Default Surge suppression but no AFCI

New construction, two service panels with what appears to be surge suppression installed but I didn't see any AFCI breakers. I want to call out the lack of AFCI breakers for bedroom circuits. Is that the correct call or is there some exception for panels with surge suppression installed?
Attached Thumbnails
surge-suppression-but-no-afci-dsc03562.jpg  



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #2  
Old 11/14/06, 7:33 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Surge suppression but no AFCI

John

In My Professional Opinion

The NEC requires the arc faults as you know. I believe you are correct in noting the lack of them.

I would think the surges are an option. What kind are they & what are they to?

In your picture I see the green screw that is supposed to be bonded to the panel. It seems that this is missing in a lot of new installs. But maybe there is another panel bond somewhere else.
Reply With Quote
  #3  
Old 11/14/06, 7:42 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Surge suppression but no AFCI

John,

I see some Doubled up Neutrals in that image, Call that out and from what i can gather.....those units do not look familiar to me...but they are not AFCI's because they dont have the proper connections...

So if this is new construction I would venture to say why the AHJ did not call this out unless for example it is not adopted in your area....remember that AFCI's were only coming into play after 2002....so while they were refered to in the 1999 NEC...they did not become technically NEC effective until 2002.

Regardless of demanding them or suggesting them...AFCI's are a great safety enhancement in my mind...worthy of suggestion even if AFCI's were not required at the time of installation.

As for the green ground screw.....we will assume this is the MAIN panel and not a remote distribution panel ( sub )..otherwise the green screw would need to be removed and Grounded conductors ( netural ) and EGC ( equipment grounds ) would need to be seperated on different bars....and the Neutral ( grounded conductor ) would need to be isolated from the panel ie: Floating.

Long story short....if your area has adopted the 2002 NEC or higher.....AFCI's are required in new construction and should then be included....regardless of it being a GOOD idea....as a man in Chicago would say...IT's CODE !



Paul W. Abernathy
Reply With Quote
  #4  
Old 11/14/06, 7:44 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Surge suppression but no AFCI

One has nothing to do with the other.

AFCI protection is required and the doubled neutrals should be corrected. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 11/14/06, 8:09 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Surge suppression but no AFCI

John,

Has the NEC 2002 been adopted in the community where this home is located?

Just my thoughts. In WI, the AFCI requirement has not been adopted yet.
Reply With Quote
  #6  
Old 11/14/06, 8:11 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Surge suppression but no AFCI

Quote:
Originally Posted by pabernathy

Long story short....if your area has adopted the 2002 NEC or higher.....AFCI's are required in new construction and should then be included....regardless of it being a GOOD idea....as a man in Chicago would say...IT's CODE !
As stated...lol



Paul W. Abernathy
Reply With Quote
  #7  
Old 11/14/06, 8:54 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Surge suppression but no AFCI

Don't forget Paul, sometimes new construction can take a year or two from permit process to finish. The AFCI's would not be required if the permits were pulled before the local AHJ adopted the 02 code. We had many new homes here passing inspection up to a year after we adopted the 02, simply because the permits had been pulled prior to the adoption. I am working with one homeowner who is his own general contractor, he has been working on the home for 3 years now!

Not saying it is a good idea not to have them just because you don't have to, kinda like GFCI's. And of course there are still many out there who are not sold on AFCI protection being what it was promised.
Reply With Quote
  #8  
Old 11/14/06, 10:15 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Surge suppression but no AFCI

Brian,

I guess I am spoiled to the BAD side here in VA where our permits only last 6 months at a time before they have to be renewed...and if they renew in a new cycle...guess what...it has to be inspected in that cycle and would have to comply to that cycle.....

Figured most would atleast have adopted the 2002 NEC by now.....VA did about 1 year ago...and we are usually one of the LAST to do so.....VA hates change....



Paul W. Abernathy
Reply With Quote
  #9  
Old 11/14/06, 11:25 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Surge suppression but no AFCI

Actually AFCIs for bedroom receptacle outlets was in the 99 code, to be effective in 2002.
Reply With Quote
  #10  
Old 11/14/06, 11:38 PM
cmccann's Avatar
cmccann cmccann is offline
Active Poster
 
Join Date: Nov 2003
Location: Canton, MI
Posts: 441
Please Note: cmccann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Surge suppression but no AFCI

Yeah, What Greg said,

Please add to 3.1 points to my rank...I will do the same for you ala Ebay....
Reply With Quote
  #11  
Old 11/15/06, 4:54 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Surge suppression but no AFCI

Quote:
Originally Posted by pabernathy
VA hates change
They call that "being conservative" and perfectly describes a certain political party.



NACHI 2005 U.S. Member of the Year

Last edited by rray; 11/15/06 at 11:31 AM..
Reply With Quote
  #12  
Old 11/15/06, 11:23 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Surge suppression but no AFCI

WHAT...all my posts and I get NO REPS.....Man thats Skewed...lol



Paul W. Abernathy
Reply With Quote
  #13  
Old 11/15/06, 11:28 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Surge suppression but no AFCI

Quote:
Originally Posted by pabernathy
WHAT...all my posts and I get NO REPS.....Man thats Skewed...lol
Paul you impatient man. Are you seeking glory so soon?

I suspect you will be in the green soon. Until then I will give you some....
Reply With Quote
  #14  
Old 11/15/06, 11:37 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Surge suppression but no AFCI

lololol.........Love It....lol

Man you have me PEGGED Michael....you are a wise man !

We all know what an Attention HOG I am.....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
AFCI Controversy rcooke Electrical Inspections 11 9/10/07 2:14 PM
AFCI's Explained by Mike Holt & Eaton Engineer pabernathy Electrical Inspections 19 2/15/07 12:05 PM


All times are GMT -4. The time now is 2:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts