Main panel feeds this sub panel.
-No over-current protection on sub panel feeders -Separate grounds and neutrals on sub panel bus bar What else? Tim Wendorff Triple B Home Inspection, LLC www.triplebhi.com 262-224-4420 A Southeastern Wisconsin home inspector specializing in residential home inspections and radon testing! |
| Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Those are both "sub" panels based on what I can see, and they're both wired improperly.
The first picture shows an equipment grounding conductor to the neutral terminal (which is improper) and then a bonding conductor connecting the neutral terminal to the grounding terminal - again, improper. In your second picture, the equipment grounding conductors are not bonded to the enclosure/panel. They are attached to the isolated neutral terminal, which is improper. In addition, the neutrals and grounds are sharing the same terminations, which is also improper. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Judging from the conductor size it appears that the top right 2-pole CB is the main which is backfed. Is there a service disconnect ahead of this panel? If this panel contains the service disconnect then the jumper between the EGC bus and the neutral bus is OK.
|
|
#4
|
|||
|
|||
|
Main disconnect is the top right breaker, the top conductors lead to a service panel.
Tim Wendorff Triple B Home Inspection, LLC www.triplebhi.com 262-224-4420 A Southeastern Wisconsin home inspector specializing in residential home inspections and radon testing! |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
So is this the service? What do you mean by a service panel? Anything past the service disconnect is considered a "subpanel".
|
|
#6
|
||||
|
||||
|
I considered that, and if that's the case, then the direct tap to the lugs (with no OCPD) is improper.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
If the 2 pole CB is a back fed main then the conductors under the top lugs would only be protected by that main. You're correct, that unless the installer has complied with a tap rule those condcutors are likely protected at an ampacity that exceeds their value.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Aluminum Wiring: Please proof this new inspection article. | gromicko | Electrical Inspections | 11 | 12/7/09 4:32 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Wiring question in panel | dmacy | Electrical Inspections | 23 | 2/14/07 11:27 AM |