Default Sub Panel

What is wrong in this SUB PANEL???
Attached Thumbnails
sub-panel-100-amp-siemens-sub-panel.jpg   sub-panel-100_0634.jpg  
Reply With Quote
  #2  
Old 2/5/09, 8:13 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Sub Panel

Quote:
Originally Posted by bhartley View Post
What is wrong in this SUB PANEL???
Well, Buck, it isn't fed with 4 wires, the grounding conductors (grounds)and grounded conductors (neutrals) aren't separated and the grounded conductors (neutrals) aren't isolated. I didn't look beyond that.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 2/5/09, 8:18 AM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Sub Panel

Larry,

Thanks, neither did I. It is amazing what people do.
Reply With Quote
  #4  
Old 2/5/09, 1:14 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: Sub Panel

Is there anything wrong with those smaller wires to the 30 amp breaker using the same conduit as the larger feeder wires? I know it's a short run, does it matter how long the conduit is?



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #5  
Old 2/5/09, 9:18 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

The proper term for that panel is a distribution panel.
Reply With Quote
  #6  
Old 2/6/09, 12:27 AM
Ron C. Bibler Ron C. Bibler is offline
Active Poster
 
Join Date: Mar 2008
Location: Healdsburg Ca
Posts: 105
Please Note: Ron C. Bibler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

The ground feader needs to be marked as a ground.
looks like you have one mis-match breaker? can see very well.
looks like you have sheet rock screws holding the panel to the wall?

Best

Ron
Reply With Quote
  #7  
Old 2/6/09, 6:06 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Sub Panel

I did notice a bond screw and strap lying on the bottom of the sub-panel. They do a better job when properly attached. This raceway is fine with multiple wires in it as long as the conduit fill isn't exceeded.
Reply With Quote
  #8  
Old 2/10/09, 5:45 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

Hi,

Better late than never.

  • The 2#10 lines coming out of the main distribution panel are illegal. By doing this you are feeding a circuit from the sub panel that goes somewhere into your house from the main distribution panel. You cannot use the main distribution panel as a junction box. Put the circuit straight into the sub panel even if you have to extend the cable with using a small junction box.
  • A case or equipment ground should have been installed from the main distribution panel to a main ground lug that seems to be missing. Your panel is grounded with the threaded offset connector but how many people actually sand the paint off the panel for a good ground.
  • The neutral wire isn’t identified with white on both ends.
  • The circuit grounds need to go directly to a ground bus on the case.
  • The three wire on the right side of the panel needs to be on a double pole breaker, not two singles.
  • There is too much insulation on the 2#14 wire coming in at the bottom of the panel.
  • You need to use proper screws to support the panel.
  • The main distribution neutral in the sub panel is already bonded in the main distribution panel. Therefore, your neutrals are bonded. If you use the bonding strap at the bottom of your panel it will create a double bonding situation. The distance is short for the double bonding and wouldn’t pose a threat but double bonding is illegal.
Just my two cents.

Last edited by Michael Thellend; 2/10/09 at 8:03 PM..
Reply With Quote
  #9  
Old 2/12/09, 7:31 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Sub Panel

Quote:
Originally Posted by Michael Thellend View Post
Hi,
  • The circuit grounds need to go directly to a ground bus on the case.
Why wouldn't they have put a ground bus in that sub-panel, or am I missing it.
Reply With Quote
  #10  
Old 2/12/09, 7:53 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

Hi John,

Well, I just asked in another thread for a Sparky to clarify something with me. I didn't realize till seeing a second panel here that the grounds are always tied with the neutrals in the USA.

In Canada they're not. Neutrals go to neutral bar screws and grounds go to the ground bar screws. Bonding takes place with a jumper. All thought I do have a keen eye for electrical deficiencies, I believe I screwed up here. I will know for the future if I have my question answered.

