Default Sub-panel Question

My reporting system (AHIT) has a couple of ticky box yes/no items and I'm not sure I know the distinction.
One says "neutral/ground separated" and the other says "neutral isolated".
What are they getting at?
Reply With Quote
  #2  
Old 1/2/09, 2:02 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Sub-panel Question

Sub-panels must have a bonded ground bus and a floating neutral bus. That is, the neutral bus must contain only neutrals and must not be bonded to the cabinet.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 1/2/09, 2:07 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 377
Default Re: Sub-panel Question

Quote:
Originally Posted by jfunderburk View Post
Sub-panels must have a bonded ground bus and a floating neutral bus. That is, the neutral bus must contain only neutrals and must not be bonded to the cabinet.
Yes but how are the two questions different?
Reply With Quote
  #4  
Old 1/2/09, 2:11 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Sub-panel Question

Not sure about the meaning of the questions. Not familiar with your software. Sorry.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 1/2/09, 3:20 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,740
Default Re: Sub-panel Question

Quote:
Originally Posted by jallingham View Post
My reporting system (AHIT) has a couple of ticky box yes/no items and I'm not sure I know the distinction.
One says "neutral/ground separated" and the other says "neutral isolated".
What are they getting at?

Quote:
Originally Posted by jallingham View Post
...but how are the two questions different?
What are they getting at? They are asking about remote distribution panels (sub panels).

"neutral/ground separated" (from each other).

"neutral isolated" (from the panel board).



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #6  
Old 1/2/09, 5:11 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,466
Default Re: Sub-panel Question

I would get rid of the AHIT paper or computer report system and use one you can create yourself like HIP. (Home Inspector Pro)

I used to use AHIT and I found it "user unfriendly"
Reply With Quote
  #7  
Old 1/2/09, 6:13 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: Sub-panel Question

Quote:
Originally Posted by jallingham View Post
My reporting system (AHIT) has a couple of ticky box yes/no items and I'm not sure I know the distinction.
One says "neutral/ground separated" and the other says "neutral isolated".
What are they getting at?
In the main distribution panel the neutral/ground should be separated (on different bus but not isolated) while in a sub-panel the neutral should be isolated (from ground/cabinet).

Does that make sense?



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #8  
Old 1/2/09, 6:58 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub-panel Question

The neutrals and grounds can be separated (on separate bars), but the neutral may not necessarily be isolated (from the panel's metal) unless the proper steps were taken. Thus, two check boxes.
Reply With Quote
  #9  
Old 1/3/09, 3:36 AM
Paul Dickerson Paul Dickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 327
Default Re: Sub-panel Question

Maybe it is for Canadian inspectors. I think I read on this board once that it is a Canadian requirement that neutrals and grounds must be installed on separate buses in the main panel. This is not a requirement in the US, and 99% of the main panels I inspect have the neutrals and grounds installed on the same bus bar(s).
Reply With Quote
  #10  
Old 1/3/09, 11:34 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Sub-panel Question

Quote:
Originally Posted by mgratton View Post
In the main distribution panel the neutral/ground should be separated (on different bus but not isolated) while in a sub-panel the neutral should be isolated (from ground/cabinet).

Does that make sense?
No, that is not correct. The neutrals and grounds do not have to be on separate buses in the main panel.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 1/3/09, 6:05 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: Sub-panel Question

Quote:
Originally Posted by jfunderburk View Post
No, that is not correct. The neutrals and grounds do not have to be on separate buses in the main panel.
Joe,

Different country, different rules; rule 10-210(1)(b)...



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/

Last edited by mgratton; 1/3/09 at 6:16 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sub panel question smcintire Electrical 2 4/13/08 10:20 PM
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 4:10 PM
Panel Question gmckenzie Electrical 9 8/24/07 2:25 AM
Service Panel question for board sparkies pbolliger Electrical 8 5/14/06 10:24 AM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 6:53 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts