Default Sub panel rating-what does it mean?

The inspection yesterday was interesting. The combined cottages had 3 sub-panels, each sub-panel has a 100AMP rating and no main breaker at the panel. If the panel is rated for 100AMP's, does that mean if you add up the installed breaker AMPS, 20A, 15A, 60A, 20A, 20A, 15A, the panel is overloaded?

Thanks,
Attached Thumbnails
sub-panel-rating-does-mean-img_13585.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 5/4/08, 9:26 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel rating-what does it mean?

No

It means that the connected load can not be more than 100 amps.

Go look at your service panel and see if the total of all the breakers installed do not equal more than the main
Reply With Quote
  #3  
Old 5/4/08, 10:43 AM
gmortensen gmortensen is offline
New User
 
Join Date: Aug 2007
Location: Cambridge, ON
Posts: 94
Please Note: gmortensen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel rating-what does it mean?

As long as the 100 amp feed wires have over current protection for 100 amps at the main service. It should be OK. Is there no means of diconnection in each cottage? The wires tapped under the feeders looks scarry!!!
Reply With Quote
  #4  
Old 5/4/08, 10:47 AM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Sub panel rating-what does it mean?

there is no located main breaker, the whole system is a little scary, one panel has double tapped main lugs, 2 have knock-outs missing, wires not secure at panel and multiple double taps.

I have recommended a Lic. Elec. evaluate further.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #5  
Old 5/4/08, 11:08 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel rating-what does it mean?

Quote:
Originally Posted by sfalvey
there is no located main breaker,
Yes this is very bad.

Quote:
Originally Posted by sfalvey
I have recommended a Lic. Elec. evaluate further.
Great call
Reply With Quote
  #6  
Old 5/4/08, 11:27 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel rating-what does it mean?

Quote:
Originally Posted by gmortensen
As long as the 100 amp feed wires have over current protection for 100 amps at the main service. It should be OK. Is there no means of diconnection in each cottage? The wires tapped under the feeders looks scarry!!!
The wire taped in the bottom of the panel is the neutral. It is commonly seen without tape over its entire length.
Reply With Quote
  #7  
Old 5/4/08, 11:30 AM
Bruce D. Pinel Bruce D. Pinel is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: North Kingstown, RI
Posts: 173
Default Re: Sub panel rating-what does it mean?

Hard to tell but is the neutral buss isolated from the ground buss?
Reply With Quote
  #8  
Old 5/4/08, 12:17 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Sub panel rating-what does it mean?

NO, there is only one bus bar and both neutrals and grounds are mounted.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #9  
Old 5/4/08, 12:32 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Sub panel rating-what does it mean?

Scott , hate to start you over on this, but....
If these go straight from the meter they are no subpanels.
Do they feed directly from their own meters?

Is it possible that the 60 is the main breaker.?

If those are feeders at the 60 amp breakers , from what I can tell here they appear to be aluminum.

Is the panel rated for aluminum (CU)?

Remember the five throw rule also.

Did you see the meters?

Sometimes the meter outside has breakers.
Reply With Quote
  #10  
Old 5/5/08, 5:43 PM
sfalvey sfalvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Sub panel rating-what does it mean?

Hi Robert,

There is only one meter on the outside. From what I can tell, the meter feeds inside the "first" house into one of those enclosed metal raceways (for lack of a better description and actaul name of system component) then from the raceway it branches off to the other two identical panels.

I guess I should have pulled off the raceway cover, but I really didn't want to go there.

I did not look for the Aluminum rating, but will remember for next time because the feeders are Aluminum.

The meter does not have a breaker.

I apologize for not having the correct photo of the layout on the inside showing the raceway, I thought I got it when I took the photo.

Thanks for the questions.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #11  
Old 5/5/08, 9:31 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel rating-what does it mean?

Quote:
Originally Posted by sfalvey
Hi Robert,

There is only one meter on the outside. From what I can tell, the meter feeds inside the "first" house into one of those enclosed metal raceways (for lack of a better description and actaul name of system component) then from the raceway it branches off to the other two identical panels.

This sounds like what is called a trough.

I guess I should have pulled off the raceway cover, but I really didn't want to go there.

I did not look for the Aluminum rating, but will remember for next time because the feeders are Aluminum.

I do not remember seeing a panel that was not rated for use with AL.

The meter does not have a breaker.

I apologize for not having the correct photo of the layout on the inside showing the raceway, I thought I got it when I took the photo.

Thanks for the questions.


added
Reply With Quote
  #12  
Old 5/5/08, 9:51 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Sub panel rating-what does it mean?

Scott if you have three Cottages or three distinct buildings, these are not Remote distrubution panels (sub panels).

Each Main panel should have its own ground rod.

If you looked around you would have or should have seen this.

Why only one meter?

Was it single family or rental with Landlord footing the bill?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Panel main rating sfalvey Electrical Inspections 7 9/24/06 8:46 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts