Came across a sub-panel with 100 amp breaker. The feed is from main panel is 40 amps which is on breaker. The circuits are all protected by breakers.

Would it make any difference that sub-panel has 100 amp breaker when only 40 amp feed. All the circuits are protected by appropriate breakers.

I find this odd and the panel was probably used and came with breakers already installed.

Appreciate thoughts and input.



Roger Frost CBCO
Barrie Home Inspector
Alliston Home Inspections
Orillia House Inspector
Barrie, ON
(705)795-8255
Reply With Quote
Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/22/11, 2:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Sub-Panel Breaker

Often, the 100 amp breaker is simply being used as a disconnect for the distribution panel. This would be the case if the feeders from the service equipment were tied to that breaker.

If the 100A breaker was being used as OCPD for another device, then it is obsolete and indicative of repairs/modifications from unqualified persons. The device will trip the 40A breaker at the service equipment before it will trip the 100A breaker.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/22/11, 2:47 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Sub-Panel Breaker

Quote:
Originally Posted by rfrost View Post
Came across a sub-panel with 100 amp breaker. The feed is from main panel is 40 amps which is on breaker. The circuits are all protected by breakers.

Would it make any difference that sub-panel has 100 amp breaker when only 40 amp feed. All the circuits are protected by appropriate breakers.

I find this odd and the panel was probably used and came with breakers already installed.

Appreciate thoughts and input.
Hi Roger

What size conductor is feeding the 100 Amp Breaker connected to the 40 Amp?
Reply With Quote
  #4  
Old 8/22/11, 3:25 PM
Roger A. Frost's Avatar
Roger A. Frost Roger A. Frost is offline
InterNACHI Member
 
Join Date: May 2005
Location: Barrie, On
Posts: 74
Default Re: Sub-Panel Breaker

Number 8 wire, supplied from 40 amp breaker in main panel.



Roger Frost CBCO
Barrie Home Inspector
Alliston Home Inspections
Orillia House Inspector
Barrie, ON
(705)795-8255
Reply With Quote
  #5  
Old 8/22/11, 4:23 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub-Panel Breaker

Quote:
Originally Posted by rfrost View Post
Number 8 wire, supplied from 40 amp breaker in main panel.

So far so good. Are the lugs on the 100 amp CB listed for #8 conductors?
Reply With Quote
  #6  
Old 8/23/11, 8:37 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Sub-Panel Breaker

Quote:
Originally Posted by Robert Meier View Post
So far so good. Are the lugs on the 100 amp CB listed for #8 conductors?
Good point but likely not a significant issue for an HI if there is a solid connection.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #7  
Old 8/24/11, 7:11 AM
Roger A. Frost's Avatar
Roger A. Frost Roger A. Frost is offline
InterNACHI Member
 
Join Date: May 2005
Location: Barrie, On
Posts: 74
Default Re: Sub-Panel Breaker

Thanks for thoughts. Noted the 100 amp dis-connect as observation that it was over-rated and would not be typically used on 40 amp feed.



Roger Frost CBCO
Barrie Home Inspector
Alliston Home Inspections
Orillia House Inspector
Barrie, ON
(705)795-8255
Reply With Quote
  #8  
Old 8/24/11, 7:49 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Sub-Panel Breaker

Quote:
Originally Posted by rfrost View Post
Thanks for thoughts. Noted the 100 amp dis-connect as observation that it was over-rated and would not be typically used on 40 amp feed.
I wouldn't say the 100A breaker/disconnect is overrated since the #8 wires are adequately protected in the service panel ... but it may not have been tested for terminating the #8 wire which means there may be a potential for a poor connection, which should be checked if you didn't

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 8/25/11 at 11:13 AM..
Reply With Quote
  #9  
Old 8/24/11, 9:56 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub-Panel Breaker

Quote:
Originally Posted by rfrost View Post
Thanks for thoughts. Noted the 100 amp dis-connect as observation that it was over-rated and would not be typically used on 40 amp feed.
Since it is not needed the rating is irrelevant. Also remember that the 100 amp is the max rating, not a minimum rating. It is serving as a redundant shutoff. You will not find a panel with a 40 amp main unless the panel was being backfeed.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Square D breaker in a General Electric panel smorris1 Electrical Inspections 2 10/26/10 8:55 PM
main breaker panel location gbaccus Electrical Inspections 4 2/19/09 3:15 PM
Breaker Panel Warranty jallingham Electrical Inspections 4 2/16/09 5:49 PM
White Wire to Breaker and Splice Inside Panel maitai11 Electrical Inspections 31 9/5/06 11:09 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts