Default Sub panel tie in

2002 I believe is when this was done. This is a 200 amp main panel in a detached garage feeding a 200 amp panel in the house. The wires are tied directly into the hot bars at the bottom of the main panel with no breakers at all except the main disconnect at the top. I've never seen this type of hook up before. I know the licensed electricain that was labeled on panel. Although I do not know if he did this. Owner bought this place in '05 so she does not know either. Technically it does follow a disconnect but I'm not sure it is right or wrong this way. Help me out guys.
Attached Thumbnails
sub-panel-tie-heck-3-9-07-056.jpg   sub-panel-tie-heck-3-9-07-060.jpg  
Reply With Quote
  #2  
Old 3/10/07, 8:31 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel tie in

That panel has "feed through lugs". You're fine. As long at the service conductors hit that main breaker first, and not those main lugs, it's correct. The main breaker will kill the power to that panel as well as those feed through lugs. In resi work, you'll normally only see panels with feed through lugs in association with mobiles and modulars.

Your second panel says those conductors are "from main panel". Do you mean they go "to" the panel in the home? That's sorta what I suspect.

I'd sorta like to see some green tape on the black EGC associated with the subfeeder conductors, but it's not the end of the world type of thing.
Reply With Quote
  #3  
Old 3/10/07, 8:36 PM
Scott A. Figert Scott A. Figert is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Cecil, Oh
Posts: 163
Default Re: Sub panel tie in

Thanks Marc I thought it was OK but wanted to know for sure. I'll let the owner know. I really like this message board. You guys are great.
Reply With Quote
  #4  
Old 3/11/07, 9:57 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,789
Default Re: Sub panel tie in

My only question would be on the service panel. It is hard to tell from the picture if the ground and nuetral bars are bonded together.
Reply With Quote
  #5  
Old 3/11/07, 11:45 AM
hmiller's Avatar
hmiller hmiller is offline
Active Poster
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 668
Please Note: hmiller is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel tie in

Marc
The topic of feed through lugs raised a question. I am assuming that this is only acceptable when the service conductor size has not decreased. (Like in the photos posted.)
Reply With Quote
  #6  
Old 3/11/07, 12:02 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Sub panel tie in

I see a lot of cosmteic/logistic stuff like marc said, but I can't see any bonding from the ground bar to cabinet or the neutral. Am I missing it?

[Clearly a chance to use my wiggly. ]

tom
Reply With Quote
  #7  
Old 3/11/07, 12:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel tie in

Quote:
Originally Posted by hmiller
Marc
The topic of feed through lugs raised a question. I am assuming that this is only acceptable when the service conductor size has not decreased. (Like in the photos posted.)
Essentially, you're right, unless the service conductors were grossly oversized for no good reason at all (in which case, the conductors on the subfeed lugs may rightfully visually be smaller). The feed through lugs will be protected by whatever size main is in that panel. As long as the conductors installed on the feed through lugs are of a gauge that jives with the rating of the main, it's fine. There's a few exceptions, like if the second panel has its own main, and is within a few feet of the panel with feed through lugs, but you're likely to never see a resi installation done that way.
Reply With Quote
  #8  
Old 3/11/07, 12:39 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub panel tie in

Quote:
Originally Posted by tdietrich1
I see a lot of cosmteic/logistic stuff like marc said, but I can't see any bonding from the ground bar to cabinet or the neutral. Am I missing it?
Now that you mention it, when you zoom in, it appears that the main bonding jumper(s) may indeed be missing. I wonder if those yellow chromated screws near the top of each bar enter the panel's backpan? Hard to say. If they do, they probably would have been green. Interesting to talk about, in the mean time.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 4:24 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts