Default Sub or load side panels

Do they, or when do they need a main breaker?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #2  
Old 9/13/06, 10:48 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Sub or load side panels

What do you mean by "main" breaker?

They need a point to disconnect power from their feeders (as with all equipment). Typically, this will be found at the service equipment or a distribution panel.

If your question is (which is what I'm assuming), "when do they require a breaker within the panel, that shuts down power to the other breakers within the panel?" The answer is, "they don't."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 9/13/06, 11:42 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Sub or load side panels

I can think of one case where it would be needed.........

Service panel already has a 100 amp branch breaker present.
Someone uses that to feed a load side panel via correct size conductors.
They use a load side panel that is rated for 60 amps.
The load side (sub) panel would then need a 60 amp "main" breaker in it.
Reply With Quote
  #4  
Old 9/13/06, 1:24 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub or load side panels

In a second building a local disconnect is required
Reply With Quote
  #5  
Old 9/14/06, 9:42 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: Sub or load side panels

Is that right guys ? Thats what I wondering...




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #6  
Old 9/14/06, 10:06 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Sub or load side panels

Local AHJ's may or may not enforce some things, that is one reason why HI's are not required to inspect for code.

Just note that no disconnect is present as information only.
Reply With Quote
  #7  
Old 9/14/06, 10:45 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Sub or load side panels

Greg is correct. A disconnect is required, but it doesn't necessarily have to be within the remote panel. Here are the references.


225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.

225.32 Location. The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors.




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 9/14/06, 7:30 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub or load side panels

Also, don't forget that there can be up to 6 disconnects. So if there are 6 or less breakers, that is your disconnecting means.
Reply With Quote
  #9  
Old 9/28/06, 9:00 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: Sub or load side panels

So, they do not have to always have a main breaker?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Load Side Panel Steven Brewster Electrical Inspections 18 5/7/06 7:40 AM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 6:31 PM
Sub or load side panels mtimpani Electrical Inspections 9 1/25/06 9:23 AM