Mike

Last edited by Michael Thellend; 2/12/09 at 8:05 PM..
Reply With Quote
  #11  
Old 2/12/09, 8:05 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

Ok,

I found a panel here in the threads that have the grounds attached to a ground bar. So maybe I'm not mistaken after all.

http://www.nachi.org/forum/f19/need-trained-eye-37175/

I guess maybe the grounds are supposed to be grounded to the box and bonding is taking place in the main distribution panel or main disconnect. I know one thing for sure, if the system is bonded somewhere else then these grounds shouldn't be on the neutrals here.

Neutrals are current carrying conductors. If you tie the bare ground onto a neutral the bare ground becomes a current carrying conductor as well. Grounds shouldn't carry current except under a fault condition.The only place that it should meet the neutral is at the bonding point to take the fault current to earth ground. Anything ahead of that and you possibly have current in your walls on bare grounds. A neutral is insulated for a reason. Why would you connect them together at the neutral bar???

Darn it, I just looked at the panel again and the neutral bar doesn't appear to be isolated from the case. So I'm back to square 1.

Where's the Sparky? lol

Mike

Last edited by Michael Thellend; 2/12/09 at 9:38 PM..
Reply With Quote
  #12  
Old 2/12/09, 9:27 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

HI,

I did a little homework on US installs.

A normal service entrance should have the main service disconnect bonded with a jumper. Neutral and ground (electrode or street side water main ground) are connected and isolated from the main service disconnect. This is the only point where the ground and neutral should touch together in a system.

From the main service disconnect you enter your panel and the neutral should go on the neutral bar and the grounds on a ground bar and there should be no jumper to the panels enclosure. I provided a picture of a panel but it's a pic from the US.

This is what I'm talking about, it should be like this and I don't know why most of the panels I see here are connected differently.

If there was no main disconnect ahead of a combination panel with main breaker, then the jumper would be installed in the panel and the grounds and neutrals would still be wired as shown in the panel. We never tie neutrals to grounds at two points in a system let alone 1, it's a hazard.

Mike


Last edited by Michael Thellend; 2/12/09 at 11:24 PM..
Reply With Quote
  #13  
Old 2/13/09, 10:20 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Sub Panel

Michael..
Many times the main panel is considered the disconnect. Houses were not always built with a breaker/disconnect on the meter can or a fused disconnect in between the meter and the main panel. It is quite common to find the grounding and grounded conductors together on the same bar. When they're under the same lug on the bar, that's the no-no.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #14  
Old 2/13/09, 3:04 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Sub Panel

Michael
First of all, thanks for all the research.
I think it's the same in Canada as in the US.
In the main panel with the disconnect, the neutral and ground come together.
In a sub-panel, the neutrals and grounds are separated, and the neutrals are isolated from the panel as well.
I was just wondering why, since the picture is of a sub-panel, there is no bus bar for the grounds.
Reply With Quote
  #15  
Old 2/13/09, 10:14 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

Quote:
Originally Posted by jallingham View Post
Michael
First of all, thanks for all the research.
I think it's the same in Canada as in the US.
In the main panel with the disconnect, the neutral and ground come together.

In a sub-panel, the neutrals and grounds are separated, and the neutrals are isolated from the panel as well.
Hi John,

You're welcome about the research.

Yes the main neutral (service entrance) and main ground (earth ground) come together on the main neutral bar lugs and these lugs are isolated from the panel enclosure except by a jumper. If there is no disconnect ahead of the panel and the panel is the disconnecting means this is correct.

The circuit grounds do not go on the neutral bar screws in this type of installation nor do they go together in a sub-panel installation. The circuit grounds are separated by a neutral bar jumper to ground in the main distribution panel. The sub panel never has the jumper installed and the grounds go on the enclosures (panel casing) ground bar and are completely separated from the neutrals.

This is what I tried to explain in my last post.

Regards,

Mike

Last edited by Michael Thellend; 2/13/09 at 10:30 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM