I have now had two homes in a row where the AFCI breakers did not trip when tested at the bedroom outlets. They did trip when tested with the "test" button in the load center. Does anyone know if the IDEAL Suretest Circuit Analyzers have any known problems? I have the older basic model with the AFCI test button. Anyone heard if they don't work as they should?

Thanks!
Reply With Quote
  #2  
Old 9/22/07, 4:44 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Suretest circuit analyzer problems?

See this thread
Reply With Quote
  #3  
Old 9/22/07, 4:52 PM
mporras mporras is offline
Active Poster
 
Join Date: Mar 2005
Location: Edmond, OK
Posts: 183
Please Note: mporras is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

Thanks Michael. That helped. It is interesting that my AFCI tester/indicator did work on previous AFCI protected outlets that I checked, but it appears that it doesn't work anymore. Hmmmm...

Last edited by mporras; 9/22/07 at 4:55 PM..
Reply With Quote
  #4  
Old 9/22/07, 5:00 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Suretest circuit analyzer problems?

Quote:
Originally Posted by mporras
Thanks Michael. That helped. It is interesting that my AFCI tester/indicator did work on previous AFCI protected outlets that I checked, but it appears that it doesn't work anymore. Hmmmm...
Give Ideal a call.
Reply With Quote
  #5  
Old 9/22/07, 6:58 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Suretest circuit analyzer problems?

Here is a bulletin from Square D on testing AFCI breakers.

Similar to GFCI devices, I think the best way to check an AFCI breaker is with the "test" button. No special tools required either ...
Attached Files
File Type: pdf AFCI Breaker Testing - SQD.pdf (77.4 KB, 139 views)



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #6  
Old 9/23/07, 1:00 AM
mporras mporras is offline
Active Poster
 
Join Date: Mar 2005
Location: Edmond, OK
Posts: 183
Please Note: mporras is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

Thanks for the info Robert.

Last edited by mporras; 9/23/07 at 1:51 PM..
Reply With Quote
  #7  
Old 9/23/07, 6:03 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

Paul (MR. Guru) said it best with this statement:

"This is why all HI's should be testing at the device itself and not with testers. The proper method is still to use the test buton built into the GFCI or AFCI itself and not rely on ancillary testers for confirmation."
Reply With Quote
  #8  
Old 9/23/07, 9:11 PM
rdawes's Avatar
rdawes rdawes is offline
Active Poster
 
Join Date: Nov 2004
Location: Plano, TX
Posts: 427
Please Note: rdawes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

What if the electrician did not wire the bedroom into an AFCI? Using only the test button will not tell you that.
Reply With Quote
  #9  
Old 9/23/07, 9:12 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

It sort of reinforces the snake oil aspect of these devices that the only way you can test them is to trust the test button. For all we know that is just a shunt trip.
Question: Do the recalled SqDs (that won't trip under a fault) trip with the test button?
Reply With Quote
  #10  
Old 9/23/07, 9:15 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

Quote:
Originally Posted by Greg Fretwell
Question: Do the recalled SqDs (that won't trip under a fault) trip with the test button?
All of the one's I've come across that were affected by the recall do.
Reply With Quote
  #11  
Old 9/23/07, 9:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

Quote:
Originally Posted by rdawes
What if the electrician did not wire the bedroom into an AFCI? Using only the test button will not tell you that.
It sure will if you trip the circuit then go see if the bedroom is now dead.
Reply With Quote
  #12  
Old 9/24/07, 7:25 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Suretest circuit analyzer problems?

Quote:
Originally Posted by Marc D. Shunk
It sure will if you trip the circuit then go see if the bedroom is now dead.
Exactly what I do...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #13  
Old 9/24/07, 9:44 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Suretest circuit analyzer problems?

My suretest has never tripped an AFCI.

If you want to trip the AFCI, do the impedance test on ground. That will trip it (if it's working).
Reply With Quote
  #14  
Old 9/24/07, 12:13 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

You can certainly create a >30ma ground fault and trip an AFCI but that does not test the "arc fault" circuit.
Reply With Quote
  #15  
Old 9/24/07, 1:26 PM
mporras mporras is offline
Active Poster
 
Join Date: Mar 2005
Location: Edmond, OK
Posts: 183
Please Note: mporras is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Suretest circuit analyzer problems?

As I mentioned in a previous post, my Ideal tester/indicator has tripped AFCI breakers in the past. Not anymore. I have yet to call the company, but I'll report here after I do. Either way, I always trip them at the load center, then check to see of the outlets are dead, as well as attempting to trip them with my tester/indicator...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Tidbits from the ASHI Message Board jbushart Miscellaneous Discussion for Inspectors 126 4/27/07 11:05 AM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM


All times are GMT -4. The time now is 2:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts