Hi Sparkies, I am the 1st to admit that electricity is my weakest area. I would like to know if I have this right and did I get it all.
Attached Thumbnails
subpanel-issues-100_6124.jpg   subpanel-issues-100_6125.jpg  



Ralph M. Smith; CMI, CHI, CI, CEO
S.H.I.R.E. Inspection Services, Inc.
"Your Home is Our Business"
http://shireinspect.com
Reply With Quote
Find an InterNACHI certified Ohio Home Inspector (and anywhere else in North America)
  #2  
Old 7/2/09, 9:36 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Subpanel issues

Looking at the mounting screw which is visible in the lower left hand side I would also guess that there may be an issue there , as it appears to not be secured properly .

Were all 4 in place or just 2 kitty corner screws ?
Reply With Quote
  #3  
Old 7/2/09, 9:38 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Subpanel issues

Am I seeing shadows or wiring. Where is the double tap?



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #4  
Old 7/2/09, 9:55 AM
Ralph Smith Ralph Smith is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Canastota, NY
Posts: 197
Default Re: Subpanel issues

Robert, all four were in place.
Blaine, Shadows, not a double tap. The top two wires are 14 gauge and the one below is a 12 gauge. The breaker is a 20 amp.



Ralph M. Smith; CMI, CHI, CI, CEO
S.H.I.R.E. Inspection Services, Inc.
"Your Home is Our Business"
http://shireinspect.com
Reply With Quote
  #5  
Old 7/2/09, 11:03 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Subpanel issues

Hi Ralph,

the only real problem in that panel is the grounds and Neutrals on the same bus, as it's a remote panel they should be seperated and the neutrals isolated from the panel box.

Yout "double tap" is the sensing wire for that GFCI/AFCI
there is nothing wrong with 2 cable assemblies in one bushing

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #6  
Old 7/2/09, 11:15 AM
Ralph Smith Ralph Smith is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Canastota, NY
Posts: 197
Default Re: Subpanel issues

Gerry, The 14 gauge wire on the 20amp GFCI/AFCI breaker is OK? 2 wires in the same box opening OK? There is no seperate bar for seperating the ground and neutrals. wrong box? I appreciate your input Gerry, I just want to make sure of all issues. Thanks to Robert and Blaine also.



Ralph M. Smith; CMI, CHI, CI, CEO
S.H.I.R.E. Inspection Services, Inc.
"Your Home is Our Business"
http://shireinspect.com

Last edited by rsmith5; 7/2/09 at 11:16 AM.. Reason: Changed # of wires
Reply With Quote
  #7  
Old 7/2/09, 11:29 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Subpanel issues

I'd note the wires undersized/oversized breaker and that the neutrals are not isolated or separated.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 7/2/09, 12:09 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Subpanel issues

Quote:
Originally Posted by rsmith5 View Post
Gerry, The 14 gauge wire on the 20amp GFCI/AFCI breaker is OK? .
Sorry, brain fart, that should be on a 15amp, my bad

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #9  
Old 7/2/09, 12:25 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Subpanel issues

Looks like you caught the issues
Reply With Quote
  #10  
Old 7/2/09, 9:08 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 739
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Subpanel issues

Just to clarify, that bond strap near the neutral buss should have been removed. An auxillary ground buss should have been added/
Reply With Quote
  #11  
Old 7/3/09, 12:15 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Subpanel issues

A few things come into mind and I most certainly don't want to MUDDY any waters over bringing up lessons to learn from. Did the OP say if this "Remote" panel was in the same structure or a detached structure as I always hate to assume it.

Depending on the Code Cycle they are in it may not be a violation to have the Case to Neutral connection, but since they DID run the four conductors then it would indeed need to be seperated as Jim and Gerry have pointed out but something to think about for those 2005 and earlier NEC jurisdictions.

Also if this was a detached structure which I again don't know that it is or isn't and I am just kinda grasping at straws here....then a grounded electrode system would also be required....just things to think about.

Another reason I ask this is it is not typical to back fed a breaker in a "sub-panel" in the same dwelling so when we see back fed devices we look for hold down devices and then think...wait a minute it may be a detached structure and then OTHER issues come into play that I wont go into right now....just think about the senerios and it helps you learn....

BTW......the first step is admitting that Electricity is a weak link...now do something about it and take the online quiz, read all you can and ask as many questions you need until your comfort level is raised. Thats what we are here for, thats why people like me and others give "FREELY and WITHOUT MONITARY GAIN" advice to help people like yourself by CHOICE.....as one knowledge is weak but as a group knowledge is STRONG !



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 7/4/09, 11:36 AM
Ralph Smith Ralph Smith is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Canastota, NY
Posts: 197
Default Re: Subpanel issues

Thanks for all the input guys. This message board is by far the best learning tool that I use. Paul, This month I am taking an electrical, continuing ed class for my license renewal requirements. [NY]



Ralph M. Smith; CMI, CHI, CI, CEO
S.H.I.R.E. Inspection Services, Inc.
"Your Home is Our Business"
http://shireinspect.com

Last edited by rsmith5; 7/4/09 at 11:37 AM.. Reason: spell check
Reply With Quote
  #13  
Old 7/4/09, 11:40 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Subpanel issues

Quote:
Originally Posted by rsmith5 View Post
Thanks for all the input guys. This message board is by far the best learning tool that I use. Paul, This month I am taking an electrical, continuing ed class for my license renewal requirements. [NY]
Excellent.....any education is a SOUND investment in your future. Good luck my friend.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got a letter from ASHI's President today. gromicko General Inspection Discussion 55 12/13/10 12:51 AM
underamped subpanel?? wstafford Electrical Inspections 12 5/13/09 6:08 PM
Neutral/ground bond in subpanel gkeene Electrical Inspections 2 1/23/09 11:14 PM


All times are GMT -4. The time now is 4:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts