Default Stumped on discoloration

Today's inspection circa 2001. 200 amp Siemens 42 circuit panel with 35 of the available circuits being utilized. All 8 of the 2-pole 240v breakers were stacked left and the 19 single pole 120v breakers on the right side. Unable to determine connection to earthen ground connection as the grounding electrode was not exposed (covered over with poured concrete side walk servicing garage man door.
This is a back to back service (first point of disconnect) located in the garage with neutrals and grounds sharing the same bars. Upon removing the dead front cover observed that all of the bare ground wires were blackened, but the neutrals and load carrying branch circuit wiring had not been affected. Opened GFCI outlets within the garage and no discoloration was observed at these devices.
While realizing that load balancing is not really that big of a deal on a residential service it is not common to see all of the single pole and 2-pole breakers stacked?
Can not verify earthen ground? Home is located on brackish waterway, irrigation water provided by public utility. No other blackening of copper wire observed at various other devices within the home and no discoloration of other wiring within the panel kinda rules out a type of environmental contaminate? I am stumped
Attached Thumbnails
stumped-discoloration-william-thomas-074.jpg   stumped-discoloration-william-thomas-075.jpg  



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/21/14, 6:10 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,465
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stumped on discoloration

It is typical to see that where the cable has gotten wet.
Reply With Quote
  #3  
Old 1/21/14, 6:28 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 459
Default Re: Stumped on discoloration

Quote:
Originally Posted by Jim Port View Post
It is typical to see that where the cable has gotten wet.
Are you thinking that perhaps the home was not dried in before electric rough; that because the current carrying conductors would not have been stripped for landing at this point and therefore would not have be affected by exposure to moisture



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #4  
Old 1/21/14, 6:33 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: By my swimming pool
Posts: 3,871
Default Re: Stumped on discoloration

Isnt it humid if FL. Not being a smart azz but just sayin. Some darkening of bare copper wiring is common IMO in areas that are suject to outdoor envirometal conditions. A open garage would be no different.






Fogarty Inspection Services Group of Palm Bay FL
Florida Licensed Home Inspector #8351
Certified Master Inspector

Home inspections, Commercial Inspections, Thermal Imaging, Wind Mitigation and Insurance Inspections for Palm Bay, Melbourne, Cocoa, Titusville, Vero Beach and all the surrounding areas.

321-506-5125
fogartyinspectionservices@gmail.com

www.homeinspectorpalmbay.com
Reply With Quote
  #5  
Old 1/21/14, 6:52 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 20,345
Default Re: Stumped on discoloration

also looks like white wire used on a 240 volt circuit should be painted or taped, black



If you do not search for more ,
......You will never find it.

............. Roycooke@hotmail.com
...................613-827-2011
Reply With Quote
  #6  
Old 1/21/14, 7:03 PM
Bradley K. Toye Bradley K. Toye is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 2,049
Default Re: Stumped on discoloration

Underground service?



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
727-403-5029
Lecsi2@gmail.com
www.LeadingEdgeInspectionServices.com
Reply With Quote
  #7  
Old 1/21/14, 7:37 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 459
Default Re: Stumped on discoloration

Quote:
Originally Posted by btoye View Post
Underground service?
Yes underground service



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #8  
Old 1/21/14, 7:44 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 459
Default Re: Stumped on discoloration

Quote:
Originally Posted by rcooke View Post
also looks like white wire used on a 240 volt circuit should be painted or taped, black
Roy,

Your correct, but until March 1st 2002 Building Officials had description as to when they adopted new code articles.As this prorpetty was permitted before FBC 2002 am unable to confirm



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #9  
Old 1/21/14, 10:18 PM
Bradley K. Toye Bradley K. Toye is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 2,049
Default Re: Stumped on discoloration

Quote:
Originally Posted by mtyson View Post
Yes underground service
Try post #8 in this thread and see if it makes sense to you, makes sense to me.

http://www.nachi.org/forum/f73/wire-corrosion-87637/



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
727-403-5029
Lecsi2@gmail.com
www.LeadingEdgeInspectionServices.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gray irregular discoloration pattern Unregistered AskNACHI.org Inspection Questions Forum 5 5/29/12 8:52 PM
Discoloration in evaporator lfoster Inspecting HVAC Systems 3 7/13/08 10:57 PM
Wooden shingle siding discoloration wdecker Exterior Inspections 4 3/26/07 11:07 AM
Ceiling discoloration from joists? dtaylor General Inspection Discussion 4 8/3/06 12:27 AM
Discoloration was caused by a lightning strike! jtedesco1 Electrical Inspections 0 1/29/06 5:51 PM

All times are GMT -4. The time now is 12:46 PM.
no new posts