Default Switchable Oulet

Today I inspected a home. Most rooms had a switchable outlet (outlet mounted upside down). In the three bedrooms the switchable outlet had 120 VAC on the top plug and only 98-99VAC on the switchable outlet. The others in the home were fine; on when on, and off when off. I'm thinking there's a wiring problem. Have you seen this? One last commonality--the bedroom's switchable is on a slider-rheostat type of wall switch.
Reply With Quote
  #2  
Old 7/21/08, 6:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Switchable Oulet

Switched receptacles are prohibited from being served by dimmers. That's your problem.
Reply With Quote
  #3  
Old 7/21/08, 7:06 PM
Gregory C. Scheer, Jr. Gregory C. Scheer, Jr. is offline
InterNACHI Member
 
Join Date: May 2008
Location: Plumas Lake, CA
Posts: 28
Default Re: Switchable Oulet

I didn't know that. Thanks. Even so, could it be the wiring of the dimmer that is allowing the lower voltage?
Reply With Quote
  #4  
Old 7/21/08, 7:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Switchable Oulet

Probably the reduction in the dimmer....depending on the setting. As Mark stated...Dimmers on receptacles is a no-no.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 7/21/08, 7:19 PM
Gregory C. Scheer, Jr. Gregory C. Scheer, Jr. is offline
InterNACHI Member
 
Join Date: May 2008
Location: Plumas Lake, CA
Posts: 28
Default Re: Switchable Oulet

Thanks Paul. I found this by checking with my plug. I noticed that the lights were on regarless of the push-to-turn-on switch position. The dimmer is located on the upper portion of the switch. The outlet plug has constant voltage. Thanks for all the info! I'm guessing who ever wired the switches probably mixed up the fan light switch with this one--in all three bedrooms.
Reply With Quote
  #6  
Old 7/21/08, 7:27 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,959
Default Re: Switchable Oulet

Quote:
Originally Posted by Marc D. Shunk
Switched receptacles are prohibited from being served by dimmers. That's your problem.
I didn't know that either... Thanks Marc!

Can you educate us some more as to the reasoning's behind that? Is it some sort of safety concern? Or what?
Reply With Quote
  #7  
Old 7/21/08, 8:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Switchable Oulet

Origionally I believe it was the problems it caused to the vacuum cleaner industry and their motors. But I am sure Marc will elaborate.

It is also a concern since most dimmers have a specific wattage rating it will allow....and without knowing what could be plugged into it.....you could exceed the rating of the dimmer which will heat up and potentially cause a fire among the largest concern.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 7/21/08 at 8:15 PM..
Reply With Quote
  #8  
Old 7/21/08, 9:29 PM
Mark Thorman Mark Thorman is online now
Active Poster
 
Join Date: Mar 2008
Posts: 166
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Switchable Oulet

Is it a code thing.
Reply With Quote
  #9  
Old 7/22/08, 11:16 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Switchable Oulet

Yes, the Code has a prohibition against receptacles being controled by dimmers.

If you think about the reduced voltage on a receptacle it would be similar to starting a manual transmission car off in 3rd instead or 1st gear.
Reply With Quote
  #10  
Old 7/22/08, 4:14 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,959
Default Re: Switchable Oulet

Quote:
Originally Posted by mnahrgang
I didn't know that either... Thanks Marc!

Can you educate us some more as to the reasoning's behind that? Is it some sort of safety concern? Or what?
Siting code isn't particularly helpful in a home inspection situation. We are not code inspectors, and as soon as we site code on one defect, we are liable for all other code violations that we might not be aware of.

The reasoning behind why the outlet is unsafe with a dimmer is useful.

Can someone explain the why behind it?

Thanks
Reply With Quote
  #11  
Old 7/22/08, 4:23 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Switchable Oulet

Most household motors and appliances are designed to start and run at full voltage and either will not start or damage the power supply if full voltage is not available.

This is also true of fluorescent bulbs including CFLs

Resistive loads like tungsten bulbs would have no problem.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #12  
Old 7/22/08, 7:20 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Switchable Oulet

hmmm...I did explain why....guess no one reads my posts anymore....lol....no problem...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 7/22/08, 7:30 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Switchable Oulet

Quote:
Originally Posted by pabernathy
hmmm...I did explain why....guess no one reads my posts anymore....lol....no problem...
Oops, must have missed.
Guess that means I did't read your8 post Paul.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #14  
Old 7/22/08, 7:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Switchable Oulet

thats ok fella.....my posts are crap anyway....Ask Marc...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 7/22/08, 7:47 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Switchable Oulet

Not everything that a person might purposely or accidentally plug in to a switched receptacle will react well to a dimmer. The results can be undesirable, often ruining certain equipment. Motors, in particular, can overheat and fail when run through a dimmer. A television set might just "die". The dimmer itself can fail when serving certain loads. It doesn't really matter what a person promises they will do with that outlet. There's a host of good and required reasons to not serve a switched receptacle by a dimmer.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 10:30 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts