I am confused about the new code for tamper resistant outlets. Do all GFCI outlets need to be tamper resistant? Do the outlets for the disposal, dishwasher, laundry sink, washer, refrigerator, etc. need to be tamper resistant? Our city recently adopted the 2009 code and I need to know this information for sure. Thanks,
Don Powell, El Paso, TX |
| Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
2009 IRC E4002.14 Tamper-resistant receptacles. In areas specified in
Section E3901.1, 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles. Commentary: Section 3901.1 addresses all 15- and 20-amp 125-volt receptacles in a dwelling; therefore all such devices must be listed tamper-resistant receptacle devices. These receptacle devices have an internal mechanism that blocks access to the plug prong openings except when a plug is inserted into the receptacle. The intent is to protect children who often insert objects into receptacles out of curiosity. The author recalls more than one experience where, as a youngster, a bobby pin or nail was inserted into a receptacle and fortunately, he lived to tell about it. The contact openings (slots) in receptacles pose a shock or electrocution hazard for anyone who purposely or accidentally inserts a metallic object into such openings in a receptacle. The Consumer Product Safety Commission (CPSC) estimates that there are approximately 3,900 injuries treated by hospital emergency rooms every year that are the result of shock or burns from receptacles. Children are the most at risk because of their curiosity and lack of knowledge of the danger and nearly one-third of the reported injuries occur to children. Tamper-resistant receptacles were developed to reduce injuries and are now required for nearly all receptacle locations. Obviously, the intent is to require tamper-resistant receptacles in all locations where there is a possibility of tampering. This section applies to 125-volt, 15- and 20-amp receptacles only. A typical tamper-resistant receptacle is shown in Commentary Figure E4002.14. Note the embossed “TR” on the face of the receptacle to indicate that it is different from a standard receptacle. Inserting a two prong (or three prong) plug into a tamper-resistant receptacle is no different than it is for a standard receptacle. Mechanisms within the receptacle sense that the two parallel prongs are being inserted simultaneously, which unlocks an internal shutter to the electrical contacts. If the internal mechanism senses only one slot being penetrated, such as with a screwdriver, nail or other object, the shutter does not release to open the slot to the electrical contacts. Each receptacle manufacturer has developed its own proprietary shutter mechanisms to comply with the operation requirements. It would be easier for installers to use “TR” receptacles in all locations rather than trying to determine what locations, if any, are exempt. Based on the extensive coverage of Section E3901.1, it is hard to determine that there are any exempt locations. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#3
|
||||
|
||||
|
Quote:
JMO & 2-Nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Under the 2008 NEC, all receptacles in a dwelling are required to be TR. That includes, GFCI, behind the refrig, basement, attic and all outdoor receptacles, etc. Receptacles installed in wet locations, such as outdoors, are required to be listed as WR (or weather resistant) as well as TR.
The 2011 NEC has relaxed some of the requirements for TR receptacles in dwellings. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Kitchen outlets | lwootten | Electrical Inspections | 4 | 11/11/10 6:21 PM |
| Tamper Resistant oulets & Testers | gbeaumont | Electrical Inspections | 18 | 5/4/10 9:29 AM |
| ungrounded outlets! | gmaher | Electrical Inspections | 29 | 6/10/07 10:58 PM |
| Properly Testing GFCI Outlets | tchristopher | Electrical Inspections | 17 | 3/17/07 11:19 AM |