#1
|
||||
|
||||
|
Home constructed in 2009 two panels in the garage fed from a meter base on the opposite side of the wall in one AHJ these panels are correct and in another AHJ they are wrong some times it get confusing for us old farts
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
| Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
That second panel is wrong no matter what the AHJ says.
Unless I am not understanding your typical cryptic post. Show us the outside. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#3
|
||||
|
||||
|
OK nothing to hide
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#4
|
||||
|
||||
|
So the building really does lack a single disconnect that removes all power and an AHJ is OK with that?
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The left panel has a main at the bottom and the right panel has a back-fed 100 main at the top. Am I missing something obvious?
|
|
#6
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#7
|
|||
|
|||
|
Quote:
no problem in having more than one equipment grounding conductor under one screw. I see nothing wrong myself Mike Whitt Contractor/Instructor |
|
#8
|
||||
|
||||
|
The lack of isolation was my first concern.
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since both of these panel contain service disconnects and are therefore service panels, the neutral must be bonded to the enclosure and both neutrals and EGC's can be terminated on the bus.
|
|
#10
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
I agree with RM, these are two service panels. I don't see any doubled neutrals and the grounding conductors can be doubled as long as same size and material.
|
|
#11
|
||||
|
||||
|
I generally call it like the AHJ requires for a given city unless I am in Bohunk.
Two cities I inspect in one requires neutrals and grounds to be isolated and one per screw only the other city is as in the pics. I did not see a back feed on the 100 amp breaker it was being fed directly from the meter base as was the other panel. I did not open the meter base as it was sealed and I don't break meter seals My comment was just to note the difference between two AHJ's what they require Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#13
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Charley, the NEC rule is one neutral per terminal and this is echoed in the installation instructions for the panel. Unused holes can be used for multiple grounding conductors by the instructions.
|
| Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Yes I am saying two different AHJ's are interrupting their own version of the NEC
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#15
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.