Default The tale of two cities right or wrong

Home constructed in 2009 two panels in the garage fed from a meter base on the opposite side of the wall in one AHJ these panels are correct and in another AHJ they are wrong some times it get confusing for us old farts
Attached Thumbnails
tale-two-cities-right-wrong-2825-chelsea-ct-enid-12-13-11-019.jpg   tale-two-cities-right-wrong-2825-chelsea-ct-enid-12-13-11-022.jpg   tale-two-cities-right-wrong-2825-chelsea-ct-enid-12-13-11-024.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/14/11, 5:33 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: The tale of two cities right or wrong

That second panel is wrong no matter what the AHJ says.

Unless I am not understanding your typical cryptic post.

Show us the outside.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 12/14/11, 5:52 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: The tale of two cities right or wrong

Quote:
Originally Posted by mlarson View Post
That second panel is wrong no matter what the AHJ says.

Unless I am not understanding your typical cryptic post.

Show us the outside.
OK nothing to hide
Attached Thumbnails
tale-two-cities-right-wrong-2825-chelsea-ct-enid-12-13-11-018.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 12/14/11, 5:57 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: The tale of two cities right or wrong

So the building really does lack a single disconnect that removes all power and an AHJ is OK with that?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 12/14/11, 6:27 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: The tale of two cities right or wrong

The left panel has a main at the bottom and the right panel has a back-fed 100 main at the top. Am I missing something obvious?
Reply With Quote
  #6  
Old 12/14/11, 6:30 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: The tale of two cities right or wrong

Quote:
Originally Posted by mlarson View Post
So the building really does lack a single disconnect that removes all power and an AHJ is OK with that?
Yipper and also the double lugging on neutral and grounds no isolation of neutrals and ground. I think the AHJ is a plumber I personally called and talked with the inspector



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 12/14/11, 6:43 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: The tale of two cities right or wrong

Quote:
Originally Posted by cbottger View Post
Yipper and also the double lugging on neutral and grounds no isolation of neutrals and ground. I think the AHJ is a plumber I personally called and talked with the inspector

no problem in having more than one equipment grounding conductor under one screw.

I see nothing wrong myself



Mike Whitt
Contractor/Instructor
Reply With Quote
  #8  
Old 12/14/11, 6:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: The tale of two cities right or wrong

Quote:
Originally Posted by cbottger View Post
Yipper and also the double lugging on neutral and grounds no isolation of neutrals and ground. I think the AHJ is a plumber I personally called and talked with the inspector
The lack of isolation was my first concern.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #9  
Old 12/14/11, 7:17 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: The tale of two cities right or wrong

Since both of these panel contain service disconnects and are therefore service panels, the neutral must be bonded to the enclosure and both neutrals and EGC's can be terminated on the bus.
Reply With Quote
  #10  
Old 12/14/11, 7:30 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: The tale of two cities right or wrong

I agree with RM, these are two service panels. I don't see any doubled neutrals and the grounding conductors can be doubled as long as same size and material.
Reply With Quote
  #11  
Old 12/14/11, 8:28 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: The tale of two cities right or wrong

I generally call it like the AHJ requires for a given city unless I am in Bohunk.
Two cities I inspect in one requires neutrals and grounds to be isolated and one per screw only the other city is as in the pics. I did not see a back feed on the 100 amp breaker it was being fed directly from the meter base as was the other panel. I did not open the meter base as it was sealed and I don't break meter seals

My comment was just to note the difference between two AHJ's what they require



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 12/14/11, 9:06 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: The tale of two cities right or wrong

Quote:
Originally Posted by cbottger View Post
I generally call it like the AHJ requires for a given city unless I am in Bohunk.
Two cities I inspect in one requires neutrals and grounds to be isolated and one per screw only the other city is as in the pics. I did not see a back feed on the 100 amp breaker it was being fed directly from the meter base as was the other panel. I did not open the meter base as it was sealed and I don't break meter seals

My comment was just to note the difference between two AHJ's what they require
So you're saying that there are local codes that affect this installation? Under the NEC it's compliant.
Reply With Quote
  #13  
Old 12/14/11, 9:59 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: The tale of two cities right or wrong

Charley, the NEC rule is one neutral per terminal and this is echoed in the installation instructions for the panel. Unused holes can be used for multiple grounding conductors by the instructions.
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/14/11, 10:17 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: The tale of two cities right or wrong

Quote:
Originally Posted by Robert Meier View Post
So you're saying that there are local codes that affect this installation? Under the NEC it's compliant.
Yes I am saying two different AHJ's are interrupting their own version of the NEC



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #15  
Old 12/15/11, 4:56 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: The tale of two cities right or wrong

Quote:
Originally Posted by cbottger View Post
Yes I am saying two different AHJ's are interrupting their own version of the NEC

I hate when they do that.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Free Books And Articles For Electrical jtedesco1 Electrical Inspections 14 1/6/08 6:45 PM
What's Wrong Here? jtedesco1 Electrical Inspections 10 12/9/07 9:36 PM


All times are GMT -4. The time now is 8:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts