Came across a sub-panel with 100 amp breaker. The feed is from main panel is 40 amps which is on breaker. The circuits are all protected by breakers.
Would it make any difference that sub-panel has 100 amp breaker when only 40 amp feed. All the circuits are protected by appropriate breakers. I find this odd and the panel was probably used and came with breakers already installed. Appreciate thoughts and input. Roger Frost CBCO Barrie Home Inspector Alliston Home Inspections Orillia House Inspector Barrie, ON (705)795-8255 |
| Need a home inspection in Florida? Check out InterNACHI's listing of Florida certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Often, the 100 amp breaker is simply being used as a disconnect for the distribution panel. This would be the case if the feeders from the service equipment were tied to that breaker.
If the 100A breaker was being used as OCPD for another device, then it is obsolete and indicative of repairs/modifications from unqualified persons. The device will trip the 40A breaker at the service equipment before it will trip the 100A breaker. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Quote:
What size conductor is feeding the 100 Amp Breaker connected to the 40 Amp? Dale Duffy Inspect Arizona Companies, Inc. Phoenix Commercial Building Inspectors, Inc. Phoenix Thermal Imaging, Inc. Infraspection Certified Thermographer 602.402.5305 Home Hints eNews
InterNACHI 2007 U.S.A Member of the Year National Association of Commercial Building Inspectors, Inc. |
|
#4
|
||||
|
||||
|
Number 8 wire, supplied from 40 amp breaker in main panel.
Roger Frost CBCO Barrie Home Inspector Alliston Home Inspections Orillia House Inspector Barrie, ON (705)795-8255 |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
So far so good. Are the lugs on the 100 amp CB listed for #8 conductors? |
|
#6
|
||||
|
||||
|
Good point but likely not a significant issue for an HI if there is a solid connection.
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#7
|
||||
|
||||
|
Thanks for thoughts. Noted the 100 amp dis-connect as observation that it was over-rated and would not be typically used on 40 amp feed.
Roger Frost CBCO Barrie Home Inspector Alliston Home Inspections Orillia House Inspector Barrie, ON (705)795-8255 |
|
#8
|
||||
|
||||
|
Quote:
JMO & 2-Nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 8/25/11 at 11:13 AM.. |
|
#9
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since it is not needed the rating is irrelevant. Also remember that the 100 amp is the max rating, not a minimum rating. It is serving as a redundant shutoff. You will not find a panel with a 40 amp main unless the panel was being backfeed.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Square D breaker in a General Electric panel | smorris1 | Electrical Inspections | 2 | 10/26/10 8:55 PM |
| main breaker panel location | gbaccus | Electrical Inspections | 4 | 2/19/09 3:15 PM |
| Breaker Panel Warranty | jallingham | Electrical Inspections | 4 | 2/16/09 5:49 PM |
| White Wire to Breaker and Splice Inside Panel | maitai11 | Electrical Inspections | 31 | 9/5/06 11:09 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |