

Many in the electric utility industry are concerned that state regulatory bodies (public service commissions or public utility commissioners), which are not necessarily technical in nature, will define issues and set arbitrary standards.

For example, one state commission has taken the instance of a tragedy to misuse the term stray voltage. Furthermore, this commission has suggested testing standards that have not been reviewed by objective technical experts as being either necessary or effective. The tragedy, as we understand it, resulted from what could only be a contact voltage, and not at all a stray voltage. Our concern is that a regulation issued by one governing agency that misuses these terms will eventually affect other jurisdictions. Some states have set low limits on stray voltage that utilities in other states don't believe are possible to meet.
DETERIORATED CABLE NEUTRALS

Synergetic Design (Raleigh, North Carolina, U.S.), which operates in 18 states providing technical services to large investor-owned municipals and electric membership cooperatives, recently performed a survey related to the impact of exposed deteriorated neutrals on stray voltage levels found in primary cable. The results show that many utilities have switched to jacketed cable to avoid this condition in the future.

About 20% of the respondents were concerned with deteriorated neutrals causing shocks on such things as swimming pools, fences and water faucets. One utility indicated it drew arcs during the repair of a corroded neutral, even after the load was transferred. About 25% of the respondents indicated they had experienced shocks directly related to deteriorated neutrals. Figure 4 shows responses to the survey question about the level of stray voltages recorded in areas with deteriorated neutrals.
FEEDER INTERACTION
In many cases, the problem of locating a source of the stray voltage is extremely complicated due to additional feeders in the same area. A portion of the neutral current returns to the substation via the ground rods and the earth. These currents also may return on additional feeder neutrals, should such a return path have lower or comparable impedance.
Reducing the impedance of the ground rods has additional effects. The impedances of the ground rods at specific areas on a feeder are critical to the magnitude of the stray voltage. Lowering the ground rod impedance initially appears to be a solution for reducing the neutral-to-earth potential at a specific location. However, this also provides a lower impedance return path for any return current in the area. This presents the possibility of increasing the neutral current at the location of the reduced impedance ground rod. This reduction in the ground rod impedance in one problem area can increase the stray voltage in other areas on the feeder.
INDUSTRY INVOLVEMENT

The subject of stray voltage, once only mentioned in relation to dairy farms, has become an issue in the electric utility industry for other reasons, not the least of which is safety. The impact of confusing the term stray voltage with higher abnormal and potentially dangerous contact voltages will likely cause considerable cost with virtually no benefit.

Additionally, the distraction of this confusion and unnecessary testing will likely siphon funds away from other projects that have more safety value for the customer. The general reduction of industry participation in the standards-writing function of IEEE has created a situation in which state commissions and lawyers — without the participation of industry experts and standards groups — may end up dictating stray voltage standards that are entirely incorrect. They could also mandate safe levels of stray voltage that would virtually be impossible to attain. More attention to this area is needed by our industry.



Paul W. Abernathy
Reply With Quote
  #23  
Old 10/26/07, 11:13 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stray Voltage can kill

SO.....lets make it clear...." Stray Voltage CAN'T kill " by its very nature....but CONTACT voltage mistaken as STRAY voltage can kill.

In the original article I am very LEARY of the statement of 1,000V on the earth as stray voltage........I would have to EXAMINE the farmers system and look to the possible issue of a transformer or something placing return path CONTACT voltage on the earth.....but it is not " Stray Voltage " by definition.

OPPS.....for to mention this ..." Thats my opinion.....like it or not......I am an opinionated P*ick 90% of the time "



Paul W. Abernathy
Reply With Quote
  #24  
Old 10/26/07, 11:34 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Stray Voltage can kill

Quote:
Originally Posted by pabernathy
I am an opinionated P*ick 90% of the time "
You too?

The original article is poor IMHO. People are always lookng for someone else to blame. And there will always be those to take some of there money and agree with them.
Reply With Quote
  #25  
Old 10/26/07, 11:40 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Stray Voltage can kill

Here is how I pick to-death an article....no matter who it is from. I look for statements that are proven wrong before I discount the entire article because even in a BAD article their are good content to learn from.

Usually it means the article was copied...lol...but alas something to learn from it. Kinda like the trouble I got Mike Holt in with the article by IDEAL on the SureTest Products....the ENG made some statements that were wrong and I sent them to Mike...well he ended up adding to it and SPLASHING it all over the place.....I and Mike were correct but the after effects left a BAD taste in some peoples mouth as bad mouthing IDEAL...when in fact we simply wanted to clear up bad information....

So in the end.....take what you read with a grain of salt...analysis it....digest it...look for Non-Facts then read it again.....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
NStar's hunt for stray volts pabernathy Electrical Inspections 0 4/18/07 5:54 PM
Stray Voltage jallingham Electrical Inspections 2 12/7/06 10:17 PM
Stray Voltage? jspringstead Electrical Inspections 4 3/9/06 11:55 AM


All times are GMT -4. The time now is 8:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts