Question Sylvania Panel

I am well aware of zinsco panels and their lap over to sylvania. This sylvania has none of the zinsco breaker colors but does appear to have AL buss bars.

I have been told some sylvania / zinsco models are accepable. I am trying to determine if this is 1 of them or not. any help is appreciated.
Attached Thumbnails
sylvania-panel-mvc-015s.jpg   sylvania-panel-mvc-016s.jpg   sylvania-panel-mvc-017s.jpg  
Reply With Quote
  #2  
Old 1/18/08, 8:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sylvania Panel

You were misinformed based on this statement

Quote:
I have been told some sylvania / zinsco models are accepable.
But this is not a cross-over. No problems are associated with this panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/18/08, 11:47 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Sylvania Panel

I guess I can't type either, "accepable"? Can you clarify or point me to materials to be able to always judge these? I read that the AL buss with CU breaker clamps was part of the problem. Some sylvania have it some don't. Some sylvania have the mult-colored magna-trip, some don't.
Reply With Quote
  #4  
Old 1/18/08, 11:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sylvania Panel

There are several variations, but the "cross-over" is simply a Zinsco panel with a Sylvania sticker - no design change whatsoever.

The thing to look for is the blade type bus bars. They may be AL or CU (copper). The earliest of Zinsco did not have bus bars, but the breakers are a dead giveaway. The last photo is the feed-thru type Zinsco breakers, prior to the copper bus bars.
Attached Thumbnails
sylvania-panel-z12.jpg   sylvania-panel-z22.jpg   sylvania-panel-zinsco1a.jpg   sylvania-panel-pb220018.jpg   sylvania-panel-s4.jpg  




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/19/08, 12:07 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sylvania Panel

Quote:
Originally Posted by kgerhauser
I read that the AL buss with CU breaker clamps was part of the problem.
Again, you've been misinformed. Read up on Zinsco here http://www.inspect-ny.com/electric/Zinsco.htm

"Magnatrip" is from their original design and is simply a reference to their "new" technology from the years where fuses were the norm. As breakers became more popular, they stopped branding "Magnatrip."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 1/19/08, 12:07 AM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Sylvania Panel

Thanks Jeff, Real Zinsco or sylvania with the pretty breaker handles I had no trouble with, but now I have a definitive item to check.
Reply With Quote
  #7  
Old 1/19/08, 12:12 AM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Sylvania Panel

I was typing during your last post.
Quote:
A principal Zinsco circuit breaker (or Sylvania circuit breaker for those Sylvania panels using the Zinsco product) point of failure appears to be at the point of contact where the circuit breaker contacts clip onto the electrical panel bus, combined with the use of an aluminum electrical panel bus.
http://www.inspect-ny.com/electric/Zinsco.htm is where I read it and this is copied from the site.
Reply With Quote
  #8  
Old 1/19/08, 12:18 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sylvania Panel

The point of contact is definitely one of the problem areas. Your reference was to "the AL buss with CU breaker clamps" which is inaccurate.

In any event, that site gives all the gory details, but if you come up with any questions, I'll do my best to help answer them for you. I've seen a few of these panels in my time. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 1/19/08, 12:21 AM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Sylvania Panel

Unfortunately, these were sold heavily in my area. Approx. 50% of my inspections have either Zinsco, Zinsco/Sylvania, or Sylvania. Thanks again.

PS gave you a greenie.
Reply With Quote
  #10  
Old 1/19/08, 12:22 AM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Sylvania Panel

And I neade to lurn to typo better.
Reply With Quote
  #11  
Old 1/19/08, 12:48 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sylvania Panel

I average 3 or 4 of these each week. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 1/20/08, 4:00 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Sylvania Panel

Jeff:

Did you note the green branch circuit conductors connected to the two breakers on your report?

Also, another defect item is when you see any circuit conductor that is "nicked" at the termination. That conductor can break when handled during any replacement or maintenance task.

Green or green with yello stripes or bare conductors are used for EGC and Bonding jumpers.

"210.5 Identification for Branch Circuits

(B) Equipment Grounding Conductor The equipment grounding conductor shall be identified in accordance with 250.119.

250.119 Identification of Equipment Grounding Conductors
Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered, or insulated. Individually covered or insulated equipment grounding conductors shall have a continuous outer finish that is either green or green with one or more yellow stripes except as permitted in this section. Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors."

Last edited by jtedesco1; 1/22/08 at 7:12 AM..
Reply With Quote
  #13  
Old 1/20/08, 11:38 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Sylvania Panel

I always mention improperly identified conductors in my reports. Along with nicked conductors, these issues are mentioned as "observations" and not necessarily "items in need of repair or correction."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 2:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts