I have seen subpanels hooked up this way several times now. It is making me wonder if I am incorrectly calling them out. Any thoughts?
The subpanel feeders are attached to the lugs of the main service lines. Thanks |
|
#2
|
||||
|
||||
|
Jeff,
This is definitely a "RED FLAG" situation. You've got a triple tap there on the main SE and the sub panels (LSE) will not trip in this situation. Those tapped wires will melt if overloaded. Fire safety issue. |
|
#3
|
||||
|
||||
|
Thats what you call a double hat trick.
|
|
#4
|
|||
|
|||
|
A double tap is bad enough.
|
|
#5
|
|||
|
|||
|
Please Note:
jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
I appreciate the input. I have seen it a few times lately. It is making me wonder if the local electricians are installing it that way, which is why I was questioning it.
|
|
#6
|
||||
|
||||
|
Please Note:
Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is sooooooooo bad good call.
|
|
#7
|
|||
|
|||
|
All I can say is WOW!
|
|
#8
|
||||
|
||||
|
Please Note:
poliner is a non-member guest and is in no way affiliated with InterNACHI or its members.
On a similar theme, I saw this arrangement, (excuse the poor pic).
The thing is, the sub panal it was feeding had a 100 amp service, and was wired like a main panel, the Neutral was bonded to the ground. So hypothetically was that the right thing to do as far as the sparks was concerned with this arrangement? Anyway the home owner assured me it was done by a pro! |
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
This is not installed by an electrician, at least not a real electrician.
I know anyone with a rusty pair of Kliens and a mouthfull of wirenuts can call himself an electrician but that does not make it so. I really suspect this was the homeowner or their friend who "knows about electrical stuff" |
|
#10
|
||||
|
||||
|
lol.....now thats a POLITE way to say a HACK did it...lol......oh and I can guarantee that on that "Grounded" neutral conductor in the LUG....how many strands to you think they CUT off or actually DO NOT make it into the lug....lol......
Nope......even a BAD "REAL" electrician would not have done this...lol Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Remote distribution panel or subpanel? | rwilcox | Electrical Inspections | 57 | 1/11/08 7:49 PM |
| Subpanel Bonding Screw | away | Electrical Inspections | 24 | 1/9/08 3:46 PM |
| SubPanel bonded, ? | lfoster | Electrical Inspections | 5 | 1/9/08 5:08 AM |
| Subpanel wired as main panel. | jlybolt | Electrical Inspections | 15 | 5/23/07 5:10 PM |
| Subpanel Ground | bkelly2 | Electrical Inspections | 26 | 7/14/06 9:16 PM |