The panel I inspected yesterday was a 150 amp split-bus configuration. The panel had numerous deficiencies (more than six disconnects, double taps, double neutrals, etc.), but it also had a surge arrestor installed.

This surge arrestor was installed on the 40 amp disconnect for the electric range. Plus, it was connected directly to the terminals (double tap).

So, my question is this:

Why would the surge arrestor be installed on just the 40 amp breaker to the range? Wouldn't it be better for the arrestor to be installed on the main lighting disconnect breaker?

Since this is a split bus panel, installing the arrestor on the just the 40 amp range disconnect would not provide protection for the rest of the panel, would it? I always thought that if you install a surge arrestor on a single bus panel that the entire panel is protected no matter where you install it on the bus, but what about a split bus panel?

Any help would be appreciated

Kevin
Attached Thumbnails
surge-arrestor-installation-p1170376.jpg   surge-arrestor-installation-p1170377.jpg  



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared ThermographerŪ, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
Find an InterNACHI certified Illinois Home Inspector (and anywhere else in North America)
  #2  
Old 9/27/09, 10:38 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Surge Arrestor Installation

Their is a difference between a Surge Arrestor and a TVSS in the allowance of their installation. A true lighting surge arrestor should be installed on the line side of the system without overcurrent protection ahead of it and the TVSS ( now called SPD's ) should be on the load side protected by a overcurrent protection device. This appears to be a Lighting Arrestor installed on the load side of a breaker.....The silver wrapping around the LA will/should say how it is to be installed based on the manufacturers intent....However....regardless of that I feel it will be pointless based on the installation.....the conductors are not as short as possible and I (my opinion ) feel it will choke itself out and provide very limited protection.

To answer your question, no it should not connect to the range overcurrent protection device and chances are the OCPD is not rated for multiple conductors anyway....so defer to an licensed electrical contractor regarding all the other issues, ask them to verify if it is a lighting arrestor or a surge protector and install it in accordance with its listings ( not just laying in the panelbox....it is designed for a KO.....then wash your hands of it.....



Paul W. Abernathy
Reply With Quote
  #3  
Old 9/27/09, 11:18 AM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: Surge Arrestor Installation

Quote:
Originally Posted by pabernathy View Post
Their is a difference between a Surge Arrestor and a TVSS in the allowance of their installation. A true lighting surge arrestor should be installed on the line side of the system without overcurrent protection ahead of it and the TVSS ( now called SPD's ) should be on the load side protected by a overcurrent protection device. This appears to be a Lighting Arrestor installed on the load side of a breaker.....The silver wrapping around the LA will/should say how it is to be installed based on the manufacturers intent....However....regardless of that I feel it will be pointless based on the installation.....the conductors are not as short as possible and I (my opinion ) feel it will choke itself out and provide very limited protection.

To answer your question, no it should not connect to the range overcurrent protection device and chances are the OCPD is not rated for multiple conductors anyway....so defer to an licensed electrical contractor regarding all the other issues, ask them to verify if it is a lighting arrestor or a surge protector and install it in accordance with its listings ( not just laying in the panelbox....it is designed for a KO.....then wash your hands of it.....
Paul,

Thank you very much for for providing your input. Your answer helps a great deal.

If this device were a true SPD, where in the panel would it be installed, if not on the 40 amp breaker for the range?

I understand that the device itself should not be laying loose in the panel and that the wires are too long (just learned that from you), but wouldn't it provide surge protection to the top breakers on the split bus? And therefore, also provide protection of the 15/20 amp breakers on the bottom of the bus?

Just trying to wrap my head around the logic. I come across a lot of these devices that are double tapped on load side breakers. Most Electricians in my area say that it's OK. This was the first time I encountered the device on a split bus, and it made me think a bit

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared ThermographerŪ, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
  #4  
Old 9/27/09, 4:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Surge Arrestor Installation

Quote:
Originally Posted by krichardson View Post
Paul,

Thank you very much for for providing your input. Your answer helps a great deal.

If this device were a true SPD, where in the panel would it be installed, if not on the 40 amp breaker for the range?

I understand that the device itself should not be laying loose in the panel and that the wires are too long (just learned that from you), but wouldn't it provide surge protection to the top breakers on the split bus? And therefore, also provide protection of the 15/20 amp breakers on the bottom of the bus?

Just trying to wrap my head around the logic. I come across a lot of these devices that are double tapped on load side breakers. Most Electricians in my area say that it's OK. This was the first time I encountered the device on a split bus, and it made me think a bit

Kevin
It would if it is a surge protector...if it is a lighting arrestor it should be on the line side of all those breakers and keeping the leads a short as possible. No, I see no reason to install it on a 40A breaker and in most all cases with a SPD it will not exceed a 15A or 20A breaker depending on the manufacturer.

Type 1: Permanently connected SPDs intended for installation
between the secondary of the service transformer
and the line side of the service disconnect overcurrent
device.

Type 2: Permanently connected SPDs intended for installation
on the load side of the service disconnect overcurrent
device, including SPDs located at the branch panel.

Type 3: Point of utilization SPDs.

Type 4: Component SPDs, including discrete components,
as well as assemblies.



Paul W. Abernathy

Last edited by pabernathy; 9/27/09 at 4:24 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
HELP - Surge protector/sub-panel set up jfrederick Electrical Inspections 5 10/27/08 12:01 AM
Surge protector on panel..? acox Electrical Inspections 6 5/27/08 12:49 PM
GFCI vs Surge protector abishop Electrical Inspections 15 11/26/06 11:01 PM
Surge suppression but no AFCI jonofrey Electrical Inspections 13 11/15/06 11:37 AM
Lighting surge lagudo Electrical Inspections 5 8/30/06 11:49 PM


All times are GMT -4. The time now is 2:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts