What do you mean by "main" breaker?
They need a point to disconnect power from their feeders (as with all equipment). Typically, this will be found at the service equipment or a distribution panel. If your question is (which is what I'm assuming), "when do they require a breaker within the panel, that shuts down power to the other breakers within the panel?" The answer is, "they don't." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
I can think of one case where it would be needed.........
Service panel already has a 100 amp branch breaker present. Someone uses that to feed a load side panel via correct size conductors. They use a load side panel that is rated for 60 amps. The load side (sub) panel would then need a 60 amp "main" breaker in it. |
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
In a second building a local disconnect is required
|
|
#5
|
||||
|
||||
|
Is that right guys ? Thats what I wondering...
"Be Proud of Your Home, Go With Pride!" 'Not just a Home Inspection, but an Education' Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties. |
|
#6
|
||||
|
||||
|
Local AHJ's may or may not enforce some things, that is one reason why HI's are not required to inspect for code.
Just note that no disconnect is present as information only. |
|
#7
|
||||
|
||||
|
Greg is correct. A disconnect is required, but it doesn't necessarily have to be within the remote panel. Here are the references.
225.31 Disconnecting Means. Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure. 225.32 Location. The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Also, don't forget that there can be up to 6 disconnects. So if there are 6 or less breakers, that is your disconnecting means.
|
|
#9
|
||||
|
||||
|
So, they do not have to always have a main breaker?
"Be Proud of Your Home, Go With Pride!" 'Not just a Home Inspection, but an Education' Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Where do I put the Aquarium? | mcyr | Structural Inspections | 3 | 11/6/07 3:05 PM |
| Load Side Panel | Steven Brewster | Electrical Inspections | 18 | 5/7/06 7:40 AM |
| FPE Panel - Do you open them up? | menser | Electrical Inspections | 11 | 2/7/06 6:31 PM |
| Sub or load side panels | mtimpani | Electrical Inspections | 9 | 1/25/06 9:23 AM |