Default Sub-Panel wiring

Main panel feeds this sub panel.
-No over-current protection on sub panel feeders
-Separate grounds and neutrals on sub panel bus bar

What else?
Attached Thumbnails
sub-panel-wiring-104_3769.jpg   sub-panel-wiring-104_3767.jpg  



Tim Wendorff
Triple B Home Inspection, LLC
www.triplebhi.com
262-224-4420

A Southeastern Wisconsin home inspector specializing in residential home inspections and radon testing!
Reply With Quote
Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/22/11, 6:16 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Sub-Panel wiring

Those are both "sub" panels based on what I can see, and they're both wired improperly.

The first picture shows an equipment grounding conductor to the neutral terminal (which is improper) and then a bonding conductor connecting the neutral terminal to the grounding terminal - again, improper.

In your second picture, the equipment grounding conductors are not bonded to the enclosure/panel. They are attached to the isolated neutral terminal, which is improper. In addition, the neutrals and grounds are sharing the same terminations, which is also improper.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/22/11, 7:12 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub-Panel wiring

Judging from the conductor size it appears that the top right 2-pole CB is the main which is backfed. Is there a service disconnect ahead of this panel? If this panel contains the service disconnect then the jumper between the EGC bus and the neutral bus is OK.

Reply With Quote
  #4  
Old 11/22/11, 7:46 PM
Timothy R. Wendorff Timothy R. Wendorff is offline
InterNACHI Member
 
Join Date: May 2010
Location: Hartford, WI
Posts: 67
Default Re: Sub-Panel wiring

Main disconnect is the top right breaker, the top conductors lead to a service panel.



Tim Wendorff
Triple B Home Inspection, LLC
www.triplebhi.com
262-224-4420

A Southeastern Wisconsin home inspector specializing in residential home inspections and radon testing!
Reply With Quote
  #5  
Old 11/22/11, 7:47 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub-Panel wiring

Quote:
Originally Posted by twendorff View Post
Main disconnect is the top right breaker, the top conductors lead to a service panel.
So is this the service? What do you mean by a service panel? Anything past the service disconnect is considered a "subpanel".
Reply With Quote
  #6  
Old 11/22/11, 7:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Sub-Panel wiring

Quote:
Originally Posted by Robert Meier View Post
Judging from the conductor size it appears that the top right 2-pole CB is the main which is backfed.
I considered that, and if that's the case, then the direct tap to the lugs (with no OCPD) is improper.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 11/22/11, 8:00 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub-Panel wiring

Quote:
Originally Posted by jpope View Post
I considered that, and if that's the case, then the direct tap to the lugs (with no OCPD) is improper.
If the 2 pole CB is a back fed main then the conductors under the top lugs would only be protected by that main. You're correct, that unless the installer has complied with a tap rule those condcutors are likely protected at an ampacity that exceeds their value.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aluminum Wiring: Please proof this new inspection article. gromicko Electrical Inspections 11 12/7/09 4:32 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Wiring question in panel dmacy Electrical Inspections 23 2/14/07 11:27 AM


All times are GMT -4. The time now is 8:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts