Default Sub panel need cover?

greetings,
at a friends pre-listing inspection i saw they had a small sub panel that was installed when a new glam bath was put in the upstairs master. the sub panel is in a closet peeking thru a cutout in the wall accessable from the crawlspace behind it. (secured properly) hope this makes sense?

there is no cover on the panel and they asked me if it needed one befause a realtor told them it did. i told them that it didnt. any comments?

thanks,
Bob
Reply With Quote
  #2  
Old 2/25/06, 11:43 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel need cover?

It needs one.
Reply With Quote
  #3  
Old 2/25/06, 11:49 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sub panel need cover?

Depends on its listing. Also, if it's in a clothes closet, it's improper.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 2/25/06, 11:56 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel need cover?

When would a panel not need a cover?
Reply With Quote
  #5  
Old 2/25/06, 3:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sub panel need cover?

Quote:
Originally Posted by bkelly1
When would a panel not need a cover?
Are you referring to a dead front cover or a breaker cover?

Most panels have two covers - interior (dead front) and exterior. Several models have only a dead front cover and no exterior, hinged cover.

So it depends on its listing - indoor use or outdoor use.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/26/06, 12:59 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Sub panel need cover?

Quote:
Originally Posted by jpope
Depends on its listing. Also, if it's in a clothes closet, it's improper.
By today's standards.

I think it's Home Depot here that sells a small security bar device to install over the panel so that flammable clothes don't come into contact with it. After all, it's going to be the rare individual who pays thousands of dollars to have the electric panel re-located from the closet to a bedroom wall or somewhere, especially in these older apartment-to-condo conversions.

I've always been curious, though, as to why the AHJ here will allow a complete make-over of an old apartment and allow it to be sold as a new condominium with the only thing not being brought up to date is the location of the electric panel. Doesn't make sense to me.
Reply With Quote
  #7  
Old 2/26/06, 1:05 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel need cover?

Quote:
Originally Posted by bmargiotti
greetings,
at a friends pre-listing inspection i saw they had a small sub panel that was installed when a new glam bath was put in the upstairs master. the sub panel is in a closet peeking thru a cutout in the wall accessable from the crawlspace behind it. (secured properly) hope this makes sense?

there is no cover on the panel and they asked me if it needed one befause a realtor told them it did. i told them that it didnt. any comments?

thanks,
Bob
I took that statement as no cover.. or exposed breakers.
Reply With Quote
  #8  
Old 2/26/06, 1:12 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Sub panel need cover?

Quote:
Originally Posted by rray
I've always been curious, though, as to why the AHJ here will allow a complete make-over of an old apartment and allow it to be sold as a new condominium with the only thing not being brought up to date is the location of the electric panel. Doesn't make sense to me.
Russel...they are doing the same thing here...last month it was a $750.00 a month dump apartment....this month it has new interior paint with a slightly upgraded kitchen and bath for $300,000.00

You can still hear the neighbors upstairs walking across the ceiling and the people next door talking through the walls.
Reply With Quote
  #9  
Old 2/27/06, 10:06 AM
bmargiotti bmargiotti is offline
New User
 
Join Date: Feb 2005
Location: Berea, OH
Posts: 66
Please Note: bmargiotti is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel need cover?

sorry for the confusion. first, this is a cloths closet. and it has a dead cover, just no hinged cover... actually there is no way to attach a hinged cover on it, didnt appear to be made that way.

imagine a panel fixed to the studs behind a wall with a square cut out so the panel (breakers) can peek out. you can open the crawlspace and look in and see the soffits, wiring and the back of the panel.

Bob
Reply With Quote
  #10  
Old 2/27/06, 10:09 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel need cover?

If it has a deadfront and location is out of reach for children I would not write it up.
Reply With Quote
  #11  
Old 2/27/06, 11:11 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Sub panel need cover?

Quote:
Originally Posted by bkelly1
If it has a deadfront and location is out of reach for children I would not write it up.
Sorry if the manufacture made a cover and it is not there write it up just like you would write up a junction box with no cover .
Remember CYA miss it and you are wrong write it up and if they do nothing you have Coverd your *****.
Roy sr
Reply With Quote
  #12  
Old 2/27/06, 4:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sub panel need cover?

Quote:
Originally Posted by bkelly1
If it has a deadfront and location is out of reach for children I would not write it up.
Except for the fact that it's in a clothes closet.

I think it was '96 or '99 when clothes closet was specified, but location near combustibles and working clearance has been addressed for many years.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 2/27/06, 5:32 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sub panel need cover?

I think the biggest concern in this type of thing is the ARC issue that can cause a fire in the event of such a thing happening.

I see a few of panels in closets and basically it was pre-1996 mentality...but again was allowed at one point.....just not so ALLOWED today...

I think it is one of those things.....if it is older and in the 1980's and earlier era which obviously will cover most all of them since the panels should not be in the cloths closets today...lol.......so I would not call if a defect I guess but more a ' Safety Awareness " posting.....

This is what i talk about when I say..."TACTFUL" explanation....you are making notice...not causing alarm......." ie: covering your *****" and stating it for the record in the report...JUST IN CASE....

But by no means is it something a SELLER should upgrade just to agree to sell the house....this is why you do not make it so alarming....just state it if you MUST......as a safety point and let THEM make the choice....

While I DONT LIKE IT.......calling anything like this a defect could slam ya in the eyes of that seller and the agents involved....

Solution......tell them to take out the closet hangers.....relabel the room a storage room....provided their is proper clearance as Jeff pointed out and be done with it...

RR.....I think alot of older places also that have upgrades tend to want to spend less on the electrical...so what they do it upgrade some of the branch....then relocate the closet area....and then relabel the room the panel is in.....thus getting around the code requirement upon upgrade.



Paul W. Abernathy

Last edited by pabernathy; 2/27/06 at 5:36 PM..
Reply With Quote
  #14  
Old 3/5/06, 4:28 PM
bmargiotti bmargiotti is offline
New User
 
Join Date: Feb 2005
Location: Berea, OH
Posts: 66
Please Note: bmargiotti is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel need cover?

thanks for the thoughts guys!

Bob
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
It's not necassary to remove Electrical Panel Cover. dvalley Electrical Inspections 15 7/3/07 3:22 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 2:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts