My reporting system (AHIT) has a couple of ticky box yes/no items and I'm not sure I know the distinction.
One says "neutral/ground separated" and the other says "neutral isolated". What are they getting at? |
|
#2
|
||||
|
||||
|
Sub-panels must have a bonded ground bus and a floating neutral bus. That is, the neutral bus must contain only neutrals and must not be bonded to the cabinet.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#3
|
|||
|
|||
|
Yes but how are the two questions different?
|
|
#4
|
||||
|
||||
|
Not sure about the meaning of the questions. Not familiar with your software. Sorry.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#5
|
|||
|
|||
|
Quote:
What are they getting at? They are asking about remote distribution panels (sub panels). "neutral/ground separated" (from each other). "neutral isolated" (from the panel board). InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#6
|
||||
|
||||
|
I would get rid of the AHIT paper or computer report system and use one you can create yourself like HIP. (Home Inspector Pro)
I used to use AHIT and I found it "user unfriendly" |
|
#7
|
||||
|
||||
|
Quote:
Does that make sense? Marcel Gratton, NACHI04011210, CMI On The Level Inspection Gatineau, Québec http://www.onthelevelinspection.com/ |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
The neutrals and grounds can be separated (on separate bars), but the neutral may not necessarily be isolated (from the panel's metal) unless the proper steps were taken. Thus, two check boxes.
|
|
#9
|
|||
|
|||
|
Maybe it is for Canadian inspectors. I think I read on this board once that it is a Canadian requirement that neutrals and grounds must be installed on separate buses in the main panel. This is not a requirement in the US, and 99% of the main panels I inspect have the neutrals and grounds installed on the same bus bar(s).
|
|
#10
|
||||
|
||||
|
No, that is not correct. The neutrals and grounds do not have to be on separate buses in the main panel.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
||||
|
||||
|
Quote:
Different country, different rules; rule 10-210(1)(b)... Marcel Gratton, NACHI04011210, CMI On The Level Inspection Gatineau, Québec http://www.onthelevelinspection.com/ Last edited by mgratton; 1/3/09 at 5:16 PM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Sub panel question | smcintire | Electrical Inspections | 2 | 4/13/08 9:20 PM |
| Electrical Safety Foundation International Links | jtedesco1 | Electrical Inspections | 5 | 12/8/07 3:10 PM |
| Panel Question | gmckenzie | Electrical Inspections | 9 | 8/24/07 1:25 AM |
| Service Panel question for board sparkies | pbolliger | Electrical Inspections | 8 | 5/14/06 9:24 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |