Old 4/18/06, 9:07 AM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
Default sub-panel or second service panel?
Called out the double tap, missing bushings and three conductors only to the sub-panel. Although I'm calling this a sub-panel it looks like the panel is not suitable as a sub-panel.
Do you agree that the double tap should be eliminated, bushings installed, the sub-panel replaced and four conductors used to feed it?
sub-panel-second-service-panel-dsc00020.jpg   sub-panel-second-service-panel-dsc00021.jpg   sub-panel-second-service-panel-dsc00022.jpg   sub-panel-second-service-panel-dsc00023.jpg
John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net
John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Old 4/18/06, 9:18 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sub-panel or second service panel?
Nuetral wire wouldn't hurt to be marked. The sub panel can have a ground bar added, the whole panel doesn't have to be replaced. The nuetral bar is already isolated. The 2 small circles on the other side are small holes under them for the ground bar mount. (most likely)
Old 4/18/06, 10:33 AM
Pierre Belarge Pierre Belarge is offline
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Angry Re: sub-panel or second service panel?
John
You have found a real mess here. In my professional opinion a DISASTER waiting to happen!!!
If the first panel is the service panel, then those taps are service taps.
The lugs they are terminated in are not designed for that type of connection.
It makes the conductors heading toward the "subpanel" service conductors and they are not protected by any overcurrent device - very dangerous!!!
What kind of wiring method is this - cable, raceway, open conductors?
The subpanel is required to have 4 conductors installed. 2-phase conductor, 1-neutral conductor, and an equipment ground conductor. You could suggest they eliminate one phase conductor and have the conductor terminated to a single pole breaker in the service panel... that would make the "subpanel" a single phase panel, no 240Volts available.
The conductors are not properly identified. Neutrals and equipment grounds in the "subpanel" need to be isolated, separated.
Taking another look at the "subpanel" installation... the way it is wired, the circuit breakers will not trip due to any kind of GROUND FAULT, as there is no equipment ground conductor or bond for the fault current to follow back to the panel supplying the "subpanel"
Very, very bad installation... if I were you I would recommend a professionally licensed electrical contractor to fix this IMMEDIATELY!!!
This will most likely be a fairly expensive change
Old 4/18/06, 11:36 AM
Jeffrey R. Pope's Avatar
Jeeze John. . .
FUBAR
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 4/18/06, 1:27 PM
Paul W. Abernathy's Avatar
Crapola....That panel DOES have some serious issues...
From the triple lugged Neutrals, to the Double Tapped Main Lugs and not to forget the cencentric rings on that panel are not in contact at all....bushing would probably do no good here....it is a mess...
As well the sub-panel is totally not installed correctly.....as Pierre has stated.....
I wont bother wish us listing all the things wrong here......90% of them are obvious but yes...DEFER to an Electrical Contractor right away....
BTW.....notice all the slimline tandoms....I am sure THIS panel is rated for a certain number of OCPD....safe to say it is beyond what the panel is listed for.....
Paul W. Abernathy,CMI,CPI,CME
Old 4/18/06, 1:37 PM
Patrick Bolliger's Avatar
Question Re: sub-panel or second service panel?
Is copper and aluminum on the double tap a " special " issue on top of the rest.. Is this a double trouble corrosion issue...
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 4:10 PM
Service Panel Quiz? hmcclard Electrical Inspections 5 10/25/07 12:53 AM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM