Default sump pump dedicated outlet GFCI

Hello All
Happy New Year
Does anyone know if nec has anything about a sump pump being on a dedicated circut and also being a gfci outlet.
Or any reason that this should be.
thank you
Mark





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/15/11, 12:27 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: sump pump dedicated outlet GFCI

Unfortunately, 2008 version required it to be on a GFCI.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #3  
Old 1/15/11, 7:16 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sump pump dedicated outlet GFCI

There is no NEC requirement for GFCI protection for a sump pump. The 2008 NEC removed the exception for 120 volt non-GFCI receptacles in dedicated spaces in garages and unfinished basements. If the location of the sump pump receptacle requires GFCI protection then you must have GFCI protection. If the sump pump were located in an area where non-GFCI receptacles are permitted then you wouldn't need GFCI protection for the pump receptacle.

Personally I dislike this requirement and would not use a GFCI protected receptacle or circuit breaker for a sump pump. One option would be to use a pump rated for 240 volts and use a 240 volt non-GFCI branch circuit.
Reply With Quote
  #4  
Old 1/15/11, 7:34 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: sump pump dedicated outlet GFCI

I have a gfci protected sump pump .
I put in a watered back up sump pump.
Gfci never dumped but during a power failure the water powered sump sved the day .
You have to be on town water of course .
Home Depot Canada $150;00
Attached Thumbnails
sump-pump-dedicated-outlet-gfci-100_0111.jpg  



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 1/15/11, 7:58 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: sump pump dedicated outlet GFCI

Perhaps sumps should not be plug in devices as that would solve the issue.
Make them hard wired.
Reply With Quote
  #6  
Old 1/15/11, 11:48 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: sump pump dedicated outlet GFCI

Quote:
Originally Posted by belliott View Post
Perhaps sumps should not be plug in devices as that would solve the issue.
Make them hard wired.
That would be nice. I see them unplugged all the time so the homeowner can plug in their dehumidifier, or other such thing.
Reply With Quote
  #7  
Old 1/15/11, 3:37 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: sump pump dedicated outlet GFCI

Quote:
Originally Posted by jjonas View Post
That would be nice. I see them unplugged all the time so the homeowner can plug in their dehumidifier, or other such thing.
Furnaces are not required to have GFCI because they are hardwired.(condensate)
Reply With Quote
  #8  
Old 1/15/11, 4:03 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: sump pump dedicated outlet GFCI

Quote:
Originally Posted by belliott View Post
Furnaces are not required to have GFCI because they are hardwired.(condensate)
I thought this was a "sump pump" thread!
Reply With Quote
  #9  
Old 1/15/11, 4:06 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: sump pump dedicated outlet GFCI

Quote:
Originally Posted by jjonas View Post
That would be nice. I see them unplugged all the time so the homeowner can plug in their dehumidifier, or other such thing.
Bob... as in "portable DEhumidifiers. Ya know, that thing that homeowners with basements use!
Reply With Quote
  #10  
Old 1/15/11, 4:23 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: sump pump dedicated outlet GFCI

Sorry to confuse anyone as I was simply trying to give an example as Furnaces are hardwired.

Junction box and switch rather than a plug.Also they are associated with water but you would never need a GFCI because they are switched.
Perhaps a bad metaphor.
Reply With Quote
  #11  
Old 1/15/11, 4:34 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: sump pump dedicated outlet GFCI

Mark -

I would leave my sump pump on a dedicated outlet WITHOUT a GFCI (don't wanta find out my GFCI tripped accidently when I'm 6" deep in water on my finished basement floor).
Reply With Quote
  #12  
Old 1/15/11, 4:36 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: sump pump dedicated outlet GFCI

Quote:
Originally Posted by dbowers View Post
Mark -

I would leave my sump pump on a dedicated outlet WITHOUT a GFCI (don't wanta find out my GFCI tripped accidently when I'm 6" deep in water on my finished basement floor).
A legitimate concern but the NEC doesn't really care if the device trips and you're underwater because of it. The code requires that the receptacle be GFCI protected if it's installed in an unfinished basement or garage.
Reply With Quote
  #13  
Old 1/15/11, 5:58 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: sump pump dedicated outlet GFCI

When I see the crawl space sump pumps around here, most are non GFCI protected.

I recommend they be GFCI protected but let the client know that the best place to put the reset is in the main family room near the tv. If the light comes on, they know they need to reset the pump. Don't like having the resets in the now flooded crawl space.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/15/11, 8:53 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: sump pump dedicated outlet GFCI

Quote:
Originally Posted by Robert Meier View Post
A legitimate concern but the NEC doesn't really care if the device trips and you're underwater because of it. The code requires that the receptacle be GFCI protected if it's installed in an unfinished basement or garage.
Why only in unfinished basement? Why not in finished basement? What's the theory behind this?




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #15  
Old 1/15/11, 9:30 PM
Marc-Andre Beauchemin's Avatar
Marc-Andre Beauchemin Marc-Andre Beauchemin is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: BROSSARD,Quebec Canada
Posts: 298
Default Re: sump pump dedicated outlet GFCI

I agree with stephen, I find it ridiculous when installed in a out of reach area. I prefer GFCI be located visible in the family room having it protect the sump pump connect to the protected plug.
A GFCI can protect up to 12 outlets. Then for this one, two could do the trick and avoid forgetting to reset it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
basement floor Unregistered AskNACHI.org Inspection Questions Forum 4 9/15/10 1:23 AM
Sump pump requirements Matthew Klein Plumbing Inspections 0 12/30/09 3:53 PM
sump pump and the GFCI in a crawlspace jfrederick Electrical Inspections 18 1/2/09 11:13 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM


All times are GMT -4. The time now is 8:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts