John H. Cooper John H. Cooper is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Juneau, AK
Posts: 26
Default Switch Over Tub

In my AHIT training manual, it states that an electrical switch should not be installed within 5 ft of a tub or shower. This bathroom has switches at the head and foot of the jetted tub, and on the back of the shower enclosure wall at the corner. They control the lights and fan. Can anyone give me a Code section that applies?
Attached Thumbnails
switch-over-tub-dscf0024_edited.jpg   switch-over-tub-dscf0025.jpg  
Reply With Quote
  #2  
Old 11/18/06, 9:56 PM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,198
Default Re: Switch Over Tub

Ya mean AHIT tells it to you but doesn't back it up with a reference????

What kind of training is that.
Reply With Quote
  #3  
Old 11/18/06, 9:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Switch Over Tub

I see no problem with the installations you've pictured, assuming the first picture is a tub only, not a tub-shower combination.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 11/18/06, 10:16 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Switch Over Tub

Ok....since AHIT wont teach it I will....lol

Article 404.4- Wet Locations - A swtich or circuit breaker in a wet location or outside of a building SHALL BE enclosed in a waterproof enclosure or cabinet that shall comply with 312.2(A) . Switches SHALL NOT be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.

IE: It has to be made into the unit and the unit manufactured for the installation otherwise a violation.

Now....just like receptacles...they can go RIGHT up to the point of the tub or shower area.....as long as they do not break into that space...or it has to meet the above article.

So the one behind the wall is fine....I MIGHT reject the first one....hmmm...now that i think about it I probably could FIGHT that one...lol.....I have been known to give it a try...lol

Even in the tub area if no shower is it subject to being WET....anyone have a 8 year old KID in a bathtub...OH YEAH...it will get wet...lol......so is it subject to saturation...?....you tell me....and if you conclude it can...then it is a wet location and would not be allowed past the threshold in MY opinion.



Paul W. Abernathy

Last edited by pabernathy; 11/18/06 at 10:33 PM..
Reply With Quote
  #5  
Old 11/18/06, 11:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Switch Over Tub

In theory, I agree that the switch in picture #1 is subject to potentially "wet" conditions, but I don't think that switch is technically in a "wet location." I think it qualifies (possibly) as "damp."

Quote:
Location, Damp. Locations protected from weather and not subject to saturation with water or other liquids but subject to moderate degrees of moisture. Examples of such locations include partially protected locations under canopies, marquees, roofed open porches, and like locations, and interior locations subject to moderate degrees of moisture, such as some basements, some barns, and some coldstorage warehouses.

The NEC is very specific with regard to the probited "zone" for receptacles and types of luminaires.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 11/18/06 at 11:15 PM..
Reply With Quote
  #6  
Old 11/18/06, 11:52 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Switch Over Tub

jeff,

Is it NOT subject to saturation?....I believe it is in my view...lol

Also......what do YOU consider "Tub or Shower Space"......do you not think the threshold is considered WITHIN that space to the point 404.4 should not apply since it directly makes a statement about switches within the location?



Paul W. Abernathy
Reply With Quote
  #7  
Old 11/19/06, 12:35 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Switch Over Tub

I don't think it's subject to saturation any more than the disposal switch, next to the kitchen sink.

With regards to 404.4, personally, I think it's too vague, and subjet to interpretation that would allow the installation as shown.

It does not say that the tub and shower space is a wet location, and it does not say the switch cannot be installed within the tub and shower space.

It says the switch shall not be installed within wet locations of the tub and shower space.

So, it's not a matter of what we consider to be "the tub and shower space," the question for me is - what is the wet location of the tub space?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 11/19/06, 12:42 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Switch Over Tub

lol....Jeff is within PVC buried a wet location....yep it is acording to the NEC...lol.....so a sink is not within the space of the BOWL area...it is outside of it..on the wall.

The switch in the first picture is clearly PAST the threshold and in the bathtub area...

Ok.....everyone has their own view of the NEC...lol...but lets say this....is the switch in THIS area more subject to being sprayed and saturated where it wont harm the wall...versus on the counter where the WIFE will get quite TICKED at the mess on the counter ...lol

Ok..lol........the original posted wanted a reference and I gave one...lol..let the interpretations fly...lol.....I would not like it personally so my interpretation is i dont like it....



Paul W. Abernathy
Reply With Quote
  #9  
Old 11/19/06, 12:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Switch Over Tub

lol...I looked up Mr. Holts opinion and guess what...he agree's with MY view jeff...lol......sorry



Paul W. Abernathy
Reply With Quote
  #10  
Old 11/19/06, 12:52 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Switch Over Tub

John,

I think AHIT was refering to Art . 680.22, outdoor spas and hot tubs near switches......the 5' issue does not apply to bathtubs,shower stalls and hydromassage bathtubs.

Hope that helps.....but personally I find the switch in the FIRST image on the inside of the tub space......and subject to saturation as well...

But thats ME...lol



Paul W. Abernathy
Reply With Quote
  #11  
Old 11/19/06, 1:45 AM
John H. Cooper John H. Cooper is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Juneau, AK
Posts: 26
Default Re: Switch Over Tub

Thanks Guys!

I really appreciate your enthusiasm. I don't like either switch, or the two switches I didn't take a picture of that were at the foot of the tub.

I can just imagine sitting in the tub after putting a dimmer switch in place of the standard switch in case I want a little more romantic mood lighting. So I put a dimmer in there. Yeah, now I can turn it down. So I reach up with lavendar bath salts running down my arm and grab the dial. The water runs down the shaft and ZAAAAP! So much for my mood.

Or, lets look at the switch by the shower stall. It is for the fan. Now I am standing in the bath with water running down my arms. You know you can stand under the shower and get a regular stream of water off your finger tips. I just realized that I forgot to turn the fan on, so I reach around the stall to turn it on. The water, mixed with the more manly Irish Spring that I am using to wash off the lavendar smell, runs down my arm and off my fingers as I grope around the corner for the light switch. After getting the switch thoroughly drenched, I finally find it. ZAAAAP!

Ok, so maybe only a small chance that there will be enough water going inside the switch to make contact. But, I don't like it.

For this inspection I am going to point out that there are differing opinions about the switch. I was hoping for an honest and for true reference that substantiated the 5' claim for switch distance from tubs and showers as indicated in the training materials I have. And yes, I know NOT to use those materials as my reference. That is why I am asking the questions. I couldn't find it in my IRC code and don't have a copy of the NEC to look it up. And I did find those sections about the hot tub and spas and figured it didn't apply here. Again, I was hoping someone else could point me to a hard reference.

John
Reply With Quote
  #12  
Old 11/19/06, 2:23 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Switch Over Tub

First of all, if there are differing opinions between myself and Paul, you should always use Paul's opinion over mine. He's the expert with regard to electrical matters, I am a Home Inspector (a generalist).

Occasionally, I like to throw things against the wall to see if anything will stick

In this case, I could make a good argument as to the way it is worded, but Paul knows better as to the intent of the code (this is his field).

Quote:
Originally Posted by jcooper2
I was hoping for an honest and for true reference that substantiated the 5' claim for switch distance from tubs and showers as indicated in the training materials I have.
The reference you are looking for does not exist (I think Paul and I both agree on that).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 11/19/06, 8:20 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Switch Over Tub

Quote:
Originally Posted by jcooper2
In my AHIT training manual, it states that an electrical switch should not be installed within 5 ft of a tub or shower. This bathroom has switches at the head and foot of the jetted tub, and on the back of the shower enclosure wall at the corner. They control the lights and fan. Can anyone give me a Code section that applies?
Hi John,

I believe that the AHIT manual (and other standard references) are wrong, the mistake being based in a Carson Dunlop image that is widely referenced by US training companies, the image that is quoted relates to Canadian rather than US codes.

Without getting into a big code interpretation discussion I believe that the NEC only prohibits the placement of switches and outlets "within the footprint of the bath or shower". I also feel that this area of code could stand some tidying up.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #14  
Old 11/19/06, 9:10 AM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,155
Default Re: Switch Over Tub

2003 IRC

E3901.7 Wet locations. A switch or circuit breaker located in a wet location or outside of a building shall be enclosed in a weatherproof enclosure or cabinet. Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.

E3902.11 Bathtub and shower space. A receptacle shall not be installed within a tub or shower space.

E3903.9 Bathtub and shower areas. Cord-connected luminaries, hanging luminaries, lighting track, pendents and ceiling-suspended paddle fans shall not have any parts located within a zone measured 3 feet horizontally and 8 feet vertically from the top of a bathtub rim or shower stall threshold. This zone is all encompassing and includes the zone directly over the tub and shower.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
  #15  
Old 11/19/06, 9:11 AM
cmccann's Avatar
cmccann cmccann is offline
Active Poster
 
Join Date: Nov 2003
Location: Canton, MI
Posts: 441
Please Note: cmccann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Switch Over Tub

Paul...Do you really LOL that much when you post? Every sentence is LOL, good info but man all that LOL is obnoxious. LOL
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Switch location requirement? srowe Electrical Inspections 8 6/15/07 11:07 PM
Safety Switch for Restaurant hmcbride Electrical Inspections 9 3/19/07 12:04 PM
Dishwasher on a switch? jfunderburk Electrical Inspections 48 8/25/06 9:58 PM
Emergency Shut-off switch sfalvey Inspecting HVAC Systems 4 8/18/06 9:11 AM
3 way switches cfuoco Electrical Inspections 4 2/1/06 8:00 PM


All times are GMT -4. The time now is 8:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts