Default sub panel

I'm new to This trade (HVAC/R TECH). I need to clarify an arguement I had today with a friend (non electrician). Do Sub panel boxes need to to be bonded to the service box via metal conduit? I said yes. I looked it up in the NEC (1999 BOOK)
QUOTE FROM THE BOOK "To remove dangerous voltage,we must clear the ground-fault by quickly opening the circuit overcurrent protection device.
To open the circuitovercurrent protectiondevice,the saftey grounding path must have sufficient low impedance.

This is accomplished by bonding metal parts to each other then bonding metal parts to the grounded (neutral)conductor at one location in accordance with sec 250-142"

Then he asked about plastic conduit that electricians are using. Well now I'm LOST AGAIN.

Plus I have an elecrtical book for wiring houses from Menards and they do not talk about bonding sub panels (Black &Decker complete guide to home wiring). So am I right about bonding sub panels with metal conduit, and what about plastic conduit?

I appreiciate all your help
Reply With Quote
  #2  
Old 1/27/07, 2:07 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,947
Default Re: sub panel

Quote:
Originally Posted by Sonny C. Shipler
I'm new to This trade (HVAC/R TECH). I need to clarify an arguement I had today with a friend (non electrician). Do Sub panel boxes need to to be bonded to the service box via metal conduit? I said yes. I looked it up in the NEC (1999 BOOK)
QUOTE FROM THE BOOK "To remove dangerous voltage,we must clear the ground-fault by quickly opening the circuit overcurrent protection device.
To open the circuitovercurrent protectiondevice,the saftey grounding path must have sufficient low impedance.

This is accomplished by bonding metal parts to each other then bonding metal parts to the grounded (neutral)conductor at one location in accordance with sec 250-142"

Then he asked about plastic conduit that electricians are using. Well now I'm LOST AGAIN.

Plus I have an elecrtical book for wiring houses from Menards and they do not talk about bonding sub panels (Black &Decker complete guide to home wiring). So am I right about bonding sub panels with metal conduit, and what about plastic conduit?

I appreiciate all your help
They need to be bonded but it can be with ground wire in Plastic pipe or
the Ground in a multi conductor cable or via the metal pipe.

Please do not hesitate to ask any questions others also learn from your questions .
Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #3  
Old 1/27/07, 2:28 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: sub panel

ROY is 100% correct......

When using EMT which I will take as such in your example, you are allowed to use the conduit itself as the Equipment Grounding Conductor ( which I happen to wish they would rename it as Equipment Bonding Conductor...but alas I don't sit on the CODE panel....YET anyway....

SO bacically you have to ensure the BONDING remains in place when using that conduit to ensure a low impedence path for a fault...when using non- metalic rigid conduit ( PVC-40 or 80 ) you will have to ensure a EGC is run ( EGC -ie: Equipment Grounding(BONDING) Conductor from the panel through that conduit to the device....

If using Romex or ( Non-Metalic Sheath Cable ) the EGC will be within the cable itself ( thus in older applications with NO EGC thus ungrounded ) and that is your bonding conductor.

I think THIS is where people get confused with the NEC.......the NEC itself does not seem to know when something is a BONDING conductor and when it is a GROUNDING conductor......yet they TRY to define it and they do it WRONG...yep I said it...the NEC Code Panel is doing it WRONG in my opinion but again who am I.....country boy in VA...

Anyway I hope this assisted you Sonny....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 1/27/07 at 5:31 PM..
Reply With Quote
  #4  
Old 1/27/07, 3:50 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: sub panel

Quote:
Ray is 100% correct......
you can call me Ray or you can call me Jay...

Reply With Quote
  #5  
Old 1/27/07, 5:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: sub panel

DANG......ROY I mean...lol.....man I can't get ANY slack...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 1/27/07, 5:35 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,947
Default Re: sub panel

Quote:
Originally Posted by pabernathy
DANG......ROY I mean...lol.....man I can't get ANY slack...lol
The humor is I read it and did not see the error . Cute EH!
Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 2:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts