Stupid Question

One pump serves the sprinkler system and the other serves the well to the house. Both are enclosed in the same pump house.
Question: Is there any condition that would require these pumps to not be bonded?

i40.jpg

i41.jpg

The pumps should be grounded by the EGC with the circuit conductors. What do you think they need to be bonded to?

Got it. Thank you.

If they were connected to the same EGC, would in theory they also be bonded? I would think so.