Default sump pump and the GFCI in a crawlspace

Is a sump pump, in a crawl, required to have GFCI protection? I'm getting a lot of mixed answers, but it appears that it's code?? I personally have always installed them with simplex receps, and this is how I would want it if it were my house (and a back-up system, of course).
So my inspection on Saturday had a GFCI outlet installed at the sump, do I just leave it be?

All help will be much appreciated!

Have a great week all!
Reply With Quote
  #2  
Old 11/17/08, 9:00 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is online now
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,208
Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: sump pump and the GFCI in a crawlspace

Hi Joshua,

I don't see it as a problem being on a GFCI, but a dedicated single outlet would be OK as well. the only issue with it being on a GFCI outlet is maybe nuisance tripping, but that is really a sign of a pump that needs replacement anyway.

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 11/17/08, 10:19 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 132
Jim Port has had a little positive feedback
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sump pump and the GFCI in a crawlspace

Under the 08 NEC the sump would be required to have GFI protection. The exception for a simplex receptacle allowance has been removed.
Reply With Quote
  #4  
Old 11/17/08, 10:48 AM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 423
Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information Ralph Brady is very trusted source of information
Default Re: sump pump and the GFCI in a crawlspace

I would advise the use of a GFCI breaker, rather than a GFCI recptacle, for convenience of reseting.

I was also under the impression that it did not need GFCI if it was a dedicated circuit, but I'm not that familiar with the codes, especially the 08 codes.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr
"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold
Reply With Quote
  #5  
Old 11/24/08, 12:47 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: sump pump and the GFCI in a crawlspace

Jim is correct. Under the 2008 NEC the exceptions that allowed areas to be relaxed from the GFCI requirements have been removed. (ie: the garage door opener receptacle in the ceiling of a garage in the 2008 NEC will need to be GFCI protected )

Fact is this.......I dont really care if the basement floods in a weather event versus walking down into the basement and being electrocuted. GFCI's generally don't trip anymore unless their is a reason and either way..its a good thing.

It is important to understand how GFCI's work.....of which i dont wish to go into again ( use the search feature )



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #6  
Old 11/24/08, 11:35 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,994
Jeffrey R. Pope .
Default Re: sump pump and the GFCI in a crawlspace

Quote:
Originally Posted by rbrady View Post
I was also under the impression that it did not need GFCI if it was a dedicated circuit, but I'm not that familiar with the codes, especially the 08 codes.
The 2007 California Electrical Code (CEC) went into effect on Jan 1, 2008. The 2007 CEC is based on the 2005 NEC. So, even if this were a new-build (in CA), it would not require a GFCI protected receptacle, unless the receptacle is "at or below grade level."



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #7  
Old 11/24/08, 7:53 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: sump pump and the GFCI in a crawlspace

Actually...in the 2005 NEC their is no provision otherwise than if the receptacle is in the crawl space it needs to be GFCI. 210.(A)(4) would require it ( no exception for dedication ). Most crawlspaces ( if not all...lol. ) are at or below ground level.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #8  
Old 1/2/09, 7:39 PM
Tyler Pay Tyler Pay is offline
New User
 
Join Date: Jan 2009
Posts: 6
Tyler Pay hasn't had much positive or negative feedback
Please Note: Tyler Pay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sump pump and the GFCI in a crawlspace

I had the same question and stopped by my Chicago suburb inspection department. They said that it needs to be either a GFI or a simplex outlet. I told him my concern regarding GFI tripping and that I would hate to have a flood, just because the GFI had something wrong and tripped when not suppose to (happens often), and he agreed that the simplex plug is the best solution. I put the simplex outlet, but I have decided to get the Basement Watchdog back up pump, which takes an outlet for the trickle charge for the batery. I guess my question is to keep code, can I put a another box next to the existing box and run power from the existing simplex outlet to a new simpex outlet. It meets code of a outlet needs to be simplex correct?
Reply With Quote
  #9  
Old 1/2/09, 8:26 PM
Tyler Pay Tyler Pay is offline
New User
 
Join Date: Jan 2009
Posts: 6
Tyler Pay hasn't had much positive or negative feedback
Please Note: Tyler Pay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sump pump and the GFCI in a crawlspace

Hey Paul W. Abernathy, one comment regarding your comment regarding that the crawl space at or below grade. I think they are referring to the location of the receptacle in the crawl space. I installed 2 dedicated 15a simpex outlets in the crawl space and the City inspector made a comment and measured the location of the outlet in relation to the grade. He was saying that if the sump over flowed for example and filled up the 42" crawl space (probally won't happen) the water would leak outside through the sill plate ans since my outlets are above grade, they should not get submerged.
Reply With Quote
  #10  
Old 1/2/09, 8:29 PM
Richard A. Maday's Avatar
Richard A. Maday Richard A. Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 2,155
Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute
Default Re: sump pump and the GFCI in a crawlspace

Tyler, what part of Chicago?



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #11  
Old 1/2/09, 9:01 PM
Tyler Pay Tyler Pay is offline
New User
 
Join Date: Jan 2009
Posts: 6
Tyler Pay hasn't had much positive or negative feedback
Please Note: Tyler Pay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sump pump and the GFCI in a crawlspace

Naperville
Reply With Quote
  #12  
Old 1/2/09, 9:02 PM
Tyler Pay Tyler Pay is offline
New User
 
Join Date: Jan 2009
Posts: 6
Tyler Pay hasn't had much positive or negative feedback
Please Note: Tyler Pay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sump pump and the GFCI in a crawlspace

what is your interprettion of the code?
Reply With Quote
  #13  
Old 1/2/09, 9:06 PM
Richard A. Maday's Avatar
Richard A. Maday Richard A. Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 2,155
Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute Richard A. Maday has a reputation beyond repute
Default Re: sump pump and the GFCI in a crawlspace

I don't interpret code.

Even if I did, I'd defer all things electrical to Paul or Marc.

Are you an inspector?



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #14  
Old 1/2/09, 9:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: sump pump and the GFCI in a crawlspace

Quote:
Originally Posted by Tyler Pay View Post
Hey Paul W. Abernathy, one comment regarding your comment regarding that the crawl space at or below grade. I think they are referring to the location of the receptacle in the crawl space. I installed 2 dedicated 15a simpex outlets in the crawl space and the City inspector made a comment and measured the location of the outlet in relation to the grade. He was saying that if the sump over flowed for example and filled up the 42" crawl space (probally won't happen) the water would leak outside through the sill plate ans since my outlets are above grade, they should not get submerged.
Well your local inspector is free to determine anything as long as you accept it. Since most all crawlspaces under dwellings are at the same grade or below the actual grade I would say 210.8(A)(4) would most certainly apply...and require the use of a GFCI receptacle.

Exceptions to 210.8 are documented directly after each position of the NEC and nothing in 210.8(A)(4) gives us an exception....except of course your local inspector if thats their choice....but in my opinion not how the NEC reads......but again the local inspector can make his own ruling.

The example of the 2008 NEC what would remove the allowance to a single receptacle is under 2005 NEC 210.8(A)(5) Ex.2....this exception was for unfinished basements and is removed in the 2008 NEC....you can't apply 210.8(A)(5) to 210.8(A)(4) in any application.

BTW- The location of the receptacle in the crawl is irrelevant...it is the crawspace that is below grade or at grade.

Figured I would add this also : We are talking in the most likely sense that most crawlspaces are areas that could have water standing, wet earth or dry earth for that matter and so on. It is not nearly an issue of the " SUMP PUMP" but more so the location that is being scoped into this requirement.

The NEC is clear on 210.8(A)(4) that crawlspaces receptacles require GFCI...the comments about the Below or At Grade level are refering to the location of the crawl...it is ok to disagree with me.....I have no problem with that.

Just for your reference....As to the intent of 210.8(A) regarding GFCI and Locations

(1)Bathrooms....no exceptions
(2)Garages....two exceptions
(3)Outdoors....one exception
(4)Crawl spaces....no exceptions
(5)Unfinished basements....three exceptions
(6)Kitchen counters....no exceptions
(7)Wet bars....no exceptions
[8]Boat houses....no exceptions



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.

Last edited by pabernathy; 1/2/09 at 9:48 PM.
Reply With Quote
  #15  
Old 1/2/09, 10:03 PM
Tyler Pay Tyler Pay is offline
New User
 
Join Date: Jan 2009
Posts: 6
Tyler Pay hasn't had much positive or negative feedback
Please Note: Tyler Pay is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sump pump and the GFCI in a crawlspace

Paul,

I have installed a 4" concrete floor and have a HVAC vent open, so think I can get away with calling this an unfinished basement? In your opinion do I have any other options than a GFCI? Do you think it's a matter of my town still going by 2005 code?