  #16  
Old 6/12/06, 1:45 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sup panel question?

Greg,

Agreed........at that point it should still be (3) conductors....not running the solid copper line.....creates potential parallel conditions.....should start with (4) wire AFTER this location.....and Isolated neutral buss...AGREED this is where I see the main problem.

I do not believe they have to run a GEC from each feeder subpanel....as this more than often in my experience is run from the main panel ahead of the "gutter" or from the gutter is direct tapped and no OCPD ahead of it.

Pierre....any comments on this setup in the images?



Paul W. Abernathy
Reply With Quote
  #17  
Old 6/12/06, 1:53 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sup panel question?

If you look closely, you can see what looks like the GEC to the groundrods at the first point of disconnect, which is ahead of the meters. This is a common setup in NY as long as the POCO can lock everything up on the line side of the meters, including the trough.

What is happening with the conductors I cannot tell from this picture.
Reply With Quote
  #18  
Old 6/12/06, 2:01 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sup panel question?

I agree about the conductors Pierre, without seeing in those meter cans I wouldn't touch it. The 4ga is just paralleling the metal in the cans anyway, assuming the meters are bonded. In my experience POCO guys don't recognize the "objectionable current in grounding conductors" issue at all. They bond the neutral every chance they get. With that in mind, if I was really being a code nazi, I would have them cut out the 4ga to the customer disconnect if I was sure it was all bonded in the service equipment but I would still be left with the parallel path of the raceways so why bother? It's there and it isn't hurting anything. I would just tell the electrician he could skip it next time and save a few bucks.
Reply With Quote
  #19  
Old 6/12/06, 2:07 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sup panel question?

Quote:
Originally Posted by Greg Fretwell
if I was really being a code nazi
lol...I like that.....



Paul W. Abernathy
Reply With Quote
  #20  
Old 6/12/06, 5:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Sup panel question?

Well there you have it James. Did you get all that?

I think this goes to show you, if the neutrals are grounded at any point other than the service disconnect (the first means of disconnecting the power after the drop or lateral), we, as HI's, should defer it to the experts.

As Pierre pointed out, there are exceptions to the rule, but we shouldn't be trying to interpret those exceptions, as we are not qualified (in most cases) to do so.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #21  
Old 6/12/06, 5:41 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sup panel question?

Jeff....you are a good man........bringing it all back together in a nice tidy package...Bravo to ya fella.....

Dang long winded Electricians......



Paul W. Abernathy
Reply With Quote
  #22  
Old 6/12/06, 6:01 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sup panel question?

So, can someone please explain this all over again.
Just kidding

Thanks everyone for your comments. I am fairly new to the business and this website and everyones comments are very educational and always appreciated.

Thank You
</IMG>
Reply With Quote
  #23  
Old 6/12/06, 7:57 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Sup panel question?

James,

I will start again.......basically............JUST KIDDING...lol



Paul W. Abernathy
Reply With Quote
  #24  
Old 6/12/06, 8:42 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sup panel question?

The short answer is you can bet the farm the POCO bonded each meter so the first place you have to look at is the unit disconnects and if that was a service disconnect we wouldn't lose our mind that there was a parallel path to the meter, three in this case. This is not something I would worry about. Just be sure the panel in the unit is right.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Service Panel question for board sparkies pbolliger Electrical Inspections 8 5/14/06 9:24 AM


All times are GMT -4. The time now is 8:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts