Default Sub Panel Amps

Are there any cases where a sub panel can have higher amps then the main?
Say the main is an old 60 amp service. I go in the house, find a sub panel in the closet and it has 100amp breaker with 4 breakers under it. Is this correct?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #2  
Old 9/28/06, 9:58 AM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel Amps

not sure of what the code is, but your weakest link is the governing factor. (60 amp main breaker in main panel)

your 100 amp sub would never be given the opportunity to draw it's potential amperage.

i guess if the sub was put in with the though of upgrading the main eventuall, it would make sense of why it was installed.

oh, and the sub in a closet is wrong, too.

Last edited by ccbrands1; 9/28/06 at 10:55 AM..
Reply With Quote
  #3  
Old 9/30/06, 11:07 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sub Panel Amps

Mark,

While anything is possible the factor here would be the Conductor Size feeding that 100A panel in the " Closet " which in itself would be a problem....even if before it was mandated...just a safety issue you should call out..but I digress....

If the panel itself in the " Closet" is rated for 100A.....which being rated alone for that is fine.......you would need to know the following:

1.) If the panel is protected by a 60A breaker in the MAIN...and the conductors going to the "sub" are rated for the 60A...it would be fine for the panel in the " Closet" to be rated at 100A....

2.) Since panels are not based on the TOTAL number of breakers listed amps...but more in diversified loads......just having the (4) breakers in it does not tell us anything.......

Question...is the panel a MLO or does it have a MB?...regardless make sure the sub panels feeder conductors are sized correctly and again just because the panel is rated at 100A...does not mean it's capacity is 100A....remember the 60A breaker feeding it will limit that...as well as the conductor size...make sure it meets the 60A capacity of the breaker feeding it.

Hope this helps



Paul W. Abernathy
Reply With Quote
  #4  
Old 9/30/06, 11:11 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel Amps

But you only have 60 amp service so the 100 amp sub panel can never pull more then 60 amps right?

This would only change should the incoming service be upgraded to 100 amp right?
Reply With Quote
  #5  
Old 9/30/06, 11:29 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sub Panel Amps

Raymond-

I went into more detail but basically the long and short is....the 60A main breaker feeding the SUB panel is the ruling factor.....I just would like them to verify the actual "FEEDER" to the sub panel was also rated for the 60A as well.

But yes...if the 60A Breaker is protecting a "sub" and even if the panel itself is rated at 100A ( which really means nothing in this case )....the service is still 60A.......the capacity of the service is still 60A...regardless of the "sub" panels rating......



Paul W. Abernathy
Reply With Quote
  #6  
Old 9/30/06, 11:52 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub Panel Amps

Thanks Paul. I confuse easily!
Reply With Quote
  #7  
Old 10/1/06, 12:05 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sub Panel Amps

lol...hey don't we all...



Paul W. Abernathy
Reply With Quote
  #8  
Old 10/1/06, 9:47 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,153
Default Re: Sub Panel Amps

me too




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 2:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts