Default sub-panel or second service panel?

Called out the double tap, missing bushings and three conductors only to the sub-panel. Although I'm calling this a sub-panel it looks like the panel is not suitable as a sub-panel.

Do you agree that the double tap should be eliminated, bushings installed, the sub-panel replaced and four conductors used to feed it?
Attached Thumbnails
sub-panel-second-service-panel-dsc00020.jpg   sub-panel-second-service-panel-dsc00021.jpg   sub-panel-second-service-panel-dsc00022.jpg   sub-panel-second-service-panel-dsc00023.jpg  



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #2  
Old 4/18/06, 8:18 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sub-panel or second service panel?

Nuetral wire wouldn't hurt to be marked. The sub panel can have a ground bar added, the whole panel doesn't have to be replaced. The nuetral bar is already isolated. The 2 small circles on the other side are small holes under them for the ground bar mount. (most likely)
Reply With Quote
  #3  
Old 4/18/06, 9:33 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Angry Re: sub-panel or second service panel?

John
You have found a real mess here. In my professional opinion a DISASTER waiting to happen!!!

If the first panel is the service panel, then those taps are service taps.
The lugs they are terminated in are not designed for that type of connection.

It makes the conductors heading toward the "subpanel" service conductors and they are not protected by any overcurrent device - very dangerous!!!

What kind of wiring method is this - cable, raceway, open conductors?

The subpanel is required to have 4 conductors installed. 2-phase conductor, 1-neutral conductor, and an equipment ground conductor. You could suggest they eliminate one phase conductor and have the conductor terminated to a single pole breaker in the service panel... that would make the "subpanel" a single phase panel, no 240Volts available.

The conductors are not properly identified. Neutrals and equipment grounds in the "subpanel" need to be isolated, separated.

Taking another look at the "subpanel" installation... the way it is wired, the circuit breakers will not trip due to any kind of GROUND FAULT, as there is no equipment ground conductor or bond for the fault current to follow back to the panel supplying the "subpanel"

Very, very bad installation... if I were you I would recommend a professionally licensed electrical contractor to fix this IMMEDIATELY!!!
This will most likely be a fairly expensive change

Last edited by Pierre Belarge; 4/18/06 at 9:38 AM..
Reply With Quote
  #4  
Old 4/18/06, 10:36 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: sub-panel or second service panel?

Jeeze John. . .

FUBAR



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 4/18/06, 12:27 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: sub-panel or second service panel?

Crapola....That panel DOES have some serious issues...

From the triple lugged Neutrals, to the Double Tapped Main Lugs and not to forget the cencentric rings on that panel are not in contact at all....bushing would probably do no good here....it is a mess...

As well the sub-panel is totally not installed correctly.....as Pierre has stated.....

I wont bother wish us listing all the things wrong here......90% of them are obvious but yes...DEFER to an Electrical Contractor right away....

BTW.....notice all the slimline tandoms....I am sure THIS panel is rated for a certain number of OCPD....safe to say it is beyond what the panel is listed for.....



Paul W. Abernathy

Last edited by pabernathy; 4/18/06 at 12:31 PM..
Reply With Quote
  #6  
Old 4/18/06, 12:37 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Question Re: sub-panel or second service panel?

Is copper and aluminum on the double tap a " special " issue on top of the rest.. Is this a double trouble corrosion issue...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
Service Panel Quiz? hmcclard Electrical Inspections 5 10/24/07 11:53 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 2:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts