Default Sub Panel

Had a unique inspection today at a condo complex that used to be a motel. There was a meter bank at the rear of the building with individual main disconnects. The panel inside the unit (inside a bedroom closet) only had 3 incoming wires. 2 hots and a neutral. Now shouldn't this first of all be a sub panel installation? The neutrals and grounds were on same bus bar, bonded to the panel. I don't want to call this out as defective if it isn't. No service grounding wire was observed either entering or leaving the panel. I was able to see down the wall, below the panel opening and several pigtails were seen, with wire nuts, inside the drywall, with no bushings for the panel knockouts. The unit is a 60 amp service and the crappy little electric range had a 60 amp breaker. Ungrounded outlets and so on. A real mess. I'm fairly confident about calling out these issues, but the panel should be a sub, right?

Thanks
Reply With Quote
  #2  
Old 3/25/07, 11:59 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

You say 3 wires coming in, but were they in some sort of metallic conduit, by chance?
Reply With Quote
  #3  
Old 3/26/07, 12:07 AM
jharashinski's Avatar
jharashinski jharashinski is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Barnegat, NJ
Posts: 62
Default Re: Sub Panel

Nope. Not at least as I could see. Pretty sure it was the normal cable sheathing.
Reply With Quote
  #4  
Old 3/26/07, 12:42 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Sub Panel

Quote:
but the panel should be a sub, right?
It's either "service" equipment, or it's "other" equipment.

You are correct. An EGC is required (whether conduit or conductor), and the grounds should be bonded to the enclosure while the neutrals are isolated. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 3/26/07, 1:00 AM
jharashinski's Avatar
jharashinski jharashinski is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Barnegat, NJ
Posts: 62
Default Re: Sub Panel

Thanks Jeff you're the best!! I thought that it should be wired as a sub. I felt a bit guilty taking this inspection since there wasn't a whole lot to inspect and the husband is a HVAC contractor. I thought I wouldn't found anything he couldn't. Only goes to show.

Not sure what you meant when you said

Quote:
Originally Posted by jpope
It's either "service" equipment, or it's "other" equipment.
I have sooo much to write up on this one. Thanks again Jeff.
Reply With Quote
  #6  
Old 3/26/07, 1:58 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Sub Panel

What I said was in reference to this. . .

Quote:
Originally Posted by jharashinski
I thought that it should be wired as a sub.
The only place where the neutral can be (and must be) grounded (bonded to the enclosure and/or grounds) is at the "service" equipment (service equipment is often referred to as the "main" panel). The service equipment is where the service disconnect is located (often referred to as the "main" breaker).

All panels past the service equipment are considered "other" equipment, or load side equipment (often referred to as "sub" panels). At "sub" panels (other equipment), there must be an equipment grounding conductor (EGC) bonded to the enclosure, and the neutrals must be isolated from the enclosure (floating).

Too many inspectors are confused by the term "sub" panel. So it's easier just to lose the term "sub," and call it what it is - an electrical panel. Then ask youself the question - Is it the "service" panel, or is it an "other" panel?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 3/26/07, 2:38 AM
alarsen1's Avatar
alarsen1 alarsen1 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 232
Default Re: Sub Panel

Great explanation, Jeff... thanks.
Reply With Quote
  #8  
Old 3/26/07, 9:26 AM
jharashinski's Avatar
jharashinski jharashinski is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Barnegat, NJ
Posts: 62
Default Re: Sub Panel

Thanks again Jeff.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 2:31 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts