Default Stupid service amperage question

60 amp service, right (not 120)?

stupid-service-amperage-question-012109-051-800x600-.jpg stupid-service-amperage-question-012109-052-800x600-.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #2  
Old 1/22/09, 12:36 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid service amperage question

Yes, 60.
Reply With Quote
  #3  
Old 1/22/09, 12:49 PM
bemelander bemelander is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Grand Rapids, MI
Posts: 341
Default Re: Stupid service amperage question

I second that yes, 60 amp



Bill Emelander
Professional Edge Home Inspection
Grand Rapids and all of West Michigan
NACHI #03111914
www.proedgehi.com
Reply With Quote
  #4  
Old 1/22/09, 1:01 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,642
Default Re: Stupid service amperage question

yes 60
Reply With Quote
  #5  
Old 1/22/09, 1:02 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Stupid service amperage question

Never add the sum of two cartridge fuses. Two 60's is 60 Amps.

Both fuse cartridges will be the same size and the total amperage is the size printed on the fuse.
Reply With Quote
  #6  
Old 1/22/09, 1:05 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Stupid service amperage question

Thanks guys.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 1/26/09, 3:53 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid service amperage question

I would mention the corrosion as well, and would we call for an electrician?
Another thing, a label on that fuse pull would make the job easier and safer, and you wouldn't have to cut power to get the fuse size.

John Kogel
www.allsafehome.ca
Reply With Quote
  #8  
Old 1/26/09, 4:35 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid service amperage question

Quote:
Originally Posted by jkogel View Post
I would mention the corrosion as well, and would we call for an electrician?
Another thing, a label on that fuse pull would make the job easier and safer, and you wouldn't have to cut power to get the fuse size.

John Kogel
www.allsafehome.ca
If we trusted labels we could just never unscrew the panel cover.
Reply With Quote
  #9  
Old 1/26/09, 6:54 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid service amperage question

Quote:
Originally Posted by relliott View Post
If we trusted labels we could just never unscrew the panel cover.
Bob, we have the panel cover off. "Appears to be 60 amp as labeled, recommend evaluation of older, corroded panel by a qualified electrician."

John Kogel
www.allsafehome.ca
Reply With Quote
  #10  
Old 1/26/09, 6:59 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid service amperage question

Quote:
Originally Posted by jkogel View Post
Bob, we have the panel cover off. "Appears to be 60 amp as labeled, recommend evaluation of older, corroded panel by a qualified electrician."

John Kogel
www.allsafehome.ca
Duh ,I see it is off but I was refering to them having a label.
I would not trust the info to be accurate.

60 amps is awfully low though.

Hope they do not use a lot of hair dryers.
Reply With Quote
  #11  
Old 1/26/09, 7:25 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid service amperage question

Quote:
Originally Posted by relliott View Post
Duh ,I see it is off but I was refering to them having a label.
I would not trust the info to be accurate.
We would use the label info PLUS the wire size, right? Just pulling your chain a bit.

But seriously, since it's an old undersized corroded installation, I'd prefer to call it as above and not even attempt to remove the fuses. Could break something.

Quote:
Originally Posted by relliott View Post
60 amps is awfully low though.

Hope they do not use a lot of hair dryers.
How many plug-in heaters would they have running day and night?
Reply With Quote
  #12  
Old 1/28/09, 9:17 PM
jbettencourt jbettencourt is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Stoney Creek, ON
Posts: 520
Please Note: jbettencourt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid service amperage question

The only stupid question is the one that is never asked.
Reply With Quote
  #13  
Old 1/28/09, 9:29 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: Stupid service amperage question

No one mentioned the missing dead cover or the extremely tight bends in the feeder cables. I would go ahead and recommend an upgrade; 60 amps is insufficient today plus the panel is a piece of antiquated crap, but that is me. The missing dead cover though could end up a tragedy if a curious child playing on the side of the house looks inside and gets electrocuted and the home inspector did not point it out in their report.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #14  
Old 1/29/09, 9:42 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Stupid service amperage question

The dead front cover wasn't missing. I removed it during the inspection. Here's what I say about low amperage services:

"The service entrance amperage is estimated to be 100 amps or less. Generally speaking, 100 amps is the minimum amperage necessary for today's modern homes. You should confirm the amperage prior to close of escrow and consult with a licensed electrician about the limitations of this size service."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 1/29/09, 12:07 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,760
Default Re: Stupid service amperage question

Good response to the 60 amp setup. I find many homes missing dead covers and a lot of Realtors and even sellers fail to understand the big deal until I point out to them the potential dangers. You would think they could see it but their eyes are often on the money not on the big picture. I thought you might have removed the dead cover due to the line of crap piled up at the bottom of the box but thought it was worth mentioning, more so for new guys who may have never thought of it being important. Small, seemingly innocuous items like this get missed but are important to the buyers whether they know it or not.



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 293 2/10/08 2:20 AM
Service disconnect question wsiegel Electrical Inspections 3 8/28/07 10:59 AM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical Inspections 13 2/8/07 2:18 PM
Service Entrance Amperage? jfunderburk Electrical Inspections 18 6/16/06 11:16 PM
Main service disonnect question jmichalski Electrical Inspections 5 1/29/06 5:32 PM


All times are GMT -4. The time now is 6:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts