  #16  
Old 2/14/09, 12:03 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Sub Panel

Quote:
Originally Posted by Michael Thellend View Post
Hi John,

The sub panel never has the jumper installed and the grounds go on the enclosures (panel casing) ground bar and are completely separated from the neutrals.

This is what I tried to explain in my last post.

Regards,

Mike
But that's what I'm saying, I don't see the ground bar in that sub panel.
Reply With Quote
  #17  
Old 2/14/09, 2:29 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

Quote:
Originally Posted by Michael Thellend View Post
Hi,

Better late than never.

  • The 2#10 lines coming out of the main distribution panel are illegal. By doing this you are feeding a circuit from the sub panel that goes somewhere into your house from the main distribution panel. You cannot use the main distribution panel as a junction box. Put the circuit straight into the sub panel even if you have to extend the cable with using a small junction box.
.
Michael, where did you get this info? I do not believe this is a violation, at least in the U.S.
Reply With Quote
  #18  
Old 2/15/09, 1:12 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

Quote:
Originally Posted by brian winkle View Post
Michael, where did you get this info? I do not believe this is a violation, at least in the U.S.
Canadian Electrical Code

12-3034 - Wiring Space Enclosures

Enclosures for overcurrent devices, controllers, and externally operated switches shall not be used as junction boxes, troughs, or raceways for conductor feeding through to another apparatus.

Well you're right, this is a Canadian code.

Mike
Reply With Quote
  #19  
Old 2/15/09, 1:21 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

Quote:
Originally Posted by jallingham View Post
But that's what I'm saying, I don't see the ground bar in that sub panel.
Hi John,

I know, I just wanted to re-interate on the fact that grounds from the circuits in the main distribution panel never touch neutrals either.

So almost all of the panels I've seen here in this forum thus far have the circuit grounds wired to the neutral bar screws and they're not correctly wired.

Mike
Reply With Quote
  #20  
Old 2/15/09, 11:43 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Sub Panel

Quote:
Originally Posted by Michael Thellend View Post
Hi John,

I know, I just wanted to re-interate on the fact that grounds from the circuits in the main distribution panel never touch neutrals either.
If you are trying to say that the neutrals and grounding conductors can't be on the same bar in the main dist. panel, you are incorrect. In the States, anyway. If you are trying to say that the neutrals and grounding conductors can't be under the same lug, then you are correct. I'm just a little confused on how you worded your statement.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook

Last edited by jwicklander; 2/15/09 at 11:48 PM..
Reply With Quote
  #21  
Old 2/18/09, 1:32 PM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

Quote:
Originally Posted by jwicklander View Post
If you are trying to say that the neutrals and grounding conductors can't be on the same bar in the main dist. panel, you are incorrect. In the States, anyway. If you are trying to say that the neutrals and grounding conductors can't be under the same lug, then you are correct. I'm just a little confused on how you worded your statement.

Jeff
neutrals and grounding conductors can't be under the same lug, then you are correct.

I did mean it the other way too, they should be separated by a bonding jumper if the panel is the main disconnecting means in the service entrance (no disconnect ahead). So if this is your practice in the US then I'm wrong here but theoretically when it comes to bonding and grounding methods I'm not.

Mike

Last edited by Michael Thellend; 2/19/09 at 9:08 AM..
Reply With Quote
  #22  
Old 2/20/09, 5:15 PM
Marc Benz Marc Benz is offline
Active Poster
 
Join Date: Sep 2007
Location: Paris France for now
Posts: 138
Please Note: Marc Benz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel

The other thing that as Mike did expain here in the USA for all subpanels useage the netral and ground must be seperated.

I know it kinda common mistake I did ran into more than once some case some peoples don't relized the code are allready written in there.

Quick call to electrician will take care the issue there.

Merci,Marc
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 2:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts