Question Suitable Disconnect?

Note the circuit breaker on the air handler itself. Is there anything that says the disconnect has to be separate from the appliance?

suitable-disconnect-042711-009.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/27/11, 5:16 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suitable Disconnect?

Nope. An integral disconnect is permitted as long as it disconnects all of the ungrounded conductors.
Reply With Quote
  #3  
Old 4/27/11, 6:09 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Suitable Disconnect?

Quote:
Originally Posted by Robert Meier View Post
Nope. An integral disconnect is permitted as long as it disconnects all of the ungrounded conductors.
Please explain why this one does not.

Also, what code to rely on? Could not find it during a word search. Thanks.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 4/27/11, 6:55 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suitable Disconnect?

I believe RM meant the Nope to mean it does not need to be a separate disconnect and that the unit switch is fine to serve as a disconnect.
Reply With Quote
  #5  
Old 4/27/11, 7:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Suitable Disconnect?

Quote:
Originally Posted by jfunderburk View Post
Please explain why this one does not.

Also, what code to rely on? Could not find it during a word search. Thanks.
NEC 422.34 Unit Switch(es) as Disconnecting Means. A unit switch(es) with a marked-off position that is a part of an appliance and disconnects all ungrounded conductors shall be permitted as the disconnecting means required by this article where other means for disconnection are provided in occupancies specified in 422.34(A) through (D).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 4/27/11, 7:42 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suitable Disconnect?

Thanks guys, yes that is what I meant in response to Joe's question "Is there anything that says the disconnect has to be separate from the appliance."
Reply With Quote
  #7  
Old 4/28/11, 12:32 AM
Richard L. Overton Richard L. Overton is offline
InterNACHI Member
 
Join Date: Apr 2009
Posts: 16
Default Re: Suitable Disconnect?

Is the disconnect fastened to the dead front in such a way as to cause a hazard when the cover is removed?
Reply With Quote
  #8  
Old 4/28/11, 1:02 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suitable Disconnect?

Quote:
Originally Posted by roverton View Post
Is the disconnect fastened to the dead front in such a way as to cause a hazard when the cover is removed?
No. Historically, those are almost always Square D QOU breakers. They clip on DIN rail. They have line and load side lugs. They still present energized terminals to the person who takes off the appliance cover. If you are an employee of an inspection agency, it would be flatly illegal for you to remove that cover without proper training and PPE. Owners, feel free to do as you please.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main Panel vs Sub-Panel and main disconnect? rbassett Electrical Inspections 11 10/24/09 6:16 PM
50 amp disconnect for 1600sf condo kmccullough Electrical Inspections 5 4/10/07 8:49 PM
A/C Disconnect question rslocum Inspecting HVAC Systems 15 9/21/06 12:16 AM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical Inspections 8 8/15/06 12:32 PM
Disconnect and Main panel srowe Electrical Inspections 10 6/13/06 7:49 PM


All times are GMT -4. The time now is 8:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts