Default System overload ?

Need some help. New meter on the back of the garage. One set of 2awg AL cables feed to a 100 amp panel in the garage, (20 breakers all for the garage). Another set of 2 awg AL cables fed directly from the exterior meter (not the garage panel) to a seperate 100 amp breaker at the front of the garage. Approx. 40 feet. This 100 amp breaker (2 awg AL wire) then feeds a 200 amp breaker in the basement of the house (approx. 30 feet). The 200 amp panel is full in the basement. Is this set up right in your opinion or should I call for review. It seems like the 200 amp panel should be in the garage with everything fed off of it. Thanks for you help. Stan
Reply With Quote
Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America)
  #2  
Old 10/16/09, 9:01 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: System overload ?

Aluminum Service Rating
2AWG 100 amps



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 10/16/09, 11:29 PM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: System overload ?

There are two sets of 2 awg AL cables attached at the lugs at the exterior meter. One goes to the 100 amp garage panel, the other runs 40 feet in the attic of the garage to a single 100 amp breaker. This single breaker feeds the 200 amp panel in the house. Altogether there are 60 breakers between the garage and house. Does this sound acceptable?Stan
Reply With Quote
  #4  
Old 10/16/09, 11:44 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: System overload ?

It might be ok for a small house with gas heat, gas water heater and gas oven assuming no other wiring issues etc. What all did you see connected as 240V loads and what is the square footage? Did you have a 4-wire feed to that 200 amp panel?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 10/17/09, 12:29 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: System overload ?

With your description it's irrelevant how many breakers exist. Each of the 2 individual panels are rated 100 amp. The 200 amp panel is 100 amp.

Also what Bruce ask, is the panel in the house a 4-wire feed? Are the grounds and neutrals separated? Is it bonded to the to the panel in the garage? Which, by your description, is the main disconnect.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 10/17/09, 1:06 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: System overload ?

The house is only going to be able to draw as much as the upstream breaker will allow it to. Even though it is a 200 amp main breaker panel, it is fed with a 100 amp breaker from the garage. The 200 amp breaker won't cause any problems, just confusion as to why it's not a true 200 amp allowable panel. The upstream 100 amp breaker will trip when the draw is over 100 amps, so the 200 amp breaker may be serving only as a disconnect.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #7  
Old 10/17/09, 1:24 AM
Stan Croenne Stan Croenne is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Springfield, IL
Posts: 60
Default Re: System overload ?

Square feet of the home is 950. The garage is probably 700 square feet. A total man cave. 3 wire feed to the house. There were 15 quad outlets in the garage. A water heater for in floor heating system in the garage. A wall air unit in the garage. I wonder if it is acceptable to have two seperate sets of feeder cables connected to the meter. It doesn't seem right. That seems like double lugging to me. Stan
Reply With Quote
  #8  
Old 10/17/09, 9:36 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: System overload ?

Most meter panels have kits available to feed two main panels. Since these are closed up/tagged we can't inspect inside them.

I'm sure you found something wrong there that will require an electrician anyway.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 10/17/09, 10:30 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: System overload ?

Is there a disconnect available to shut off the power to the house from one location? The disconnects should be grouped together.

If the cables running to the 2nd panel in the garage are unfused, that would also be incorrect.

Double lugs in a meter socket are common. These are 2 lugs on the same stud, not 2 wires in one lug.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Make $50.00 More Profit per Inspection with Septic Tanks ebeahm1 Ancillary Inspection Services & Additional Topics 6 8/20/09 1:38 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 2:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts