Default SubPanel bonded, ?

Looked at subdivision house yesterday for the Seller, built in 1986. Both were GE 125 Amp panels.

Service panel on exterior did not have visible ground/ground rod, etc. The only conduit to the ground was under meter can. No notations for 'ufer' ground.

Sub distribution panel on interior had lots of internal paint/drywall overspray. Someone had scrubbed the paint off an upper corner of the neutral bar and inserted bonding screw. Left a note in panel 'Bonding screw, do not remove'

They had also taken a piece of multistrand and screwed one end to the back of the panel; the other end screwed to the bottom of the neutral bar. Note here, too, 'do not disconnect this ground'.

Infomation is that an electrician did all this when the buyer purchased the house 6 yrs ago.

I refered for further evaluation by electrician.

The subpanel bonding screw and added grounding strap cancelled the separation of neutral and ground. Right ?

Thanks,
Linda
Attached Thumbnails
subpanel-bonded-100_6496-small-.jpg.jpg
Views:	121
Size:	35.3 KB
ID:	12394   subpanel-bonded-100_6533a-small-.jpg.jpg
Views:	130
Size:	46.2 KB
ID:	12395  
Reply With Quote
  #2  
Old 6/17/07, 12:15 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: SubPanel bonded, ?

Linda,

If the panel on the right is the " remote distribution panel" then the connection between the grounded ( Neutral ) and the grounding buss bar should not take place as you stated.

Also due to all the overspray onto the termination points I would most certainly put that in your report.....and I will assume that the connection between these two panels is only (3) conductors and should be (4) unless of course they are connected by metalic conduit.....but I can't see that taking place...

Seems to me that they know they did it wrong and in an effort to ATLEAST feel they are providing a fault current path they wanted the bonding jumper in place....BUT we know this can't happen in this senerio....so most certainly call it out and let the electrician go through the mess.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 6/17/07, 12:45 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: SubPanel bonded, ?

Holy crap, that's a lot of over spray. The whole panel is ruined.
Reply With Quote
  #4  
Old 6/17/07, 1:04 AM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: SubPanel bonded, ?

Guess masking tape is too much. Guess removing the busses was too much.

Geezz.....
Reply With Quote
  #5  
Old 6/17/07, 2:51 PM
Linda J. Foster's Avatar
Linda J. Foster Linda J. Foster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 463
Default Re: SubPanel bonded, ?

Thanks, guys. The picture on the left is the service panel, right is the sub. I would almost bet the overspray was original to the house. 3 wire feed,

My thought, too, was that it was pretty much all wrong. Just wanted to reinforce my thoughts.

There was new overspray around the furnace area, but some of that had been replaced in the last 5 to 6 years.

This is the same builder that puts an electric hot water heater in the lower part of mechanical closet, electric furnace in the upper. The return air comes through the door grate, across the water heater, and up in to the furnace. It's ok to do this according to the officials of San Antonio.

Go figure **
Reply With Quote
  #6  
Old 1/9/08, 5:08 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: SubPanel bonded, ?

Also, the right cabinet and panelboard are defective as well, because the integrity of the condition of the electrical equipment and connections

Internal parts of electrical equipment, including busbars, wiring terminals, insulators, and other surfaces, cannot be damaged or contaminated by foreign materials such as paint, plaster, cleaners, abrasives, or corrosive residues.

There cannot be any damaged parts that may adversely affect safe operation or mechanical strength of the equipment such as parts that are broken; bent; cut; or deteriorated by corrosion, chemical action, or overheating.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonded to building Steel Structure Frame mcyr Electrical 11 4/29/09 12:50 PM
Remote distribution panel or subpanel? rwilcox Electrical 57 1/11/08 7:49 PM
Subpanel Bonding Screw away Electrical 24 1/9/08 3:46 PM
Bonded to panel? cobarr Electrical 8 4/14/06 1:09 AM
bonded sub. Jay Moge Electrical 2 3/5/06 11:54 PM


All times are GMT -4. The time now is 1:08 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts