Default Surge protector on panel..?

Just found this on today's inspection. The panel is mounted outside the carport. The Square D "Secondary Surge Protector" is mounted to the bottom of the box,with 2 black wires and one white.
The 2 black wires lead up to the service conductors and are tapped into there. The white wire appears to go to the neutral bus.

Is this the correct installation for this? I've never seen this device used before.
Attached Thumbnails
surge-protector-panel-p1100037-845-x-634-.jpg.jpg
Views:	133
Size:	102.4 KB
ID:	21524   surge-protector-panel-p1100040-845-x-634-.jpg.jpg
Views:	128
Size:	86.1 KB
ID:	21525  



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #2  
Old 5/27/08, 2:10 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Surge protector on panel..?

No, it should be on a load side breaker, not the service conductors. If that thing shorts out you will have a fire.
Reply With Quote
  #3  
Old 5/27/08, 6:37 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Surge protector on panel..?

Every time I see one of those they are double lugged. Is that the recommended method of installation?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #4  
Old 5/27/08, 6:49 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Surge protector on panel..?

Quote:
Originally Posted by bsmith
Every time I see one of those they are double lugged. Is that the recommended method of installation?
Yes.
Reply With Quote
  #5  
Old 5/27/08, 7:38 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Surge protector on panel..?

By connecting the Tytewadd Power Filter across the main breaker of an electrical panel, all circuits in that panel can be protected from damaging moderate surges (those exceeding 130 volts), and also, from very destructive lightning surges that produce amperages ranging into the thousands.

Normally, two different types of arresters are used to achieve this dual level protection, however, the Tytewadd is a multi-purpose unit especially designed to handle both.

Where refrigeration and/or critical equipment is present, it is recommended that the Tytewadd Power Filter be installed on a two-pole breaker in a single phase panel and a three-pole breaker in a three phase panel. Each incoming line must be connected to the surge arrester for full protection.

Tytewadd Power Filters are U.L. Listed and CSA Certified. Tested under ANSI/IEEE C62.1 Standards for Secondary Surge Arresters, they exceed test requirements and are in compliance with CSA Standard C22.2 No. 0-M1982





Marcel
Reply With Quote
  #6  
Old 5/27/08, 11:13 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Surge protector on panel..?

These are listed for connection on the load side of a breaker. Whether you "double tap" or pigtail it in depends on trhe listing of the breaker (assuming you don't have it on it's own breaker).
The manufacturers say you get the same protection on the load side as you would on the line side. If you have this on the line side of the service disconnect and it shorts out the only thing putting the fire out will be for the leads to blow open or a fireman hosing the place down.
You are not going to blow the primary fuse on the transformer.
Reply With Quote
  #7  
Old 5/27/08, 12:49 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: Surge protector on panel..?

Thank guys. Now, the Square D info http://ecatalog.squared.com/pubs/Ele...8291-0014D.pdf

says there is a diagnostic light in the middle of this device. The light is out, indicating a fault.
I'm going to recommend the new owners simply have it removed as it's installed improperly and not working anyway. Since they already have some minor electrical work to be done, this shouldn't be much of an expense.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 2:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts