  #1  
Old 1/14/09, 3:33 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 766
Send a message via AIM to jfrederick
Default Sub-panel

House built in 1968. Main panel is a 200 amp split bus. 100 amp breaker feeds sub panel in hallway closet. Grounds & neutrals were together. No bonding screw to panel. Question - Is this O.K. because it's a 3-wire system? See more info/pics at the Move In Certified/Seller Inspection forum, here.
Reply With Quote
  #2  
Old 1/14/09, 4:55 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Sub-panel

A SUB-PANEL, or REMOTE DISTRIBUTION PANEL, is merely an extension of the main service panel. Since the neutrals are bonded to the grounding wires in the MAIN SERVICE PANEL, the grounding wires (bare) and the neutral wires (white) should never be connected in any manner beyond the main panel. However, the grounding wires should be bonded to the sub-panel.

And “objectionable current” may flow on metal parts (grounding wire or metal conduit) when the grounded neutral conductor (white wire) is bonded to the metal case of a panel-board that is not part of service equipment (such as a sub-panel). Occasionally, the wires may come in contact with each other in their jacket causing a short circuit in the grounding/grounded system.

[If a neutral wire became disconnected (and, it does happen), the return path for electric current could be along a ground wire. While that itself may not always be a hazard, if that ground wire also became disconnected somewhere, parts of the ground system could be energized. That is NEVER supposed to happen.]

The neutral wire is essentially a "low-risk" return path for the electric current in that branch of the system. All of the neutral wires have the same electrical potential...zero. At least, no potential compared to ground. There is, of course, 120 volts of potential difference between a neutral wire and any hot wire in the average residential system.

If one were to touch the metal part of a live neutral wire one should not receive a shock. (Don't try it!) By tying the neutral to ground at one point (in the main panel), half of the conductors (in a typical 120 volt circuit) have no dangerous electrical potential. Of course, as always, the hot wires are still dangerous.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #3  
Old 1/14/09, 4:56 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Sub-panel

I got that from Paul, I think...



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #4  
Old 1/14/09, 5:02 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Sub-panel

Jae went the long way to say "NO," it's not right.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/14/09, 5:04 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Sub-panel

Quote:
Originally Posted by jpope View Post
Jae went the long way to say "NO," it's not right.
But I like to explain things, even if I don't understand it.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #6  
Old 1/14/09, 5:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Sub-panel

A simplified version is "you cannot ground a neutral at any point past the service equipment." [exceptions apply, but we won't go there]



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 10:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 12:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts