New construction. None of the tested Square-D breakers would trip with a Sure-test. Got a strange read-out. What do you think?

sure-test-fails-trip-afci-breakers-060611-069-800x600-.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/7/11, 12:38 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 7,280
Default Re: Sure Test fails to trip AFCI breakers

You didn't wait long enough between tests. After a series of tests, it needs to cool down. Manual calls for 20 seconds between tests to dissipate heat.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #3  
Old 6/7/11, 1:01 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,967
Send a message via Yahoo to jfunderburk
Default Re: Sure Test fails to trip AFCI breakers

Thanks Stephen.

None of the AFCI's tripped however. I've heard that the test button is the accepted test method, but when I can't get them to trip using the Sure-test, I write it up.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #4  
Old 6/7/11, 4:59 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 20,725
Default Re: Sure Test fails to trip AFCI breakers

Quote:
Originally Posted by jfunderburk View Post
Thanks Stephen.

None of the AFCI's tripped however. I've heard that the test button is the accepted test method, but when I can't get them to trip using the Sure-test, I write it up.

Did they trip with the test button?? .
That is the recommended way to test




If you do not search for more ,
......You will never find it.

............. Roycooke@hotmail.com
...................705-999-1030
Reply With Quote
  #5  
Old 6/7/11, 6:17 AM
bkelly2's Avatar
bkelly2 bkelly2 is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 16,083
Default Re: Sure Test fails to trip AFCI breakers

Quote:
Originally Posted by rcooke View Post
Did they trip with the test button?? .
That is the recommended way to test

Exactly Roy.
Reply With Quote
  #6  
Old 6/7/11, 7:54 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 12,638
Default Re: Sure Test fails to trip AFCI breakers

Have you got a updated one/ we had problems with a couple of manufactures Siemens was one . Ideal had to update the unit



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #7  
Old 6/7/11, 8:11 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,125
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sure Test fails to trip AFCI breakers

Quote:
Originally Posted by jfunderburk View Post
Thanks Stephen.

None of the AFCI's tripped however. I've heard that the test button is the accepted test method, but when I can't get them to trip using the Sure-test, I write it up.

Does the test button trip the breaker? If so how can you write it up? Isn't the TEST button the prescribed testing method set forth by the manufacturer?
Reply With Quote
  #8  
Old 6/7/11, 9:17 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,967
Send a message via Yahoo to jfunderburk
Default Re: Sure Test fails to trip AFCI breakers

Quote:
Originally Posted by Robert Meier View Post
Does the test button trip the breaker? If so how can you write it up? Isn't the TEST button the prescribed testing method set forth by the manufacturer?
What do you say when your tester won't trip a GFCI? I view AFCI's no differently. If I have an expensive device that is designed to trip the breaker and it does not, I write it up like so:

"An arc-fault circuit interrupters protecting the bedrooms and living areas do not trip when tested using a Sure-Test circuit analyzer, and should be evaluated by a licensed electrician. AFCI receptacles are life saving devices but may fail or be defective from the manufacturer. Any claim that the only reliable test is by using the breaker's integrated test button should be substantiated with written documentation from the manufacturer."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com


Last edited by jfunderburk; 6/7/11 at 10:38 AM..
Reply With Quote
  #9  
Old 6/7/11, 10:14 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,515
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sure Test fails to trip AFCI breakers

The only UL recognized test method is the built-in test buttons. You are not using a tester, it is more properly called an indicator.

To write up something when the proper procedure works would be a poor call IMO.
Reply With Quote
  #10  
Old 6/7/11, 10:21 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 9,967
Send a message via Yahoo to jfunderburk
Default Re: Sure Test fails to trip AFCI breakers

Ideal's test recommendation:

http://www.idealindustries.com/media...d_circuits.pdf



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CBO, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
Angie's List Super Service Award Winner 2013, 2012, 2011, 2010.
Ph: 704-351-1776
NACHI ID: NACHI05120170
www.aohomeinspection.com

Reply With Quote
  #11  
Old 6/7/11, 10:31 AM
Larry Kage, CMI Larry Kage, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: NW, MI
Posts: 12,202
Default Re: Sure Test fails to trip AFCI breakers

Quote:
Originally Posted by jfunderburk View Post

From the link...They recommed using the integral test button.

Can the underlined/bolded always be verified by the home inspector?

1. At the panel, operate the test button on the AFCI breaker installed in the branch circuit.
a. If the AFCI breaker trips, reset the breaker to restore power.
b. If the AFCI breaker does not trip, verify proper installation of the breaker. If the installation is correct and the breaker still does not trip, replace the faulty breaker.
2. Then, check each outlet on the branch circuit for proper wiring configuration by using the LEDs on the 61-059 tester.
3. Go to the furthest outlet on the branch circuit from the panel and conduct an AFCI trip test with the tester.
a. If the breaker trips, then use the tester to check that each outlet on the branch circuit has been de-energized to confirm that the outlets are on the same AFCI branch circuit.
b. If the breaker doesn’t trip, then the branch circuit may have excessive line impedance (i.e. voltage drop) from undersized wiring, loose wire connections and/or faulty wiring devices. The SureTest® model 61-165 can be used to further identify the source of high impedance on the branch circuit.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/
____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
whis11 @ charter.net
The above post represents my personal opinion.
Reply With Quote
  #12  
Old 6/7/11, 11:38 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,828
Default Re: Sure Test fails to trip AFCI breakers

There are certain types of AFCI breakers that do not trip when the SureTest is used, although the AFCI function is operational.

As long as the circuit is opened when the internal test button on the breaker is used, the AFCI is considered functional.

The readings on your SureTest show "caution" (triangle with exclamation), "don't operate" (circle with line), "over heated" (thermometer) and "wait" (hour glass) - in other words STOP!



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 6/7/11, 9:13 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: By my swimming pool
Posts: 3,917
Default Re: Sure Test fails to trip AFCI breakers

I thought the appropriate way was to test at the breaker itself??






Fogarty Inspection Services Group of Palm Bay FL
Florida Licensed Home Inspector #8351
Certified Master Inspector

Home inspections, Commercial Inspections, Thermal Imaging, Wind Mitigation and Insurance Inspections for Palm Bay, Melbourne, Cocoa, Titusville, Vero Beach and all the surrounding areas.

321-506-5125
fogartyinspectionservices@gmail.com

www.homeinspectorpalmbay.com
Reply With Quote
Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 6/7/11, 9:36 PM
bkelly2's Avatar
bkelly2 bkelly2 is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 16,083
Default Re: Sure Test fails to trip AFCI breakers

Quote:
Originally Posted by Jim Port View Post
The only UL recognized test method is the built-in test buttons. You are not using a tester, it is more properly called an indicator.

To write up something when the proper procedure works would be a poor call IMO.
Exactly.

Same if your Tester does not trip a GFCI and the Test Button does trip the Circuit, it is not a defect.
Reply With Quote
  #15  
Old 6/7/11, 9:58 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,601
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sure Test fails to trip AFCI breakers

Quote:
Originally Posted by bkelly2 View Post
Exactly.

Same if your Tester does not trip a GFCI and the Test Button does trip the Circuit, it is not a defect.
I carry 3 GFCI testers in my tool kit from the small $10 type to the original Suretest I bought in 1985. If none of my testers will trip a GFCI and the test button does, I call it as a defect!! Just being safe......... when 3 testers that are designed to "create a ground fault condition" do not cause a trip, I'm assuming the GFCI unit will not trip when a real one occurs!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI breakers straylor Electrical Inspections 3 1/6/11 4:59 PM
AFCI breakers cbono Electrical Inspections 15 2/27/08 2:33 PM
Stacking AFCI, GFCI breakers abolt Electrical Inspections 6 4/17/07 11:57 AM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 7:31 PM

All times are GMT -4. The time now is 3:10 PM.
no new posts