Default Sub-panels - one more time

I've seen many discussions on this subject in general, but have one more (hopefully final) question.... If there is a sub-panel in a remote building, where there is no other conducting path connecting the two, a 3-wire service was acceptable under earlier code editions. My question is - if all the conditions are present to qualify for that exception, should a ground rod be driven at the remote location and be connected to the neutral / ground bus in the sub-panel? TIA



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/22/11, 7:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Sub-panels - one more time

Yes.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 3/22/11, 7:46 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: Sub-panels - one more time

Jeff, I understand that to be required for detached buildings for lightning protection. Is that correct?
Reply With Quote
  #4  
Old 3/22/11, 8:21 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub-panels - one more time

Quote:
Originally Posted by mcyr View Post
Jeff, I understand that to be required for detached buildings for lightning protection. Is that correct?
Yes, that's correct. I would add one thing, a ground rod is not required but a grounding electrode is. It could be something other than a rod. Here's what the NEC has to say about why things are grounded:

Quote:
250.4 General Requirements for Grounding and Bonding.
The following general requirements identify what grounding and bonding of electrical systems are required to accomplish. The prescriptive methods contained in Article 250 shall be followed to comply with the performance requirements of this section.
(A) Grounded Systems.
(1) Electrical System Grounding. Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation.
FPN: An important consideration for limiting the imposed voltage is the routing of bonding and grounding conductors so that they are not any longer than necessary to complete the connection without disturbing the permanent parts of the installation and so that unnecessary bends and loops are avoided.
(2) Grounding of Electrical Equipment. Normally non–current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected to earth so as to limit the voltage to ground on these materials.
(3) Bonding of Electrical Equipment. Normally non–current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path.
(4) Bonding of Electrically Conductive Materials and Other Equipment. Normally non–current-carrying electrically conductive materials that are likely to become energized shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path.
(5) Effective Ground-Fault Current Path. Electrical equipment and wiring and other electrically conductive material likely to become energized shall be installed in a manner that creates a low-impedance circuit facilitating the operation of the overcurrent device or ground detector for high-impedance grounded systems. It shall be capable of safely carrying the maximum ground-fault current likely to be imposed on it from any point on the wiring system where a ground fault may occur to the electrical supply source. The earth shall not be considered as an effective ground-fault current path.
Reply With Quote
  #5  
Old 3/22/11, 8:26 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Sub-panels - one more time

Not approved In Canada .
The system ground must be carried with the two hot wires and the neutral.
The neutral is then complete isolated from the ground through out the rest of the system.
A secondary ground in out buildings frequently causes Eddie currents

( http://www.oeb.gov.on.ca/OEB/_Docume...s_20080530.pdf)



(http://www.mrec.org/pubs/ARSpub696/document.pdf )



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #6  
Old 3/22/11, 8:30 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: Sub-panels - one more time

Thanks Robert.

One more for you that I heard today from an electrician on the job.

The newest NEC code requires that there be two ground rods 6' apart and a grounding conductor goes to the panel and a #6 ground wire has to go from the water service piping back to the meter and not the panel as it is now.
Is that the way it is now?
Reply With Quote
  #7  
Old 3/22/11, 8:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sub-panels - one more time

Quote:
Originally Posted by mcyr View Post
Thanks Robert.

One more for you that I heard today from an electrician on the job.

The newest NEC code requires that there be two ground rods 6' apart
The requirement for two 8' ground rods has been around for a while, sort of. The old requirement was for a single rod to have a resistance or 25 ohms or less. So on a service you could buy expensive testing equipment and prove 25 ohms or less or you could simply install two rods a minimum of 6' apart (we always just install two rods). The 2011 simply reverses the requirement, now you must install two rods or prove that a single rod has a resistance of 25 ohms or less. IMO this makes more sense.

Quote:
Originally Posted by mcyr View Post
and a grounding conductor goes to the panel and a #6 ground wire has to go from the water service piping back to the meter and not the panel as it is now.
Is that the way it is now?
I have not heard this for 2011. Under the 2008 and earlier code editions you need to connect all of the electrodes together to form a grounding electrode system (GES). You're permitted to connect one electrode to another with a bonding jumper or a GEC back to the neutral bus at the service disconnect.

Here's a nice GES graphic from Mike Holt:


Last edited by Robert Meier; 3/22/11 at 9:38 PM.. Reason: Spelling
Reply With Quote
  #8  
Old 3/22/11, 8:50 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,795
Default Re: Sub-panels - one more time

Thanks Robert, that is a good illustration, I will print it out.
Reply With Quote
  #9  
Old 3/22/11, 8:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Sub-panels - one more time

Quote:
Originally Posted by Robert Meier View Post
I would add one thing, a ground rod is not required but a grounding electrode is. It could be something other than a rod.
I gave a simple answer, but you are certainly correct. The requirement is for an effective GE.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Old electrical panels? ysoltis General Inspection Discussion 2 1/14/06 10:58 AM
Old electrical panels? ysoltis Electrical Inspections 0 1/13/06 11:38 AM