Ok, take a look at this panel.....just want any words of wisdom you can share. Thank you!!
Michael Byrd Byrd-House Inspections Belpre, Oh |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not so much to say, really. Square D, with plug on fuse units. I still have boxes of NOS fuse holders for these. Nothing's jumping out at me in the pic, but naturally a fella would want to make sure the connected wire gauge jives with the fuse size.
|
|
#3
|
|||
|
|||
|
Thanks Marc. I didn't see anything that SCREAMED at me....but I always feel better after some NACHI assistance!
Michael Byrd Byrd-House Inspections Belpre, Oh |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
You're bound to have doubled, tripled, and quadrupled up neutrals in a panel of that style, but I think that's something you guys generally look for no matter what style of panel you're faced with.
|
|
#5
|
|||
|
|||
|
Please Note:
afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
there seems to be a single white wire exiting the panel unprotected through a drilled (?) hole on the upper right of the panel and not through a knock-out. hard to tell from the photo.
|
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The only thing that ever screams at me on a plug fuse panel is matching the wire size to the fuse. Type S fuses are great if they have the right adapter but I have seen 20/30 adapters (a single type) on 14ga wire. They usually end up with "greenies" in them. I am not even sure why that adapter is listed/sold.
|
![]() |